Re: [EnergyPlus_Support] Re: Design Day





The ddy file won't be empty -- it will at least have the location in it.

You can look at the stat file that is included with the zip -- if there was no ASHRAE location for your weather, then there will have been a statistical "guess" included in the stat file -- based on the weather data.

Or, you can look at a location near yours and tweak their design day conditions to more match yours.

In the macro data sets folder, there is a spreadsheet "locations-designdays" and it contains links to design day definitions for all the ASHRAE 2009 HOF sets.  (by WMO region).  You can download these and then use the guidelines that Jim provided for the IDF Editor.

At 12:05 AM 3/5/2011, quad_nich wrote:

I can't find the content of .ddy file in my country's weather data that I request from E+ ( .ZIP ),, it is empty..


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___