[EnergyPlus_Support] Re: Warning Message: air volume flow per cooling capacity out of range



All,

I was able to get the model to run when I changed the "Rated Air Flow Rate" for each of the 5 coils.

I'm now getting a lot of errors - 950,000.

example:

   *************  ** Warning ** Coil:Cooling:DX:SingleSpeed "9085 AHU COOLING COIL" - Air volume flow rate per watt of rated total cooling capacity is out of range error continues...
   *************  **   ~~~   **   This error occurred 228990 total times;
   *************  **   ~~~   **   during Warmup 0 times;
   *************  **   ~~~   **   during Sizing 0 times.
   *************  **   ~~~   **   Max=2.055983E-005  Min=1.922954E-005
   *************
   *************  ** Warning ** Coil:Cooling:DX:SingleSpeed "9085 AHU COOLING COIL" - Full load outlet temperature indicates a possibility of frost/freeze error continues. Outlet air temperature statistics follow:
   *************  **   ~~~   **   This error occurred 10568 total times;
   *************  **   ~~~   **   during Warmup 0 times;
   *************  **   ~~~   **   during Sizing 0 times.
   *************  **   ~~~   **   Max=1.99968  Min=-11.578451

As  you can see, none of these errors occur during "warmup" or "sizing". 

I don't know that there's a way to get rid of these errors with the "work around" that I'm using. I also looked at the outputs of the model and it doesn't seem to be effecting the outputs. Can anyone offer guidance?

Thanks again.

Brendan

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "bcmcgr" <bcmcgr@...> wrote:
>
> Don,
> 
> I do have coils:cooling:DX:Singlespeed. I have 5 of them. In this case the "Rated Total Cooling Capacity" is a set number (Watts) but the "Rated Air Flow Rate" is "autosize". This is why I was drawn to changing the infiltration input, as it was a set number.
> 
> I'll try changing this number to get the model to run right.
> 
> Brendan
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Don Shirey <shirey@> wrote:
> >
> > "ZoneInfiltration:DesignFlowRate"  defined infiltration of outdoor air into the zone... that is not the issue here.
> > 
> > You must have a DX cooling coil object somewhere in your EnergyPlus 
> > input data file, don't you (Coil:Cooling:DX:*) ?
> > 
> > It has rated airflow rate and rated capacity inputs.
> > 
> > 
> > On 2/10/2011 3:28 PM, bcmcgr wrote:
> > > James,
> > >
> > > Basically what I was asking was that if I could just change the  "Zone Airflow" ->  "ZoneInfiltration:DesignFlowRate" to make the (m3/s)/W fall within the range stipulated by E+. In the E+ idf file that is the only location that I can find to change the supply flow. It seems to be where E+ pulls it from DB.
> > >
> > > I was able to change those values iteratively to get within the range and keep my heating and cooling capacities at actual size.
> > >
> > > Is there another place within E+ to modify the "supply air flow rate"?
> > >
> > >
> > > Brendan
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/