PLR = Load/Capacity. RTF tells you how long the system has to operate to overcome cycling losses. When an AC system starts, it takes a few minutes for the capacity to get up to full output. This is the "losses" I describe, the system started but the capacity wasn't fully there for a few minutes. The RTF is usually a few percent larger than PLR because the system has to operate a little longer to get the capacity to the zone. RTF is only used to calculate energy use. For example PLR=0.43 and RTF = 0.48. The load is 43% of the capacity, or the system ran 43% of the time. To calculate power we look at RTF and it says the system needed to operate 48% of the time (the system had to run 5% longer because the system did not provide full capacity when it started). Your input file is fine unless you want to change schedules or lighting/equipment loads or something like that. On 7/11/2011 2:33 PM, Aditya Ravi wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |