The first part-load ratio I see is 0.43. This means that the AC ran 43% of the time. Or the load is 43% of the AC system capacity. So the unit is cycling on (43% of the time) and off (57% of the time). When the building loads get smaller, the PLR will be smaller. In summer, the PLR should approach 1 if you have the correct size system. Anything around 0.9 is about right. Also change your reporting frequency to match the other report variables. Use Timestep instead of Hourly. On 7/11/2011 1:50 PM, Aditya Ravi wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.