[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Heating/Cooling load



So this method is quite easy. You must first be aware that there are many objects that you can add to introduce gain into a zone from lights, equipment, etc. Find that section in the Input Output Referance documentation. The object that you want is called EquipmentOther or OtherEquipment (can't remember exactly). Here is the trick: For a negative value to work you have to sometimes make a small adjustment in another file found in your eplus installation folder called the .idd file (look for this extention). This file describes (amongst others) what values are allowed to be entered in the various fields of objects such as EquipmentOther. In this file you must find the EqipmentOther object and its input field for the Wattage that corrisponds to where you would input the negative load. Change the default setting to also accept negative values. This is perfectly fine as this object is designed for this (has been used to simulate refridgeration display cabinets in the past). Run simulation with the EquipmentOther used to "take" load from a zone. As far as I remember, it can also take latent load from a zone. I used this once to model the effect of fan coils without having to setup the eplus fancoil objects (which require a lot more work) when I was just starting with eplus. 

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "amyquartette" <amyquartette@...> wrote:
>
> Thank you very much for your suggestion.
> 
> For step 2 with the radiant system, I would not spend too much time to get a gross view of the heating/cooling load.And also because I am a beginner,I think I will try the idea of equipment gains with negative values.But I have still no idea of this method. 
> 
> I would appreciate for your advise! Thank you again.
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@> wrote:
> >
> > The HVACTemplate:Zone:IdealLoadsairSystem is exactly right for the job. I would run all three envelope senarios using this. It will give you an excellant comparison. 
> > 
> > For step 2, the investigation of different HVAC types, incorporating radiant systems (especially radiant cooling ceiling and radiant floor heating) is a right pain. I'm sure by the time I've written a macro that adds this zone equipment and connects it flawlessly to the plant with automatic branch creation and insertion into said plant mixer splitter list and branch lists, not to mention creating the interzone surface and reverse surface with correct dimensions and constructions, by the time I've coded such a macro, e+ will have brought out a update with an easy template. I know a baseboard radiator template exists, but if you're a begginer stay away from embedded concrete or panel systems. Instead, just use the equipment gains with negative values and be wary of dew point temperature in the zone not falling below 16 deg C.
> > 
> > hope this helps more than confuses
> > 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "amyquartette" <amyquartette@> wrote:
> > >
> > > Dear all,
> > > 
> > > I'm modeling one apartment house with 3 different building envelopes.I would like to specify Heating and Cooling system (air condition system or radiant system)according to the performance of the building envelopes.
> > > 
> > > My questions are:
> > > 1)till now I found the HVACTemplate:Zone:IdealLoadsairSystem, is it an easy way to achieve the ideal loads air heating rate for the air condition system?
> > > 
> > > 2)is there any Template for Heating/Cooling load for radiant system?
> > > 
> > > Any suggestions would be welcome.Thank you very much.
> > >
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/