The 20kW of OtherEquipment doesn’t add to the electricity consumption
meter, it just adds heat load to the zone. This is to replace the 20kW of
heat “lost” by the pumps -- heat that originally came from electricity
used by the pumps. ElectricEquipment would add 20kW to the electricity
meter thus double counting the 20kW of electricity. A few types of equipment, like water heaters, already do add
their skin losses to zone. The wish list does include getting all types
of equipment inefficiencies coupled to zone loads. From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of James V Dirkes II, PE Dear Brent, I’m missing something….. If the energy is already accounted for
in, say, the pump object, How can it be that adding an
OtherEquipment object with 20kW doesn’t double count? The
Building Performance Team From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of Griffith, Brent
OtherEquipment is less hassle than
ElecticEquipment, it does not consume energy that would need to be backed out
to avoid double counting. From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of jvd2pe
Dear Forum, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.