"ZoneInfiltration:DesignFlowRate"  defined infiltration of outdoor air into the zone... that is not the issue here.

You must have a DX cooling coil object somewhere in your EnergyPlus 
input data file, don't you (Coil:Cooling:DX:*) ?

It has rated airflow rate and rated capacity inputs.


On 2/10/2011 3:28 PM, bcmcgr wrote:
> James,
>
> Basically what I was asking was that if I could just change the  "Zone Airflow" ->  "ZoneInfiltration:DesignFlowRate" to make the (m3/s)/W fall within the range stipulated by E+. In the E+ idf file that is the only location that I can find to change the supply flow. It seems to be where E+ pulls it from DB.
>
> I was able to change those values iteratively to get within the range and keep my heating and cooling capacities at actual size.
>
> Is there another place within E+ to modify the "supply air flow rate"?
>
>
> Brendan


------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/