If you model your house accurately (surface
geometry, surface layers and
materials) you shouldn't be worried too much about
thermal bridging, the
software takes care of properly simulating heat
transfer through the surfaces.
When dealing with windows, however, there are two
fields related to thermal
bridging due to window frames in the
WindowProperty:FrameAndDivider object:
"Ratio of Frame-Edge Glass Conductance to
Center-Of-Glass
Conductance" and "Ratio of Divider-Edge Glass
Conductance to
Center-Of-Glass Conductance". Look them up in the
I/O Reference document,
and see for yourself if they are of any use to you
(they will only be usefull
for window frames, as mentioned).
Infiltration rates can be obtained using the zone
infiltration objects (in the
IDF, they are under the zone airflow group).
Again, take a look at the
documents to see how they work.
As for natural ventilation, things might get a bit
more tricky. For this, you
have to use the AirflowNetwork:Multizone objects.
These are a bit more complex,
and you should expect the need to spend a bit more
time around this to learn
how it works. The documentation provides much
information on the AN setup (look
first in the I/O ref document) and you can also
take a look at the example file
AirflowNetwork3zvent, for starters. Any further
questions/problems you
encounter, feel free to ask.
Note: you wont be able to use the zone
infiltration objects at the same time
you use the airflow network (simply because its
the way the software works).
The first ones are there for a more general
approach on zone infiltration,
whereas the airflow network is for detailed
natural ventilation prediction and
zone infiltration.
Pedro.
On 06-10-2011 12:31, tichaona wrote:
Dear Collegues
I am just beginning using Energy Plus. I am
creating geometry using Open Studio
and then importing it to Energy Plus. I have
modelled a light steel frame
house, which has glasswool in combination with
light steel, hence there is
going to be thermal bridging. How can i input
this in the energy plus IDF
editor. How can i also input infiltration
rates in the energy plus IDF editor?
How can I also do natural ventilation analysis
using the IDF editor. I will be
very gratefull for any help in this regard.
Kind Regards
T. K