The air loop can fail convergence for reasons other than tolerance. Are you getting many of these errors?
Are you using chilled water coils? If so try setting the availability schedules for the water coil to always on and see if the message disappears.

On 9/30/2010 8:50 AM, grandocu wrote:
 

Hello everyone,

I have a warning that keeps popping up saying "Maximum iterations (20) exceeded" and the message below says the airloop failed, but all tolerance values below are 0. Does anyone know why this message is showing up if all the tolerance values are 0?

** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ANNSIM, 01/02 05:10 - 05:11
** ~~~ ** SimFlags=[TFFFFFFF] AirLoops[T],ZoneEq[F],NonZoneEq[F],PlantLoops[F],CondLoops[F],ElecCircuits[F],PlantDemandLoops[F],CondDemandLoops[F]..F=ok,T=fail
** ~~~ ** HVAC Tolerance Flags=[0000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0]..0=ok,1=fail
** ~~~ ** HVAC Tolerance Values, Most Recent listed first
** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** HVAC side outlet node=[724 - AHU-B-6 RETURN AIR OUTLET]
** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** HVAC side outlet node=[723 - AHU-B-3 RETURN AIR OUTLET]
** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** HVAC side outlet node=[720 - AHU-B-5 RETURN AIR OUTLET]
** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** HVAC side outlet node=[719 - AHU-B-4 RETURN AIR OUTLET]
** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** HVAC side outlet node=[722 - CB AHU-B-2 RETURN AIR OUTLET]
** ~~~ ** Plant Tolerance Flags=[00000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0],PlantFlowMassFlow[0]..0=ok,1=fail
** ~~~ ** Plant Tolerance Values, Most Recent listed first
** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** Plant side outlet node=[390 - CB CONDENSER DEMAND OUTLET NODE]
** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** Plant side outlet node=[347 - CHW_LOOP CNDW DEMAND OUTLET]
** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** Plant side outlet node=[383 - CB CONDENSER DEMAND INLET NODE]
** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** Plant side outlet node=[342 - CHW_LOOP CNDW DEMAND INLET]
** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** Plant side outlet node=[314 - HW_LOOP HW DEMAND OUTLET]
** ~~~ ** Plant Flow Tolerance Values, Most Recent listed first
** ~~~ ** PlantFlowFlowTol=0.000
** ~~~ ** PlantFlowFlowTol=0.000
** ~~~ ** PlantFlowFlowTol=0.000
** ~~~ ** PlantFlowFlowTol=0.000
** ~~~ ** PlantFlowFlowTol=0.000


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___