For direct-expansion cooling, packaged and split system simulations: HVACTemplate:Thermostat
HVACTemplate:Zone:Unitary HVACTemplate:System:Unitary I think this grouping provide both cooling and heating in the system:Unitary. The Zone Unitary can provide additional heating. Therefore the use of availability schedules must be very carefully considered. In the IDF, the cooling is always ON. Then what happens, when heat is required? The expIDF did provide type 4 thermostat for you. I am surprised that the use of Weekdays twice in the following schedule did not produce a warning. The schedule should be split into Summer and Winter seasons. Schedule:Compact, Minimum Outside Air, !- Name Fraction, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: Weekdays SummerDesignDay, !- Field 2 Until: 24:00, 1, !- Field 4 For: Weekends WinterDesignDay Holidays AllOtherDays, !- Field 5 Until: 24:00, 0; !- Field 7 Because the expIDF used the template schedule, I think the above was not used. I think the expandIDF knows the preferred conditions and corrects them.================ HVACTemplate:System:Unitary, UnitarySystem4, !- Name School HVAC, !- System Availability Schedule Name Zone 4, !- Control Zone or Thermostat Location Name 0.708, !- Supply Fan Maximum Flow Rate {m3/s} continuous, !- Supply Fan Operating Mode Schedule Name 0.6, !- Supply Fan Total Efficiency 250, !- Supply Fan Delta Pressure {Pa} 0.9, !- Supply Fan Motor Efficiency 1, !- Supply Fan Motor in Air Stream Fraction SingleSpeedDX, !- Cooling Coil Type Always_On, !- Cooling Coil Availability Schedule Name 13130, !- Cooling Coil Capacity {W} autosize, !- Cooling Coil Rated Sensible Heat Ratio 3.6635, !- Cooling Coil Rated COP {W/W} Gas, !- Heating Coil Type , !- Heating Coil Availability Schedule Name 16120, !- Heating Coil Capacity {W} 0.8, !- Gas Heating Coil Efficiency , !- Gas Heating Coil Parasitic Electric Load {W} autosize, !- Maximum Outdoor Air Flow Rate {m3/s} 0.22656, !- Minimum Outdoor Air Flow Rate {m3/s} Minimum Outside Air, !- Minimum Outdoor Air Schedule Name DifferentialDryBulb, !- Economizer Type NoLockout, !- Economizer Lockout 25, !- Economizer Upper Temperature Limit {C} , !- Economizer Lower Temperature Limit {C} , !- Economizer Upper Enthalpy Limit {J/kg} , !- Supply Plenum Name , !- Return Plenum Name BlowThrough, !- Supply Fan Placement StayOff, !- Night Cycle Control , !- Night Cycle Control Zone Name None, !- Heat Recovery Type 0.7, !- Sensible Heat Recovery Effectiveness 0.65, !- Latent Heat Recovery Effectiveness , !- Dehumidification Control Type , !- Dehumidification Control Zone Name , !- Dehumidification Setpoint {percent} , !- Humidifier Type , !- Humidifier Availability Schedule Name , !- Humidifier Rated Capacity {m3/s} , !- Humidifier Rated Electric Power {W} , !- Humidifier Control Zone Name ; !- Humidifier Setpoint {percent} ============================ Some of the numbers are modified by the template expension. I have not look into the expanded version yet. Because you are using multiple origines for the zones geometry, I have not b een able to associate the zone names with the room location yet. There are 6 zones, but the roof is divided into 8 parts. The modified air flowrate by the template schedules may have changed your design values. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: zqianmin@xxxxxxxxx Date: Fri, 8 Jul 2011 12:54:43 -0700 Subject: Re: [EnergyPlus_Support] Extremely high user design load for heating for HVAC system 3
yea, I found out the user design value are closed to my input.
Like what I said, it is a finished design project, so I will assume they selected the correct equipment based on their calculation. But from energyplus hvac summary report, the calculated design air flow is about 400cfm, which is too small compared to the equipment of 1800cfm for a 800ft^2 class room. Above is for zone cooling. For zone heating, the calculated design air flow are less than 70cfm for each classroom zone.
On Fri, Jul 8, 2011 at 12:14 PM, Jason Kirkpatrick <jason.alan.kirkpatrick@xxxxxxxxx> wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |