|
Jim, I totally agree with you. Outdoor drybulb minimum limit control is on the list of high-priority development items. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jim Dirkes Dear Chandan, Brent, Jean, Thanks for the feedback! I must say, though, that I was hoping to avoid learning EMS for maybe 30 years or so… Perhaps this is actually a development issue, but I thought about this a bit more and would like to know your thoughts in response: The normal warning I receive is shown below and is quite understandable. Occasionally a DX coil “wants” to start to satisfy a cooling load in cool weather due to high internal loads, or (as is my case) it may be a DOAS with hot gas reheat and is trying to dehumidify a humid zone. Both uses are legitimate. Both will result in a lot of warnings. In the first case, I can live with a slight increase in the zone temperature during those hours. In the second case, the zone h
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |