[EnergyPlus_Support] Re: No water flow with underfloor heating system
That was it! Thank you very much!
Jan
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Pedro Peixeiro <ppeixeiro@...> wrote:
>
> Hi Jan.
>
> Check you setpoint manager, seems to me you're trying to control the
> temperature on outletpipe_out to 1ºC by using the Baseboard Operation
> Schedule. what you need here is a temperature schedule for that node.
>
> Also, seems to me you try to use the normal setpoints in the zones to
> control the radiant units. you'll need to do the controlling of each
> unit on the Heating Control Temperature Schedule Name in each of these
> objects. Again, you had the Baseboard Operation Schedule, and its
> expecting a temperature schedule.
>
> couldnt do a run to confirm that these were the problems. hope it helps.
>
> Pedro.
>
>
> On 25-03-2011 12:20, energyplus_problem wrote:
> >
> > Here is the error file, but there is nothing that has to do with my
> > problem I think
> >
> > ** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall
> > outside the range of 15-25C.
> > ** ~~~ ** These values may be inappropriate. Please consult the Input
> > Output Reference for more details.
> > ** Warning ** Weather file location will be used rather than entered
> > Location object.
> > ** ~~~ ** ..Location object=SUSTEN
> > ** ~~~ ** ..Weather File Location=Visp Valais CH Custom-67270 WMO#=67270
> > ** ~~~ ** ..due to location differences, Latitude difference=[38.38]
> > degrees, Longitude difference=[38.79] degrees.
> > ** ~~~ ** ..Time Zone difference=[0.0] hour(s), Elevation
> > difference=[0.00] percent, [0.00] meters.
> > ** Warning ** GetSolutionAlgorithm: HeatBalanceAlgorithm Algorithm is
> > Conduction Finite Difference but Number of TimeSteps in Hour < 20,
> > Value is 6.
> > ** ~~~ ** ...Suggested minimum number of time steps in hour for
> > Conduction Finite Difference solutions is 20. Errors may occur.
> > ** Warning ** CalcSurfaceCentroid: 3 Surfaces have the Z coordinate < 0..
> > ** ~~~ ** ...in any calculations, Wind Speed will be 0.0 for these
> > surfaces.
> > ** ~~~ ** ...in any calculations, Outside temperatures will be the
> > outside temperature + 9.750E-003 for these surfaces.
> > ** ~~~ ** ...that is, these surfaces will have conditions as though at
> > ground level.
> > ** Warning ** Calculated design cooling load for zone=EG ZONE is zero..
> > ** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
> > ** Warning ** Calculated design cooling load for zone=OG ZONE is zero..
> > ** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Ehsan Baharvand
> > <ebaharvand@> wrote:
> > >
> > > Hi,
> > >
> > > Did you look in the ERR.file? Are there any errors or warnings?
> > >
> > > Kind regards,
> > > Ehsan
> > >
> > >
> > >
> > >
> >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/
=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17190)
http://www.pctools.com/
=======