I don't see a problem with your schedules. You can try submitting your input file to the E+ Helpdesk. That's where developers of Energyplus will help you. The Yahoo group is a user-to-user forum.

http://energyplus.helpserve.com/

On 11/4/2011 1:46 PM, Amruta Khanolkar wrote:
 
---------------
Schedule:Compact,
    CLGSETP_SCH_New,         !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 06/27,          !- Field 1
    For: Weekdays SummerDesignDay,  !- Field 2
    Until: 06:00, 26.7,      !- Field 4
    Until: 22:00, 24.0,      !- Field 6
    Until: 24:00, 26.7,      !- Field 8
    For: Saturday,           !- Field 9
    Until: 06:00, 26.7,      !- Field 11
    Until: 18:00, 24.0,      !- Field 13
    Until: 24:00, 26.7,      !- Field 15
    Through: 06/28,          !- Field 16
    For: Weekdays SummerDesignDay,  !- Field 17
    Until: 06:00, 26.7,      !- Field 19
    Until: 14:00, 24.0,      !- Field 21
    Until: 15:00, 25.1,      !- Field 23
    Until: 16:00, 26.2,      !- Field 25
    Until: 17:00, 27.3,      !- Field 27
    Until: 22:00, 24.0,      !- Field 29
    Until: 24:00, 26.7,      !- Field 31
    For: Saturday,           !- Field 32
    Until: 06:00, 26.7,      !- Field 34
    Until: 18:00, 24.0,      !- Field 36
    Until: 24:00, 26.7,      !- Field 38
    Through: 12/31,          !- Field 39
    For: Weekdays SummerDesignDay,  !- Field 40
    Until: 06:00, 26.7,      !- Field 42
    Until: 22:00, 24.0,      !- Field 44
    Until: 24:00, 26.7,      !- Field 46
    For: Saturday,           !- Field 47
    Until: 06:00, 26.7,      !- Field 49
    Until: 18:00, 24.0,      !- Field 51
    Until: 24:00, 26.7,      !- Field 53
    For WinterDesignDay,     !- Field 54
    Until: 24:00, 26.7,      !- Field 56
    For: AllOtherDays,       !- Field 57
    Until: 24:00, 26.7;      !- Field 59
 
---------------
 
Schedule:Compact,
    HTGSETP_SCH,             !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: Weekdays,           !- Field 2
    Until: 06:00, 15.6,      !- Field 4
    Until: 22:00, 21.0,      !- Field 6
    Until: 24:00, 15.6,      !- Field 8
    For SummerDesignDay,     !- Field 9
    Until: 24:00, 15.6,      !- Field 11
    For: Saturday,           !- Field 12
    Until: 06:00, 15.6,      !- Field 14
    Until: 18:00, 21.0,      !- Field 16
    Until: 24:00, 15.6,      !- Field 18
    For: WinterDesignDay,    !- Field 19
    Until: 24:00, 21.0,      !- Field 21
    For: AllOtherDays,       !- Field 22
    Until: 24:00, 15.6;      !- Field 24
---------------
On Fri, Nov 4, 2011 at 10:19 AM, Richard Raustad <RRaustad@xxxxxxxxxxxx> wrote:
 

copy the 2 schedules (cooling and heating set point temperatures) from your input file into the email so we can see them



On 11/4/2011 1:16 PM, Amruta Khanolkar wrote:
 
I did not make any changes in the heating setpoint schedule. I just increased the cooling setpoint schedule. So all the cooling setpoints in my new schedule are higher than the heating setpoints still it is giving me this error message,
"DualSetPointWithDeadBand: Effective heating set-point higher than effective cooling set-point".
 
Please help.
 
Thanks,
Amruta
 
 
 
On Fri, Nov 4, 2011 at 6:07 AM, Richard Raustad <RRaustad@xxxxxxxxxxxx> wrote:
 

You increased the heating set point above the cooling set point. The cooling set point must be higher than the heating set point. Raise both temperatures.



On 11/4/2011 2:40 AM, ask_ami wrote:
 

Hi All,

I am working on a DOE prototype building(medium office). I created a new cooling set point schedule and assigned it at Thermostatsetpoint:DualSetpoint. In the new schedule I have just increased the set point temperature in stepped pattern by total 3.3 deg. C for 3 peak hous for a peak summer day. Remaining schedule is not changed. I am running this simulation for just that peak day. But after this change I got a severe error and my simulation terminated. The error is:
-------
** Severe ** DualSetPointWithDeadBand: Effective heating set-point higher than effective cooling set-point - increase deadband if using unmixed air model
** ~~~ ** occurs in Zone=CORE_BOTTOM During Warmup, Environment=Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, at Simulation time=06/28 00:00 - 00:10
** ~~~ ** LoadToHeatingSetPoint=-41431.055, LoadToCoolingSetPoint=-125592.948
** ~~~ ** Zone TempDepZnLd=429.02
** ~~~ ** Zone TempIndZnLd=11375.49
** ~~~ ** Zone ThermostatSetPoint=0.00
** ~~~ ** Zone HeatingSetPointOffset=0.00
** ~~~ ** Zone CoolingSetPointOffset=0.00
** Fatal ** Program terminates due to above conditions.
-------
Can somebody please explain me where did I go wrong?
Thanks,
Amruta


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___