Re: [EnergyPlus_Support] Window Error - outward facing angle





Dear Laurent,

You need to reverse the ordering of the vertices that describe your window:
Vertex 1 -> Vertex 4
Vertex 2 -> Vertex 3
...
Vertex 4 -> Vertex 1

I often get this error when geometry is generated by an external program that doesn't know EnergyPlus' conventions.

Best regards,

Wouter

On 09/29/2011 07:30 AM, Laurent Kanago wrote:

I am getting an error that I can’t get around. I have a wall where there are 27 windows and each window causes the same error below. I tried deleting and rebuilding the wall and windows but I still get the same error. All the other walls in the zone give no problems. If you can help that would be great, let me know if you need more information.

 

   ** Severe  ** GetSurfaces: Outward facing angle [270.0] of subsurface="FE9DF0" significantly different than

   **   ~~~   ** ..facing angle [90.0] of base surface=1E5242 Tilt=90.0

   **   ~~~   ** ..surface class of base surface=Wall

 

Thanks,

 

Laurent Kanago

Technology Director

 

EHSlogo1

About | Services | Projects

Office: 312.235.2225

Fax: 773.989.8679

Cell: 312.730.2419

5030 N. Marine Dr #807

Chicago, IL 60640

 

“Please consider the environment before printing this e-mail. Thank you.”

 

 

 

 



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___