Dear Rodrigo,,

 

You will need to “autosize” the PFP fans, find their capacity from .eso file (or the “HVACEquipmentSizing” report), and then use that value as “Maximum Primary Air Flow Rate”, and one half for the “Minimum Secondary Air Flow Rate”, something like the example below….

 

 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Rodrigo Perez Gallegos
Sent: Thursday, September 30, 2010 4:05 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Simulation LEED _ System 8

 

 

Dear

 

I'm simulating a building to meet LEED

the system to use is 8 per ASHRAE (VAV with PFP Boxes)

But I have a question to the point of Ashrae G3.1.3.14

90.1-2007.

 

According to Ashrae, fan in parallel VAV fa Powered boxes shall be sized for 50% of the peak design flow rate, this flow corresponds to the field MAXIMUM PRIMARY AIR FLOW RATE in AirTerminal:SingleDuct:ParallelPIU:Reheat?????

 

According to Ashrae, minimum volumen setpoint fan powered-boxes shall be equal to 30% of peak design flow rate or the rate required to meet the minimum outdoor air ventilation requirement, this flow corresponds to the field MINIMUM PRIMARY AIR FLOW FRACTION en AirTerminal:SingleDuct:ParallelPIU:Reheat, expressed as a fraction?????

 

 

Thank.

 

Best Regards.

 

Rodrigo Pérez.

Engineer HVAC | MDCS.

 

 



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___