Or build two models and use the chiller + (cooling tower) energy from the single cilled water system and the model with two chillers for the rest of the system energy.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Eddie Corwin <ecorwin@...> wrote:
>
>
>
>
> I would go with the two chiller approach, but modify the performance curves so
> that they better reflect the actual conditions.
>
>
>
>
>
> ________________________________
> From: "James V Dirkes II, PE" <jim@...>
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Sent: Thu, September 30, 2010 1:56:43 PM
> Subject: RE: [EnergyPlus_Support] Chilled Beams need a separate water control
> loop
>
>
> Thanks, Brent.
>
> Two chillers changes part load relationships a lot.
> Lower water temp to the chilled beams probably affects their performance, too,
> but I suspect the bigger impact will be on the chiller performance.
>
> I think Iâ??ll go with the one chiller approach.
>
> This might be a nice item to add to the development list, if itâ??s not already on
> it!
>
> The Building Performance Team
> James V. Dirkes II, P.E., LEED AP
> 1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
>
> From:EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Griffith, Brent
> Sent: Thursday, September 30, 2010 12:36 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: RE: [EnergyPlus_Support] Chilled Beams need a separate water control
> loop
>
>
> In E+, you either end up needing to use two separate chilled water loops (and
> two chillers), or ignore the higher temp water for the beams and use one supply
> temperature.
>
> From:EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jvd2pe
> Sent: Thursday, September 30, 2010 7:45 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Chilled Beams need a separate water control loop
>
>
> Dear Forum,
>
> In a typical chilled water system using CHILLED BEAMS, you need:
> * a chilled water loop for air handler coils at ~45F / 7C
> * another chilled water loop for the chilled beams at ~60F / 15C
> * both served by single chiller
>
> Does anyone have suggestions about how to set this up in E+?
>
> Thanks in advance!
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/