Re: [EnergyPlus_Support] EMS temperature control





Very nice drawing.

The heat pump water heater already has a deadband, but of course this is not based on zone temperatures, but a fixed schedule. The mixed water heater also has a schedule and a deadband, and if the water temperature falls below the tank's schedule value minus the deadband, the 12kW electric heater will turn on in the tank.

WaterHeater:HeatPump,
    Heat Pump Water Heater Plant,  !- Name
    HP on/off,               !- Availability Schedule Name
    HPWH HW SP AN,           !- Compressor Setpoint Temperature Schedule Name
    2.0,                     !- Dead Band Temperature Difference {deltaC}

WaterHeater:Mixed,
    HPWH Tank,               !- Name
    0.00379,                 !- Tank Volume {m3}
    HPWH TANK HW SP AN,      !- Setpoint Temperature Schedule Name
    2.0,                     !- Deadband Temperature Difference {deltaC}

Since you do not have report variables for the mixed water heater in your input file, I wonder if you actually know what is heating the tank. What is the tank temperature? Is it 55? or 60? Your actually not reporting anything of value and do not know what is happening in your simulation. How can you possibly debug your simulation?

In addition, how is the zone temperature going to rise above the set point when you still have hot water in the tank. The baseboards will continue to supply heating to the zones until the tank temperature falls to some low temperature. After that the zone temperature will rise, and THEN you want your HPWH to turn on?

The first thing I would do is add more report variables (see the rdd file) to see what is happening.
The next this I would do is disable the electric element in the tank (set it to 0kW) if your tricking the HPWH to act on EMS programming. You could also control the tank hot water temp schedule with the EMS if you didn't want to disable the electric element (set it very low until you want the electric element to turn on).

P.S. most users on this yahoo site will not or can not help you with more complex input files. This question is more geared towards an Energyplus Helpdesk question. But do your homework before asking for help from that site. If you send this same email and input file to that site without modification, I will give you the same answer I gave you here. Add more report variables and try to figure out what is happening with your simulation.

To access the help desk, send your email and input file to:

energyplus-support@xxxxxxxx or go to http://energyplus.helpserve.com/


On 2/24/2011 1:09 PM, John Kirby wrote:
 

Hi.

I am using EMS to control the on/off status of a heat pump. I have sensors for each Zone Mean Air Temperature. I also have a sensor for the heating setpoint defined in the schedules(It is set @ 22 degrees for each period ) .The Zone Mean Air Temperature output variable of Zone3 is being compared against the heating setpoint to decide whether or not to turn the heat pump on.

The program defines the turn on point as the heating setpoint, and the turn off point as the heating setpoint + Toffset. The actuator is set up so for on/off supervisor control to actuate the heating loop.

The program is having no influence on the output temperatures. The EDD file suggests that the program recognizes the heating setpoint ( 22 and 24). I am confident that the Actuator is set up correctly but results suggest that it is not doing what it is meant to do.

It is a very simple program, but after discussing with a colleague over the last couple of days we have been unable to get it to work. I attached the idf file. I have also attached a diagram of the heating loop being used. If anyone has any suggestions I thank you in advance.

Kindest Regards

John Kirby



-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___