[EnergyPlus_Support] i get this type of error anyone has any idea what I am doing wrong?
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] i get this type of error anyone has any idea what I am doing wrong?
- From: "motabmx1" <motabmx1@xxxxxxxxx>
- Date: Mon, 29 Nov 2010 12:30:59 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Mon, 29 Nov 2010 05:31:12 -0700
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1291033872; bh=gEtNkNIvk5bPlRcc+Oa8IZf+1/TAJ5SsyxT7u+h0C74=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=iqHc965DRMqUvrOQ5b/2z/p0TLFB7u/qAP3+YsezVyxk08bXzgMAAO4BggCtvjNPTdRtIzkR7yCBAOhnaj9Ft4Ww8Fs0FUcY99iRLEq45+NHwj5ygamXTRtVONDAhQBR
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=ZVzafeZHiTR57rlWXczNfc056uyBZciAwH4puaGnhv81eTKu5WGGdW9+CZb6bRUIFsIrBGejj9kqOW3HfWkH8lmsDToeV80ogV8qYJrDjELEgsH27rcIzK/3s0IaGOAa;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
If anyone knows what I am doing wrong in any of this errors can please drop me a line to say how I can solve them
many thanks
Program Version,EnergyPlus 6.0.0.023, 29/11/2010 12:13,IDD_Version 6.0.0.023
** Warning ** No Timestep object found. Number of TimeSteps in Hour defaulted to 4.
** Warning ** No reporting elements have been requested. No simulation results produced.
** ~~~ ** ...Review requirements such as "Output:Table:SummaryReports", "Output:Table:Monthly", "Output:Variable", "Output:Meter" and others.
** Warning ** ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
** Warning ** World Coordinate System selected. Any non-zero Building/Zone North Axes or non-zero Zone Origins are ignored.
** ~~~ ** These may be used in daylighting reference point coordinate calculations but not in normal geometry inputs.
** Warning ** Distance between two vertices < .01, possibly coincident. for Surface=ADF1C2, in Zone=TOILET_CORRIDOR
** ~~~ ** Vertex [3]=(38.50,19.56,0.00)
** ~~~ ** Vertex [1]=(38.50,19.56,0.00)
** Warning ** ProcessScheduleInput: Schedule:Compact="PEOPLE_OFFICE_WEEKDAY_SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_OFFICE_SCHEDULE_dy_1
** ~~~ ** ref Schedule:Compact="LIGHTS_OFFICE_SCHEDULE"
** Warning ** ProcessScheduleInput: Schedule:Compact="LIGHTS_OFFICE_SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=ELEC_EQUIP_OFFICE_SCHEDULE_dy_1
** ~~~ ** ref Schedule:Compact="ELEC_EQUIP_OFFICE_SCHEDULE"
** Warning ** ProcessScheduleInput: Schedule:Compact="ELEC_EQUIP_OFFICE_SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Warning ** ProcessScheduleInput: Schedule:Compact="ACTIVITY_OFFICE_SCH", Schedule Type Limits Name="ANYNUMBER" not found -- will not be validated
** Warning ** ProcessScheduleInput: Schedule:Compact="HEATING-SETPOINT-SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Warning ** ProcessScheduleInput: Schedule:Compact="VENTILATION_ HOURS_OF_OPERATION" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAYS
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_STORAGE_SCHEDULE_dy_1
** ~~~ ** ref Schedule:Compact="LIGHTS_STORAGE_SCHEDULE"
** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_STORAGE_SCHEDULE_dy_2
** ~~~ ** ref Schedule:Compact="LIGHTS_STORAGE_SCHEDULE"
** Warning ** ProcessScheduleInput: Schedule:Compact="LIGHTS_STORAGE_SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_MEETING_ROOM_SCHEDULE_dy_1
** ~~~ ** ref Schedule:Compact="LIGHTS_MEETING_ROOM_SCHEDULE"
** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_MEETING_ROOM_SCHEDULE_dy_2
** ~~~ ** ref Schedule:Compact="LIGHTS_MEETING_ROOM_SCHEDULE"
** Warning ** ProcessScheduleInput: Schedule:Compact="LIGHTS_MEETING_ROOM_SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Warning ** ProcessScheduleInput: Schedule:Compact="ELEC_EQUIP_NON-OFFICE_AREAS_SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Warning ** ProcessScheduleInput: Schedule:Compact="ELEC_EQUIP_MEETING_SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Warning ** ProcessScheduleInput: Schedule:Compact="HEATING-SETPOINT_NON_OFFICES-SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Warning ** ProcessScheduleInput: Schedule:Compact="COOLING-SETPOINT_NON_OFFICES-SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Warning ** ProcessScheduleInput: Schedule:Compact="COOLING-SETPOINT-SCHEDULE" has missing day types in Through=12/31
** ~~~ ** Last "For" field=FOR: SUNDAY
** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
** ~~~ ** Missing day types will have 0.0 as Schedule Values
** Fatal ** ProcessScheduleInput: Preceding Errors cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=6
..... Last severe error=ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_MEETING_ROOM_SCHEDULE_dy_2
************* Fatal error -- final processing. More error messages may appear.
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
************* No node connection errors were found.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 18 Warning; 6 Severe Errors; Elapsed Time=00hr 00min 3.14sec
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/