|
Hi Jan. Check you setpoint manager, seems to me you're trying to control the temperature on outletpipe_out to 1ºC by using the Baseboard Operation Schedule. what you need here is a temperature schedule for that node. Also, seems to me you try to use the normal setpoints in the zones to control the radiant units. you'll need to do the controlling of each unit on the Heating Control Temperature Schedule Name in each of these objects. Again, you had the Baseboard Operation Schedule, and its expecting a temperature schedule. couldnt do a run to confirm that these were the problems. hope it helps. Pedro. On 25-03-2011 12:20, energyplus_problem wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17180) http://www.pctools.com ======= |