[EnergyPlus_Support] Need help in understanding the error





What does the following error mean. 
** Severe  ** Sizing: Coil:Cooling:DX:SingleSpeed "ZONE ONE PTAC COOLING COIL": Rated air volume flow rate per watt of rated total cooling capacity is out of range.
   **   ~~~   ** Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[1.433E-005], Max Rated Vol Flow Per Watt=[6.041E-005]. See Input-Output Reference Manual for valid range.
   ** Severe  ** For object = Coil:Cooling:DX:SingleSpeed, name = "ZONE ONE PTAC COOLING COIL", the combination of
   **   ~~~   ** rated air volume flow rate, total cooling capacity and sensible heat ratio yields coil exiting
   **   ~~~   ** air conditions above the saturation curve. Possible fixes are to reduce the rated total cooling
   **   ~~~   ** capacity, increase the rated air volume flow rate, or reduce the rated sensible heat ratio for this coil.
   **   ~~~   ** If autosizing, it is recommended that all three of these values be autosized.
   **   ~~~   **  During Warmup, Environment=RALEIGH_NC_USA ANNUAL HEATING 99% DESIGN CONDITIONS DB, at Simulation time=01/21 00:00 - 00:05
   **  Fatal  ** Check and revise the input data for this coil before rerunning the simulation.


Till now I was using the 'autosize' option. If I need to give my own cooling supply rate and heating air supply rate for a PTAC HVAC how should I go about doing it.

Kindly help.

Regards,

Aditya


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___