Yes. That's how I've checked when the schedule value
becomes non-zero, and this is the bit that I don't get.
When I look at the day schedule in the idf, I can't
understand why the "Schedule Value" report variable for
schedule 10001 reports the first non-zero values so early
(06:30 I think...see eso) even on timestep reporting
interval...the first non-zero should be reported at 08:00:
! Profile: KiTa_Workingday_Profile
Schedule:Day:List, 10000 , Any number, No,
30,
0,
0,
0,
0,
0,
0,
0,
0,
0,
0,
0,
0,
0,
0,
0,
.4,
.5,
.8,
1,
.85,
.8,
.8,
.8,
.8,
.8,
.8,
1,
.6,
.65,
.6,
.6,
.6,
.7,
.45,
.6,
.25,
.4,
0,
0,
0,
0,
0,
0,
0,
0,
0,
0,
0;
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx,
Richard Raustad <RRaustad@...> wrote:
>
> Have you tried using the "Schedule Value" report
variable and
> comparing this output to the people sensible heat
gain and occupation
> outputs?
>
> On 10/15/2010 7:53 AM, jeannieboef wrote:
> >
> > Hi James.
> >
> > 1. I'm going to replace the "Always On" schedule
with a "binarized
> > occupation schedule".
> >
> > (although I now know that if e+ expects a 1/0
schedule and sees a
> > fractional, for example occupation schedule, it
will automatically
> > assume all non-zeros to be 1 and zeros to be
zero, so I could use the
> > occupation schedule here)
> >
> > I wanted to maintain the abillity of the fan
availibility to turn on
> > and off on schedule and when availible and on,
deliver a constant
> > volume. It should cycle on and off to meet both
the minimum air and
> > room loads as required during its availibillity
on time.
> >
> > 2. Yes, this manager is not used, but I thought
to keep it if it
> > became apparent that it is needed at a future
stage. I will try and
> > delete this manager (which overides scheduled
values as specified) as
> > it maybe suppressing ventilation during
"darkness hours". Good thinking.
> >
> > 3. The ODA controller is auto-sizing to the
correct value (checked
> > it). More over I checked with this also manually
set (no difference),
> > so that was not the problem. I don't want the
master of the
> > auto-sizing to become irrelivant, as I'd rather
adjust as little
> > inputs as nessesary, so that's why I left this
on auto.
> >
> > Well spotted. Thanks for the input.
> >
> > Could you figure out why my PEOPLE sensible heat
gains and occupation
> > seem to start earlier than the 10001 occupation
schedule suggests?
> >
> > The day schedule is set up in 30min intervals. I
have the feeling
> > something is interpolating backwards.
> >
> > Kind regards,
> >
> > jean.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>,
"James V Dirkes II, PE"
> > <jim@> wrote:
> > >
> > > Dear Jean,
> > >
> > >
> > >
> > > A quick review suggests that you look at:
> > >
> > >
> > >
> > > 1. You are using an On/Off fan. The fan
uses an "Always on" schedule,
> > > but the nature of this fan is to cycle on
and off as needed for building
> > > loads.
> > >
> > > 2. You are also using
AvailabilityManager:NightCycle set for
> > > "StayOff". Normally this means that your
fan will never operate at
> > night.
> > > I'm not sure what happens with an OnOff fan
., but you might get rid
> > of this
> > > manager since it does not apply to your
situation.
> > >
> > >
> > >
> > > 3. Finally, you are autosizing minimum
outdoor air in the
> > > Controller:Outdoor Air. I'd be inclined to
set the minimum at a non-zero
> > > value or create a minimum fraction or
schedule for outdoor air.
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > The Building Performance Team
> > > James V. Dirkes II, P.E., LEED AP
> > > 1631 Acacia Drive NW
> > > Grand Rapids, MI 49504
> > > 616 450 8653
> > >
> > >
> > >
> > > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>
> > > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>] On
Behalf Of jeannieboef
> > > Sent: Friday, October 15, 2010 3:46 AM
> > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>
> > > Subject: [EnergyPlus_Support] Re: Schedule
10001 - Output Value is time
> > > shifted
> > >
> > >
> > >
> > >
> > >
> > > Thank you Dr. Li,
> > >
> > > You're right. The only reason the schedule
is "any number" not
> > "fraction"
> > > and this complicated is because this is the
output from
> > designbuilder. I use
> > > the graphics from designbuilder in my
simulation report which
> > explain the
> > > schedule much nicer than the syntax of a
Schedule:Compact object. As
> > to the
> > > time shift...I'm still at a loss. I use
xEsoView to check the
> > outputs in the
> > > eso file. Therefore I specified the
Schedule Output Values for both
> > hourly
> > > and timestep. Looking at the timestep
values I still don't under
> > stand why
> > > it doesn't start with the day schedule
time.
> > >
> > > I've posted the idf in the user exchange
area.
> > >
> > > My other problem is that the specified min
ODA is not happening, and
> > I can't
> > > figure out why (It should be constantly on
night and day).
> > >
> > > Regards,
> > >
> > > Jean
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>