Jason,
Thanks for the suggestions. Tried those output objects before, but
they report only to the building surfaces and fenestrations, not to
the window shading devices. As for the hand calculation, its
something i've thought about, but i'm not sure what to do with the
temperature difference in that object you mentioned, since the
absorbed heat by the shading is in the form of radiation (mostly at
least, the air temperature wont be higher than the shading during
the day), i would need an equivalent temperature for that dT. I was
thinking about using these objects instead:
Window Convection Heat Gain from Shade to Zone [W]
Window Net Infrared Heat Gain from Shade to Zone [W]
I think it sums up the heat exchange between the zone and the shade,
and from here apply the m Cp dT relation, with dT between zone air
and shading. what you think?
BTW, i got a response from the authors of that paper that sparked
all this: they say they obtained the temperature values of the
blinds from the surface inside temperature object, using V4.0. maybe
such a report was available on that version?
Pedro
On 13-01-2011 18:09, Jason Kirkpatrick wrote:
Pedro,
Will any of these work for what you are trying to
accomplish?
Output:Variable,*,Surface Inside Temperature,hourly; !-
Zone Average [C]
Output:Variable,*,Surface Outside Temperature,hourly; !-
Zone Average [C]
Output:Variable,*,Surface Int Adjacent Air
Temperature,hourly; !- Zone Average [C]
If not, maybe you could take the following output
Output:Variable,*,Window Solar Absorbed:Shading Device
Energy,hourly; !- Zone Sum [J]
and calculate the temp by hand as Q = m C dT
where Q is energy absorbed by shade, m is mass of shading
system, C is specific heat of material dT is change in
temp
Hope this helps,
Jason
On Thu, Jan 13, 2011 at 7:44 AM,
Pedro Peixeiro <ppeixeiro@xxxxxxx>
wrote:
Hope so, even if its just a confirmation
that it cant be reported. I've read recently a
paper with results on shading temperature,
wich just makes things a bit more strange.
I've asked the authors about it, still waiting
on an answer.
Pedro
On 13-01-2011 12:31, James V Dirkes II, PE
wrote:
Dear Pedro,
I do not know how to
monitor the temperature of an internal
surface. I doubt that it can be
done. Perhaps others in the forum
have an idea?
The Building
Performance Team
James V.
Dirkes II, P.E., LEED AP
1631 Acacia
Drive NW
Grand Rapids, MI 49504
616 450 8653
James,
I'm not looking for an air
temperature. I was searching for
the actuall temperature of the
shading system (blinds) mounted on
some of my glazings. I'm not using
any mechanical system, just
natural ventilation. If you feel
your answer is still correct, then
i dont see what you mean. if you
could please explain it a bit
further i would be very grate
full. thank you
Pedro.
On 12-01-2011 14:28, James V
Dirkes II, PE wrote:
Dear Pedro,
The air
temperature that you
want is present at a
node in your air loop.
Just ask for that node’s
temperature to be
reported!
The
Building Performance
Team
James
V. Dirkes II, P.E.,
LEED AP
1631 Acacia
Drive NW
Grand Rapids, MI 49
504
616 450 8653
Hello everyone.
I went searching the I/O
reference for a
temperature outp ut
object for a window
blind shade system, but
for my surprise i didnt
find one. Is there
really no output for
this, or am i missing
something? thank you for
any help you can give.
Regards,
Pedro
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at: