Oops. Wherever I refer to “captured” and “exhausted”, it should be “Not captured” and “exhausted” The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of James V Dirkes II, PE Dear All, Here are a few additional thoughts: · If the “mist” actually contains water (as opposed to oil), Ned is exactly correct that the effectiveness of the mist capture can be significant. If the capture rate is 80%, 20% of the moisture will become part of the zone and you are interested in accounting for that impact. Therefore you need to know (a
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.