Re: [EnergyPlus_Support] A possible bug or I am doing somethinh wrong





Note that it is using your calculated volumes, not the ones it calculates.

The volume calculation is quite robust but may not be accurate for non-enclosed zones.

If you enter:
SHOWZONESURFACES_DEBUG;

into your idf it also should show some debug outputs on the .dbg file

At 07:01 AM 12/11/2010, motabmx1 wrote:
Hi all, I found that my eio file is providing me wrong room volumes. I created the iDF file in energy plus with relative coordenates. I put the name to the IDF and then I did the geometric in open studio. I checked all zone coordenates and they are all the same in both programs (energy plus and open studio). I run the simulation in energy plus,0 warnings, 0 severe erros, 0 fatal erros. Them I checked my eio file and I found that energy plus is calculating volumes much higher that the ones I obtain by doing it by hand. Anyone there has come across anything similar?


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___