RE: [EnergyPlus_Support] Large Reheat Consumption During Summer





Hi James,

Thank you for the reply.

I have transitioned the file to v5. However I still find that I am getting the same problem as before.

I have attached to updated idf file.

--- On Fri, 10/15/10, James V Dirkes II, PE <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:

From: James V Dirkes II, PE <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>
Subject: RE: [EnergyPlus_Support] Large Reheat Consumption During Summer
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Received: Friday, October 15, 2010, 9:34 AM

 

Dear Langdon.

 

The text â??AHU HEATING COIL CONTROLLERâ?? does not appear in your IDF, so I canâ??t figure out what is referred to by the error.  In addition, the IDF is difficult to read because of the many interspersed comments.

 

I recommend that you begin using the newest version, so it can be opened by the IDF Editor.  Transition of your IDF to the current version is almost a one click affair!

 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Langdon Alger
Sent: Friday, October 15, 2010 8:58 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Large Reheat Consumption During Summer

 

 

Hello,

 


I am running multiple simulations using various building configurations and I have run into the problem in my results which I can't determine the cause for.

I get low natural gas consumption in the winter months and high consumption during the summer due to the reheat system. I am using an old version of EnergyPlus which I hope is not a problem.

I do get a Severe error in my simulations which occurs multiple times:

Severe ** Controller error for controller = AHU HEATING COIL CONTROLLER
** ~~~ ** Occurrence info=EDMONTON STONY PLAIN AB CAN WYEC2-B-25145 WMO#=711230, 08/06 04:02 - 04:03
** ~~~ ** Controller function is inconsistent with user specified controller action = "" action
** ~~~ ** Actuator will be set to minimum action
** ~~~ ** Note: Chilled water coils should be reverse action and the entering chilled
** ~~~ ** water temperature should be below the setpoint
** ~~~ ** Note: Hot water coils should be normal action and the entering hot
** ~~~ ** water temperature should be above the setpoint

I have attached the simulation file I am working with and the weather file.

Thank you for your help.
 

 




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
d:\eudora\attach\File_1_v5.idf