[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: Design Day V.S. Schedule





huh,,I didn't see any attachment.


On Thu, Jul 14, 2011 at 3:52 PM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 

For sizing maximum, there are  csv files with sz in the file name.

QMZ_DD_skylightSsz.csv   for system sizing.

QMZ_DD_skylightZsz.csv   for zone sizing.

 
 Dr. Li  

 


Date: Thu, 14 Jul 2011 15:45:34 -0700

Subject: Re: [EnergyPlus_Support] Re: Design Day V.S. Schedule

 
Oh, got it! So this number is kind of useless to size the hvac system. I didn't realize they are averaged number before. What I want to look at are the number in .csv file. Thank you!
Qianmin



On Thu, Jul 14, 2011 at 3:20 PM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 


If you referring the table result:

FENESTRATIONSURFACE:DETAILED 24
 
These are monthly averaged values.
 
You know that the daily response has a half sinewave shape.  The value is the transmitted value.   There are day to day variations due to weather condition.  The sun rise and sun set time is also changing.  June 21 is the longest day of the year.
 
Therefore,the monthly averaged value is always less than the max. hourly value in the CSV.
That was why I mentioned that I did not see the angle between the surface normal and the sun in your calculation.  This angle controls the value in the CSV and is changing daily at solar noon.
 
 Dr. Li  

 
Date: Thu, 14 Jul 2011 14:42:36 -0700

Subject: Re: [EnergyPlus_Support] Re: Design Day V.S. Schedule

 
Zone 6 has two same skylight, fenestration surface: 23 and 24 

I run the simulation to a year period, in my table report, window report monthly, for fenestrationsurface:detailed 23, the one in zone 6 has

max WINDOW HEAT GAIN [W]: 403.85 in Jun, which is higher than it in July

in .csv file, 
ZONE 6:Zone Window Heat Gain[W](Hourly): 3883.43 @ 13:00

I don't understand why the zone window heat gain in .cvs of 3883.43W/hr doesn't equal or close to 2 x 403.85W

there are only two skylight in zone 6. I didn't count other fenestration since they are all shaded in summer time, and won't contribute a lot at here, I assume...

Any opinion? Thanks.

Qianmin


On Thu, Jul 14, 2011 at 1:40 PM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 


Zone 6 is facing South.

Earth tilt, latitude and roof tilt together may still an angle intensity reduction for that skylight on a Summer day. 
I only did a sizing DesignDay simulatin, and should  have max values in the sizing table.
 
Zone window heat gain includes all windows, and is not the beam transmission value through one sky light.
 
So you may be comparing different numbers. Your window names are all mixed, so I do not know which is which.  The OpenStudio could not give me the window ID's.
 
In the HTML report summary choose  Jtokwh  instead of IP would give you the results in metric format.
 
 Dr. Li  

 

Date: Thu, 14 Jul 2011 12:03:43 -0700

Subject: Re: [EnergyPlus_Support] Re: Design Day V.S. Schedule

 
Dr. Li,

Thanks a lot. These additional objects come from openstudio template... I'll read your results carefully.

From my result variable, ZONE 6:Zone Window Heat Gain[W](Hourly) is 2959.68 at 07/31  13:00:00, which match the value of my hand calculation.
But, just in result table(html), WINDOW HEAT GAIN [Btu/h] max is 1380.75 for one skylight of 26ft2, which is about 1/3 of my hand calculation
zone 6 has two skylight, 

I'm working on unit conversion now, and will run a simulation without unit conversion to check the number.

Regards,
Qianmin



On Thu, Jul 14, 2011 at 11:24 AM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 


You have 500 unused material and constructions in your IDF.  The attached IDF has been sorted and report variables added and deleted.
 
See whether the result in the csv files are reasonable.

 Dr. Li  

 
Date: Thu, 14 Jul 2011 10:08:48 -0700

Subject: Re: [EnergyPlus_Support] Re: Design Day V.S. Schedule

 
I choose " Run simulation for weather file run periods"

Here is the equation used to calculated window solar incident:

window_transmitted_hg = tau_D * E_D + tau_diff * E_diff
tau_D is the transmittance of the  window to direct (beam) radiation
E_D is the incident direct (beam) radiation flux
tau_diff is the transmittance of the  window to diffuse radiation
E_diff is the incident diffuse radiation flux

From my calculation @ 20:00
surface azimuth angle: 0
                     latitude: 38.7
                declination: 20.64
                 solar time: 36
                            tilt: 18.97
         incidence angle: 1.588(rad)
  cos(incidence angle): 0.9998
                           SC: 0.64
transmittance of the window to direct radiation: 0.557
transmittance of the window to diffuse radiation: 0.511
                 incident direct (beam) radiation flux: 284 Btu/hr-sq.ft
                incident diffuse (beam) radiation flux: 39  Btu/hr-sq.ft
transmitted heat gain=0.557 x 284.97 + 0.511 x 39.94 = 179.17 Btu/hr-sq.ft (565 watt/meter square)
window with 26sq.ft = 26 x 179= 4658 Btu/hr

1 Btu/hr·ft2 = 3.154W/m2 

Above are my hand calculation

I'm not sure how energyplus calculate incident solar irradiance on window. Attached is my idf file.

I really appreciate your time, thanks.
Qianmin


On Thu, Jul 14, 2011 at 5:08 AM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 


Cannot comment without knowing what is included in your hand calculation, and whether you were using DesignDay sizing or weather file run.   What is the listed solar direct normal value  and Global diffused horizontal value used.  What solar altutude angle did you use?
 
The location and roof tilt do not cover all the necessary conditions.  You need to calculate the angle between the skilight normal and the solar beam at the time of calculation.
 
The maximum solar radiation intensity must not exceed 1400 watt/meter square.  It is only around 1000 watt/meter square measured in Kuching, East Malaysia.

Because you are using IP units, it is not easy to compare the result with the weather file input conditions.
 
 Dr. Li  

 

From: zqianmin@xxxxxxxxx
Date: Wed, 13 Jul 2011 14:41:00 -0700
Subject: Re: [EnergyPlus_Support] Re: Design Day V.S. Schedule


 
I have a skylight in my modeling, the simulation result shows this skylight has following maximum value
window transmitted solar of 1142.11Btu/h, 
window transmitted beam solar of 858Btu/h 
window transmitted diffuse solar of 284btu/h
window heat gain of 1382.65btu/h

this skylight window has a 
u-factor of 0.35, 
SHGC of 0.55,
Visible transmittance of 0.71, 
23ft^2, 
latitude of 38.7
longitude of -121.6  (Sacramental CA)
tilt angle is 18.97degree

hand calculating with radiant time series method give me following results:
window transmitted heat gains of 3360btu/h, which two times bigger than energyplus result.

I looked at the engineering reference, but still don't know why the value from energyplus are so small, about one third of hand calculating results.

Any one could give me some help? Thanks a lot.
Qianmin


 


























__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___