|
If you have two pipe fan coil in each zone, you will need seasonal control, and choose the correct thermostat control to match the seasonal value. The connection and the master thermostat sharing problem is not resolved by this fan coil change. CBVAV, ChangeOver VAV as an independent temperature controlled fresh air loop may help. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: vieira.jose99@xxxxxxxxx Date: Fri, 15 Apr 2011 12:03:15 +0000 Subject: [EnergyPlus_Support] Re: Zone FanCoils and an AHU
Looks like I really need some help.
Can someone please explain how do you put an AHU for fresh air for various zones and in each zone there is a 2 pipe FanCoil for air temperature control? I have been trying to put a AirTerminal:SingleDuct:Uncontrolled and a ZoneHVAC:FourPipeFanCoil in the same zone. The air flow rate on the singleduct:uncontrolled is zero!?. I have both equipments in the same colum in ZoneHVAC:EquipmentList. Thank-you --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote: > > > Hi, Vieira > I have looked at your IDF. It is for an hospital. > Hospital had different fresh air requirement and filtering requirement for the operating theaters. > I was involved in the design of the air-conditioning requirement of the hospital building of the Faculty of Medicine in Kuala Lumpur, Malaysia. It was in 1967/9 period. I was not the designer and was in the reviewer capacity for the University. > I have not been following the advances in this field. If you are designing a new hospital, you may need to look at any new requirements not to mix up the air from different areas of the hospital units. > That means that more then one AHU unit are required, and each one may be required to have fresh air and return air filtering unit and tighter temperature and humidity control at the feeding duct to the diffuser unit. > > Dr. Li > > > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > From: vieira.jose99@... > Date: Thu, 14 Apr 2011 16:20:08 +0000 > Subject: [EnergyPlus_Support] Zone FanCoils and an AHU > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Hello, first I want to thank all that helped me understand a little better E+ on this previous topic: http://tech.groups.yahoo.com/group/EnergyPlus_Support/message/19759 > > > > Now I have a 74 zone building and want to simulate one AHU to "treat" the minimum new air for occupancy for all the zones and use FanCoils to "treat" the air temperature so that mean air temperature of the zones are 20ºC for winter and 25ºC for Summer. > > > > What i am tring: Air from the AHU splits to the various zones, then it enters the zone FanCoil, the return air from the zones goes back to the AHU for later on apply recovery mechanisms. > > > > For now I am only looking to do this on two zones, so that it is easier to correct mistakes, then when it is working, its easier to do copy/paste for the other zones. For now I am also simulating for the summer design day. > > > > The problem is that the mean air temperature is outragous, it is above 40ºC for the summer design day. There was no return air from the zone to the AHU, the air was being released by the FanCoil relief outlet node, so I hooked that node up to the air mixer, so that it would return to the AHU. > > > > I have uploaded the .idf to the problem submital section, the link is: > > > > http://f1.grp.yahoofs.com/v1/ABqnTWqT74N-28mPIl7kRupySkocrpNc68HOk3a6kHyyGzAmoXDeVi-g1ZaLd_Xwt1650MFZVHq1eZm43mA1RYZJNQxC15tMDPG-/_Problem_Submittals/Sim1_sem_recuperacoes_duas_zonas.zip > > > > I have put two other zones with the FanCoil HVAC template, so I may make comparisions and later on try to modify it. > > > > The air temperature leaving the AHU must be in the 20/25ºC range, only the FanCoils will warm/cool the zone air. > > > > Can someone point me in the wright direction? What is it that is not working here? > > > > Thank-you > > Best Regards, > > Vieira > __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups..yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320) http://www.pctools.com ======= |