Dear Jean, · If the model is NOT affected significantly by incident solar radiation on internal walls, I just add InternalMass in each zone of an amount the same as the internal walls. You need a wall Construction of the right materials and a rough measurement of the area. (Area must be doubled if both surfaces of the wall are exposed to the zone) · If the model IS affected significantly by incident solar radiation, I add the walls in the model. o This is something of a judgment call! · When combining multiple floors (e.g., floors 2-9 for a 10 story building), make sure you have the floor constructions properly accounted for. · Furnishings and equipment are a bit more of a judgment call, since their mass varies so much. My approach is to make sure I’ve got the walls accounted for and then add 10-20% for furnishings, depe
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.