The chilled beam model is controlled based on load and the heat transferred
to the chilled water won’t really vary with inlet water temps. The
mass flows and temps are different, but not the energy flow rate. The return temps into the chiller will depend a lot on the pumping
configuration, the relative magnitudes of flows, etc. But in many cases
the mixing of different return flows can work out to be not very different from
what a higher-temp secondary loop loads would do to a lower-temp primary loop. So
yes, I agree the single chiller approach can be adequate. From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of James V Dirkes II, PE Thanks, Brent. Two chillers changes part load
relationships a lot. Lower water temp to the chilled beams
probably affects their performance, too, but I suspect the bigger impact will
be on the chiller performance. I think I’ll go with the one chiller
approach. This might be a nice item to add to the
development list, if it’s not already on it! The
Building Performance Team From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of Griffith, Brent
In E+, you either end up needing to use
two separate chilled water loops (and two chillers), or ignore the higher temp
water for the beams and use one supply temperature. From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of jvd2pe
Dear Forum, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.