I am not sure of your question (1). I do not treat the un-met hour as a problem. I do not know how ASHRAE defines it. To me, any time there is change in the schedule (load or temperature), there may be an un-met warning. I do not think that the un-met period is for the whole hour.
For (2), the ASHRAE guide line simply means that do not included the fan power calculation twice. When the fan goes on and off with the compressor, it should be included in the system power for COP or EER calculation, and not as a separate item. Many of you keep mentioning the base line and the proposed case. What is the base line case, a standard building specified by ASHRAE? If it is, simply use the same IDF and replace the proposed building related section in the IDF. If the base line building is cycling, the proposed building should also be cycling, as you are comparing the energy consumption for the two buildings. This may also cleared up some question raised by some user on ABUPS table, whether the electricity cooling load includes the fan power. Dr. Li To: equest-users@xxxxxxxxxxxxxxxxxxxxx; EnergyPlus_Support@xxxxxxxxxxxxxxx From: vigneshkumar1986@xxxxxxxxx Date: Sun, 6 Nov 2011 13:43:14 +0530 Subject: [EnergyPlus_Support] Regarding the Temperature Set point and Fan night cycle on/off Hi every one 1.If a zone temperature is above or Below the Temperatue set point of (68 - 76)F the zone hour is considered un met hour, my question is which standard sets these limits of (68-76)F and in which document could i be able to find this. and is the temperature limit is 68-76 F or is there any tolerences.
2."Fan should be cycled on during un occupied hours as per ASHRAE 90.1 G 3.1.2.4 .If the supply fan is modeled as cycling and fan energy is included in the energy-efficiency rating of the equipment, fan energy shall not be modeled explicitly". my question is wether the fan should be cycled on/off in both the base and the proposed case. if the Fan power is not splitted and it is included in the EER of the unit , when the fan is cycling the cooling unit will not run and the energy will not be consumed by the fan. the energy will only be consumed when the cooling unit is running , since the EER for the unit is inclusive of the fan energy . since there wont be any energy consumption during the cycling time , why do we need to do this. can we model the building with out the cycling.
Regards vignesh.
-- vigneshkumar
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |