Dear I'm simulating a building to meet LEED the system to use is 8 per ASHRAE (VAV with PFP
Boxes) But I have a question to the point of Ashrae
G3.1.3.14 90.1-2007. According to Ashrae, fan in parallel VAV fa Powered boxes shall be sized
for 50% of the peak design flow rate, this flow corresponds to the field
MAXIMUM PRIMARY AIR FLOW RATE in AirTerminal:SingleDuct:ParallelPIU:Reheat????? According to Ashrae, minimum volumen setpoint fan powered-boxes shall be equal to 30% of peak design flow rate or the rate required to meet the minimum outdoor air ventilation requirement, this flow corresponds to the field MINIMUM PRIMARY AIR FLOW FRACTION en AirTerminal:SingleDuct:ParallelPIU:Reheat, expressed as a fraction????? Thank. Best Regards. Rodrigo Pérez. Engineer HVAC | MDCS. |