[EnergyPlus_Support] Re: Controlling windows in one zone based on the temperature of a non-adjacent zone





Lixing:

 

Thank you very much for your reply. I will definitely try to use EMS. However, I would like to know if using the AvailabilityManager:HybridVentilation might help. I was intending to use the HVAC template objects to define an HVAC system to cool the PDEC zone and use the AvailabilityManager:HybridVentilation to control its operation. I was wondering if it is possible to input the name of this HVAC system serving the PDEC zone in the HVAC Air Loop Name Field while using the OFFICE zone as input in the Controlled Zone Name Field. In other words, can the zone controlling the HVAC system be different from the zone served by the that same system?

 

Thanks

Omar

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lixing Gu <gu@...> wrote:
>
> Omar:
>
> The existing controls could not meet your requirements. A possible way is to
> try EMS. Please read manual EMS_Application_Guide.pdf for further guide.
>
> Thanks.
>
> Lixing
>
>
>
>
>
>
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of omarvelling
> Sent: Wednesday, April 20, 2011 12:06 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Controlling windows in one zone based on the
> temperature of a non-adjacent zone
>
>
>
>
>
>
>
>
> Hello,
>
>
>
> I was wondering if it is possible to control the opening/closing of windows
> in one zone based on the temperature of another zone in the model not
> adjacent to the first. This is because I'm trying to emulate passive
> downdraught evaporative cooling (PDEC) in a multi-storey office building.
> For Simplicity, I'm starting with a single office floor model that consists
> of three zones; a PDEC zone, an ATRIUM zone (spanning three floors in
> height), and an OFFICE zone. I've uploaded a schematic of the model to the
> user exchange folder in the files section:
>
>
>
> http://f1.grp.yahoofs.com/v1/AAOvTY7uC2gK0JzgM4fCqonvr5UhhE0zFSEcx75GgblUJLm
> GfFFv6FPpX9tGOyapgd-lSSBv6Xne-QLj5YFwHR_7XAmrtITcFA/User%20Exchange/Controll
> ing%20vents.jpg
>
>
>
> The temperature of the PDEC zone is controlled using
> ZoneHVAC:IdealLoadsAirSystem with a setpoint that changes each hour as a
> function of the difference between the external dry bulb temperature and the
> wet bulb depression to emulate the evaporative cooling process. The PDEC
> zone is located at the upper end of the ATRIUM's north wall while the OFFICE
> zone lies at the lower end of the ATRIUM's south wall. The ATRIUM is
> connected to the two zones by vertical interior windows. The PDEC and OFFICE
> zones have exterior windows on the walls opposite to the atrium, i.e. the
> PDEC zone has a north exterior window while the OFFICE zone has a south
> exterior window. The ATRIUM also has an exterior window at the upper end of
> its south wall, i.e. opposite the interior window connecting it to the PDEC
> zone.
>
>
>
> The intended flow pattern is such that external air flows into the PDEC zone
> where it is cooled, then into the ATRIUM where it flows downwards (due to
> negative buoyancy) and finally through the OFFICE where it exits the
> building from the exterior window at its south wall..
>
>
>
> What I'm trying to achieve is to control the opening at the PDEC/ATRIUM
> interface

__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17350)
http://www.pctools.com
=======