The model for surface heat transfer in EnergyPlus is not what you seem to imagine. Trying to assemble an internal reflective cavity using Construction and Material objects does not work. You would need to develop equivalent properties for that portion of the assembly and collapse them into a single Material layer.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of reza m
Sent: Sunday, December 12, 2010 8:15 AMSubject: Re: [EnergyPlus_Support] problem with thermal radiation
i saw many details that they use 3 or 4 metal layers with foam as insulation layers.
On Sun, Dec 12, 2010 at 4:09 PM, Griffith, Brent <brent.griffith@xxxxxxxx> wrote:
Your metal layers are inside the construction and will not do anything to affect thermal radiation. Only the first and last Materials affect the surface radiation properties of the Construction.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of reza m
Sent: Saturday, December 11, 2010 4:31 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] problem with thermal radiation
Hi,
I investigate on thermal radiation and its effects
I have two alternative materials
1- external wall ( with two metal layers)
2- external wall2 (with out metal)
The difference between two simulations was very poor and thermal radiation energy loos by the wall that has this material wasn't change.
A9C38D:Surface Ext Thermal Radiation Heat Loss to Outdoors [kWh](Monthly)
with out Reflector
with Reflector
January
108.8691475
108.8541296
February
128.5922864
128.6258381
March
251.0705809
250.9363295
April
395.7446768
395.1045226
May
566.9424429
567.0461548
June
587.9205448
587.9979196
July
638.0636581
638.0444506
August
516.8364084
516.6539877
September
348.7579962
348.6593856
October
215.2195033
215.3210677
November
122.2107265
122.2722356
December
90.07916896
90.1409641
do you have any idea?
what should i do to have better result for radiation
i attached my IDF file
thank you in advance for your time
REZA
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___