Silvana, The limits on the Area/Perimeter ratio are related to the auto-gridding algorithm. The alternative is to manually specify the grid. If you use this approach, keep in mind that there is a numerical limit on the size of the cells to ensure a stable solution. Neal Kruis From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Silvana Flores I'm studying the physical model behind the slab preprocessor. It was hard to find information about it, particularly why the aspect ratio Area/Perimeter shoul be higher than 1.5. I've read the Bahnfleth model and I didn't find limitations to A/P. The Eplus Manual does not comment anything on this subject. Does it come from grid limitations, or from the thermal model? Would this imply that for a 5m x 5m prototype I cannot use the slab preprocessor? Thank you very, very much. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.