Hi,
Brendan. I
don't have a specific answer that solves your issue. I don't know either what to
do when you get this error message when your capacities and airflows have
already been sized. I hope some of this additional information helps and I
wish you the best: Error Message: "rated air volume flow rate,
total cooling capacity and sensible heat ratio yields coil exiting air
conditions above the saturation curve. Possible fixes are to reduce the rated
total cooling capacity, increase the rated air volume flow rate, or reduce
the rated sensible heat ratio for this coil. If autosizing, it is
recommended that all three of these values be autosized." Design Builder Help: - HVAC Sizing : Compact "Tip: If you are using the Manual
sizing option together with Compact HVAC and wish to use different cooling
sizes to those obtained from looking at the output of previous EnergyPlus autosizing calculations (e.g .
from eplusout.eio) you will need to ensure that
the maximum supply flow is changed accordingly. If you increase the maximum
cooling capacity but don't increase the Maximum supply flow rate (or even leave
it as Auto) you will get "Rated air volume flow rate per watt of rated
total cooling capacity is out of range" errors in the EnergyPlus
simulation because the cooling capacity requested cannot be achieved with the
specified air flow rate. Also due to a quirk in EnergyPlus, the Auto Maximum
supply flow rate option does not work well with Manual sizing option and
automatically calculated Maximum supply flow rates do not account for the
'higher than autosized' cooling capacity requested." You might want to check these
related previous E+ Yahoo Entries: Francisco Minoyetti: Sustainability Assistant - Energy
Simulation: Bovis Lend
Lease S.A. El presente correo electrónico y sus archivos adjuntos son
confidenciales. Si Usted no fuere el destinatario original del presente correo
por favor tenga a bien notificárnoslo respondiendo este e-mail a la dirección
del remitente, y proceda inmediatamente a borrar toda copia de este mensaje. La
copia o uso de la presente comunicación, o de la información que ésta contenga,
se encuentra estrictamente prohibido. Muchas gracias. This email and any attachments are confidential. If you are not
the intended recipient please notify us by reply e-mail and immediately delete
all copies of this message. Copying or use of this communication or the
information in it is strictly prohibited and may be unlawful. Thank you. 2011/2/9
bcmcgr <bcmcgr@xxxxxxxxx> "Rated air volume flow
rate per watt of rated total cooling capacity is out of range." __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |
Attachment not found: C:\Users\lklawrie\Downloads\Embedded\image00181.png
Attachment not found: C:\Users\lklawrie\Downloads\Embedded\image00225.png