[EnergyPlus_Support] Min ODA rate is not being met?



Min ODA rate is not being met. Resulting airflow is 0.03 m3/s which is smaller than the 0.175 Min ODA rate input in the sizing object.

Any idea why?

!JMM VENTILATION 118204
Sizing:System,
  118204 AHU,                                              !- AirLoop Name
  Sensible,                                                !- Type of Load to Size On
  0.175000,                                                !- Design (minimum) outside air volumetric flow rate {m3/s} !630 m3/hr
  1,                                                       !- Minimum System Air Flow Ratio
  7,                                                       !- Preheat design set temperature {C}
  0.008,                                                   !- Preheat design humidity ratio {kg-H2O/kg-air}
  11,                                                      !- Precool design temperature {C}
  0.008,                                                   !- Precool design humidity ratio {kg-H2O/kg-air}
  13,                                                      !- Central cooling design supply air temperature {C} ! For cooling room setpoint 24°C as per G3.1.2.8  deltaT = 11°C
  32,                                                      !- Central heating design supply air temperature {C} ! For heating room setpoint 21°C as per G3.1.2.8  deltaT = 11°C
  NonCoincident,                                           !- Sizing Option
  No,                                                      !- 100% Outdoor Air in Cooling
  No,                                                      !- 100% Outdoor Air in Heating
  0.008,                                                   !- Central cooling design supply air humidity ratio {kg-H2O/kg-air}
  0.008,                                                   !- Central heating design supply air humidity ratio {kg-H2O/kg-air}
  DesignDay,                                               !- Cooling Design Air Flow Method
  0,                                                       !- cooling design air flow rate {m3/s}
  DesignDay,                                               !- Heating Design Air Flow Method
  0;                                                       !- heating design air flow rate {m3/s}



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/