Robin, please note that inside EnergyPlus, the calculations are based on mass flow rate. The input design volume flow rates are converted to design mass flow rates using a standard density (but with an altitude adjustment). So even though the models might be referred to as constant volume, they are really constant mass flow rate. The volume flow rates are available for reporting but are derived from mass flow rates and available with two different options for density. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of rgen1202 Lixing, Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.