[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: problem with output cooling/heating loads





thanks for your answer
 
kind regards
 
Fernando


From: Liam O'Brien <liambrn@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Wed, December 8, 2010 3:09:23 PM
Subject: [EnergyPlus_Support] Re: problem with output cooling/heating loads

 

Fernando,

It's certainly possible to have both in the summer. If your heating and cooling setpoints are close together, you could have situations when the cooling system keeps the temperature moderate during the day and then as the outdoor temperature drops at night, heating may be required.

If *apparent* simultaneous heating and cooling are being reported for a single zone, this indicates that your reporting frequency is lower than the time step frequency. This can be misleading...

If you want to prevent heating in summer, play with the schedules (e.g., set heating setpoint in summer to something ridiculously low).

Hope that helps,

Liam O'Brien

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "motabmx1" <motabmx1@...> wrote:
>
> Hi all,
>
> I am not sure if i am undestanding the data output correctly or not. I am getting cooling loads, only during the months of summer (uk location)
> however, I am getting heating loads in all the months of the calendar, I thought that when my HVAC idealsystem is providing cooling, the heating system should have 0 values. Can anyone there clarify this, and tell me what i am doing wrong
>
> many thanks again
>
> fernando
>




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___