Dear Rodrigo,,
You will need to “autosize” the PFP
fans, find their
capacity from .eso file (or the “HVACEquipmentSizing”
report), and
then use that value as “Maximum Primary Air Flow
Rate”, and one
half for the “Minimum Secondary Air Flow Rate”,
something like the
example below….
The Building Performance
Team
James
V. Dirkes II, P.E., LEED AP
1631
Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
Dear
I'm
simulating a building to meet LEED
the system
to use is 8 per ASHRAE (VAV with PFP
Boxes)
But I have
a question to the point of Ashrae
G3.1.3.14
90.1-2007.
According
to Ashrae, fan in parallel VAV fa
Powered boxes shall be sized for 50%
of the peak design flow rate, this
flow corresponds to the field MAXIMUM
PRIMARY AIR FLOW RATE in
AirTerminal:SingleDuct:ParallelPIU:Reheat?????
According
to Ashrae, minimum volumen setpoint
fan powered-boxes shall be equal to
30% of peak design flow rate or the
rate required to meet the minimum
outdoor air ventilation requirement,
this flow corresponds to the field
MINIMUM PRIMARY AIR FLOW FRACTION en
AirTerminal:SingleDuct:ParallelPIU:Reheat,
expressed as a fraction?????
Thank.
Best
Regards.
Rodrigo
Pérez.
Engineer
HVAC | MDCS.
|