Re: [EnergyPlus_Support] EP-launch with separate weather file





If you use the weather file, it will override any location that would be specified in the idf.

For design conditions, you would need to reference the special periods on the weather file or incorporate an external file.

You will still need to have a RunPeriod (for weather file) object
and
a SimulationControl object to direct EnergyPlus what to do.

What sections of the manual did you look at?

At 12:01 AM 10/12/2010, airscapefans wrote:
I'm trying to run a single idf file without specifying any weather location or design conditions within the idf file.
Instead I'm specifying the weather file from EP-Launch.
Result = errors (missing location, etc...)

Can I launch/run with 'external' location and design conditions ?
If so, I could not find any section in the manual on why this should or should not work.


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___