You cannot use OtherSideCoefficients with Windows.  However, you can use them with doors.  I'd create a material/construction that is approximately the same U Value as your window and call it a door.

Light will not transmit through there, of course, but you will be able to put your temperature profile in.

At 05:02 AM 7/1/2011, gerardmor wrote:
Hi, I'm Gerard Mor, a beginner user in EnergyPlus, I'm doing a calibration of a building that I was simulated in EnergyPlus. Briefly, I want to know if I can put a Outside Boundary Condition like OtherSideCoefficient or similar in a FenestrationSurface object (a window).