In my opinion you can follow this approach a)
Concerning repetitive thermal
bridges (as studs or rafters in a wall) the best option is to use “equivalent”
layers including the effect of thermal bridges b)
Concerning linear thermal bridges
(as intersections between wall and floors or…) the best option is to
introduce a small opaque surface (=door) with the equivalent thermal transmittance
than the previously obtained following 2D calculations. The principle is to
introduce a “fictitious door” having similar thermal transmission
than the thermal bridging effect. It will be easier if Energy plus could accept “linear
elements” (one line instated surfaces) characterized by its linear
thermal transmittance Y expressed in W/m·K but I don’t know if this improvement
will be included in some newer releases ¿can someone inform us? Josep
Solé De: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] En nombre de Pedro Peixeiro point taken. thanks. though i dont see how one can be more
carefull about thermal bridges in E+ other than modelling the building as
accurately as possible, i'm not aware of specific inputs for this issue. Concerning thermal bridges in
buildings I’m not fully agree. If thermal bridges are not
avoided they will a big issue specially in Passive Houses or Nearly Zero Energy
houses then you need to take care before to say “…you
shouldn’t worried very much….”- For your specific case have a
look on “Composite wall constructions” in IO reference document
probably will help you For linear thermal bridges
due to intersection between building elements some special care is needed when
modeling in Energy + Josep Solé De: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
En nombre de Pedro Peixeiro
If you model your house accurately (surface geometry, surface layers and
materials) you shouldn't be worried too much about thermal bridging, the
software takes care of properly simulating heat transfer through the surfaces.
When dealing with windows, however, there are two fields related to thermal
bridging due to window frames in the WindowProperty:FrameAndDivider object:
"Ratio of Frame-Edge Glass Conductance to Center-Of-Glass
Conductance" and "Ratio of Divider-Edge Glass Conductance to
Center-Of-Glass Conductance". Look them up in the I/O Reference document,
and see for yourself if they are of any use to you (they will only be usefull
for window frames, as mentioned).
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.