--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Matthew Anderson <matthew.sverre.anderson@...> wrote:
>
> Hello Everybody,
>
> I have attached an IDF (which I hope you can all see) that I need help
> on. My problem is that the model seems to say that it requires no
> cooling even though there are definitely setpoints for the zones and the
> air handler. I simply cannot figure out what I am doing incorrectly.
>
> What I did was start with the DualDuctVariableVolume example file, then
> I imported in geometry/constructions from my building. I then changed
> the type/fan to constant volume and changed the chiller/operation
> schedule to reflect a single district cooling system operating 24/7.
>
> Anyway, the system has setpoints which seem to be /calling/ for cooling
> but the system seems to ignore it and never cools. It appears to be
> heating just fine, but never cools. I tried switching from
> ThermostatSetpoint:HeatingOrCooling to Thermostat:DualSetpoint (when
> should we be using these different setpoints?) which seemed to
> accomplish nothing. I really cannot seem to figure out what I need to do
> to get this working.
>
> I am currently running in circles and I would love if anybody could
> review this.
>
> Thank you,
> Matthew Anderson
>
> !-Generator IDFEditor 1.38a
> !-Option OriginalOrderTop UseSpecialFormat ViewInIPunits
>
> !-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
> !- Use '!' comments if they need to be retained when using the IDFEditor.
>
> ThermostatSetpoint:DualSetpoint,
> Heating Cooling Setpoint Sched, !- Name
> HEATING COOLING SETPOINTS, !- Heating Setpoint Temperature Schedule Name
> HEATING COOLING SETPOINTS; !- Cooling Setpoint Temperature Schedule Name
>
> Output:Variable,*,System Node Setpoint Temp,Hourly;
> Output:Variable,*,Zone/Sys Thermostat Heating Setpoint,Hourly;
>
> Sizing:Plant,
> Chilled Water Loop, !- Plant or Condenser Loop Name
> Cooling, !- Loop Type
> 7.22222241354578, !- Design Loop Exit Temperature {C}
> 6.66666684327303; !- Loop Design Temperature Difference {deltaC}
>
> Sizing:Plant,
> Hot Water Loop, !- Plant or Condenser Loop Name
> Heating, !- Loop Type
> 82.2222244003673, !- Design Loop Exit Temperature {C}
> 11.111111405455; !- Loop Design Temperature Difference {deltaC}
>
> Sizing:System,
> Main Dual Duct Air Loop, !- AirLoop Name
> Sensible, !- Type of Load to Size On
> autosize, !- Design Outdoor Air Flow Rate {m3/s}
> 1, !- Minimum System Air Flow Ratio
> 29.4444452244559, !- Preheat Design Temperature {C}
> 0.008, !- Preheat Design Humidity Ratio {kg-H2O/kg-Air}
> 11.0000002914005, !- Precool Design Temperature {C}
> 0.008, !- Precool Design Humidity Ratio {kg-H2O/kg-Air}
> 12.7777781162733, !- Central Cooling Design Supply Air Temperature {C}
> 29.4444452244559, !- Central Heating Design Supply Air Temperature {C}
> NonCoincident, !- Sizing Option
> No, !- 100% Outdoor Air in Cooling
> No, !- 100% Outdoor Air in Heating
> 0.008, !- Central Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-Air}
> 0.008, !- Central Heating Design Supply Air Humidity Ratio {kg-H2O/kg-Air}
> DesignDay, !- Cooling Design Air Flow Method
> , !- Cooling Design Air Flow Rate {m3/s}
> DesignDay, !- Heating Design Air Flow Method
> ; !- Heating Design Air Flow Rate {m3/s}
>
> Sizing:Zone,
> CONFERENCE, !- Zone Name
> 12.7777781162733, !- Zone Cooling Design Supply Air Temperature {C}
> 50, !- Zone Heating Design Supply Air Temperature {C}
> 0.008, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
> 0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
> Flow/Zone, !- Outdoor Air Method
> 0, !- Outdoor Air Flow per Person {m3/s}
> 0, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
> 0, !- Outdoor Air Flow per Zone {m3/s}
> 1, !- Zone Heating Sizing Factor
> 1, !- Zone Cooling Sizing Factor
> DesignDay, !- Cooling Design Air Flow Method
> 0, !- Cooling Design Air Flow Rate {m3/s}
> , !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
> , !- Cooling Minimum Air Flow {m3/s}
> 0, !- Cooling Minimum Air Flow Fraction
> DesignDay, !- Heating Design Air Flow Method
> 0, !- Heating Design Air Flow Rate {m3/s}
> , !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
> , !- Heating Maximum Air Flow {m3/s}
> 0; !- Heating Maximum Air Flow Fraction
>
> Sizing:Zone,
> EAST, !- Zone Name
> 12.7777781162733, !- Zone Cooling Design Supply Air Temperature {C}
> 50, !- Zone Heating Design Supply Air Temperature {C}
> 0.008, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
> 0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
> Flow/Zone, !- Outdoor Air Method
> 0, !- Outdoor Air Flow per Person {m3/s}
> 0, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
> 0, !- Outdoor Air Flow per Zone {m3/s}
> 1, !- Zone Heating Sizing Factor
> 1, !- Zone Cooling Sizing Factor
> DesignDay, !- Cooling Design Air Flow Method
> 0, !- Cooling Design Air Flow Rate {m3/s}
> , !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
> , !- Cooling Minimum Air Flow {m3/s}
> 0, !- Cooling Minimum Air Flow Fraction
> DesignDay, !- Heating Design Air Flow Method
> 0, !- Heating Design Air Flow Rate {m3/s}
> , !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
> , !- Heating Maximum Air Flow {m3/s}
> 0; !- Heating Maximum Air Flow Fraction
>
> Sizing:Zone,
> OPEN, !- Zone Name
> 12.7777781162733, !- Zone Cooling Design Supply Air Temperature {C}
> 50, !- Zone Heating Design Supply Air Temperature {C}
> 0.008, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
> 0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
> Flow/Zone, !- Outdoor Air Method
> 0, !- Outdoor Air Flow per Person {m3/s}
> 0, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
> 0, !- Outdoor Air Flow per Zone {m3/s}
> 1, !- Zone Heating Sizing Factor
> 1, !- Zone Cooling Sizing Factor
> DesignDay, !- Cooling Design Air Flow Method
> 0, !- Cooling Design Air Flow Rate {m3/s}
> , !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
> , !- Cooling Minimum Air Flow {m3/s}
> 0, !- Cooling Minimum Air Flow Fraction
> DesignDay, !- Heating Design Air Flow Method
> 0, !- Heating Design Air Flow Rate {m3/s}
> , !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
> , !- Heating Maximum Air Flow {m3/s}
> 0; !- Heating Maximum Air Flow Fraction
>
> Coil:Cooling:Water,
> Main Cooling Coil, !- Name
> Always On, !- Availability Schedule Name
> autosize, !- Design Water Flow Rate {m3/s}
> autosize, !- Design Air Flow Rate {m3/s}
> autosize, !- Design Inlet Water Temperature {C}
> autosize, !- Design Inlet Air Temperature {C}
> autosize, !- Design Outlet Air Temperature {C}
> autosize, !- Design Inlet Air Humidity Ratio {kg-H2O/kg-air}
> autosize, !- Design Outlet Air Humidity Ratio {kg-H2O/kg-air}
> Cooling Coil Water Inlet Node, !- Water Inlet Node Name
> Cooling Coil Water Outlet Node, !- Water Outlet Node Name
> Cooling Coil Inlet Node, !- Air Inlet Node Name
> Cooling Coil Outlet Node,!- Air Outlet Node Name
> SimpleAnalysis, !- Type of Analysis
> CrossFlow; !- Heat Exchanger Configuration
>
> Output:Diagnostics,
> DisplayUnusedSchedules, !- Key 1
> DisplayExtraWarnings; !- Key 2
>
> Fan:ConstantVolume,
> SupplyFan, !- Name
> Always On, !- Availability Schedule Name
> 0.7, !- Fan Efficiency
> 996.355860658514, !- Pressure Rise {Pa}
> autosize, !- Maximum Flow Rate {m3/s}
> 0.9, !- Motor Efficiency
> 0, !- Motor In Airstream Fraction
> Supply Fan Inlet Node, !- Air Inlet Node Name
> Supply Fan Outlet Node, !- Air Outlet Node Name
> General; !- End-Use Subcategory
>
> Output:SQLite,
> SimpleAndTabular; !- Option Type
>
> Output:Variable,*,Zone/Sys Thermostat Cooling Setpoint,Hourly;
> Output:Variable,*,System Node Temp,Hourly;
> Output:Variable,*,Outdoor Dry Bulb,Hourly;
> Output:Variable,*,Zone/Sys Sensible Load Predicted,Hourly;
> Output:Variable,*,Zone/Sys Air Temperature,Hourly;
> Output:Meter,DistrictHeating:Facility ,Monthly;
> Output:Meter,Cooling:DistrictCooling,Monthly;
> Output:Meter,Electricity:Building,Monthly;
>
> Site:Location,
> Lincoln Municipal Arpt_NE_USA Design_Conditions, !- Name
> 40.83, !- Latitude {deg}
> -96.77, !- Longitude {deg}
> -6.0, !- Time Zone {hr}
> 357.00; !- Elevation {m}
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Htg 99.6% Condns DB, !- Name
> -20.8, !- Maximum Dry-Bulb Temperature {C}
> 0.0, !- Daily Temperature Range {deltaC}
> -20.8, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 3.4, !- Wind Speed {m/s}
> 350, !- Wind Direction {deg}
> 0.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 1, !- Month
> WinterDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Htg 99% Condns DB, !- Name
> -17.6, !- Maximum Dry-Bulb Temperature {C}
> 0.0, !- Daily Temperature Range {deltaC}
> -17.6, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 3.4, !- Wind Speed {m/s}
> 350, !- Wind Direction {deg}
> 0.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 1, !- Month
> WinterDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Hum_n 99.6% Condns DP=>MCDB, !- Name
> -20.1, !- Maximum Dry-Bulb Temperature {C}
> 0.0, !- Daily Temperature Range {deltaC}
> -25.4, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 3.4, !- Wind Speed {m/s}
> 350, !- Wind Direction {deg}
> 0.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 1, !- Month
> WinterDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> DewPoint; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Hum_n 99% Condns DP=>MCDB, !- Name
> -16.8, !- Maximum Dry-Bulb Temperature {C}
> 0.0, !- Daily Temperature Range {deltaC}
> -22.1, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 3.4, !- Wind Speed {m/s}
> 350, !- Wind Direction {deg}
> 0.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 1, !- Month
> WinterDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> DewPoint; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Htg Wind 99.6% Condns WS=>MCDB, !- Name
> -2.7, !- Maximum Dry-Bulb Temperature {C}
> 0.0, !- Daily Temperature Range {deltaC}
> -2.7, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 13.9, !- Wind Speed {m/s}
> 350, !- Wind Direction {deg}
> 0.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 1, !- Month
> WinterDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Htg Wind 99% Condns WS=>MCDB, !- Name
> -4, !- Maximum Dry-Bulb Temperature {C}
> 0.0, !- Daily Temperature Range {deltaC}
> -4, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 12.1, !- Wind Speed {m/s}
> 350, !- Wind Direction {deg}
> 0.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 1, !- Month
> WinterDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg .4% Condns DB=>MWB, !- Name
> 36.2, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 23.9, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg 1% Condns DB=>MWB, !- Name
> 34.3, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 23.5, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg 2% Condns DB=>MWB, !- Name
> 32.6, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 23.1, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg .4% Condns WB=>MDB, !- Name
> 32.6, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 25.7, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg 1% Condns WB=>MDB, !- Name
> 31.7, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 25, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg 2% Condns WB=>MDB, !- Name
> 30.4, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 24.1, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg .4% Condns DP=>MDB, !- Name
> 29.5, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 23.8, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> DewPoint; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg 1% Condns DP=>MDB, !- Name
> 28.7, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 22.9, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> DewPoint; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg 2% Condns DP=>MDB, !- Name
> 27.9, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 22.2, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> DewPoint; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg .4% Condns Enth=>MDB, !- Name
> 32.8, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 81.3, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> Enthalpy; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg 1% Condns Enth=>MDB, !- Name
> 31.5, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 77.7, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> Enthalpy; !- Humidity Indicating Type
>
> SizingPeriod:DesignDay,
> Lincoln Municipal Arpt Ann Clg 2% Condns Enth=>MDB, !- Name
> 30.5, !- Maximum Dry-Bulb Temperature {C}
> 12.1, !- Daily Temperature Range {deltaC}
> 74.4, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 97109., !- Barometric Pressure {Pa}
> 6.6, !- Wind Speed {m/s}
> 180, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> Enthalpy; !- Humidity Indicating Type
>
> RunPeriod,
> , !- Name
> 1, !- Begin Month
> 1, !- Begin Day of Month
> 12, !- End Month
> 31, !- End Day of Month
> USEWEATHERFILE, !- Day of Week for Start Day
> Yes, !- Use Weather File Holidays and Special Days
> Yes, !- Use Weather File Daylight Saving Period
> No, !- Apply Weekend Holiday Rule
> Yes, !- Use Weather File Rain Indicators
> Yes, !- Use Weather File Snow Indicators
> 1; !- Number of Times Runperiod to be Repeated
>
> RunPeriodControl:SpecialDays,
> New Years Day, !- Name
> January 1, !- Start Date
> 1, !- Duration {days}
> Holiday; !- Special Day Type
>
> RunPeriodControl:SpecialDays,
> Veterans Day, !- Name
> November 11, !- Start Date
> 1, !- Duration {days}
> Holiday; !- Special Day Type
>
> RunPeriodControl:SpecialDays,
> Christmas, !- Name
> December 25, !- Start Date
> 1, !- Duration {days}
> Holiday; !- Special Day Type
>
> RunPeriodControl:SpecialDays,
> Independence Day, !- Name
> July 4, !- Start Date
> 1, !- Duration {days}
> Holiday; !- Special Day Type
>
> RunPeriodControl:SpecialDays,
> MLK Day, !- Name
> 3rd Monday in January, !- Start Date
> 1, !- Duration {days}
> Holiday; !- Special Day Type
>
> RunPeriodControl:SpecialDays,
> Presidents Day, !- Name
> 3rd Monday in February, !- Start Date
> 1, !- Duration {days}
> Holiday; !- Special Day Type
>
> RunPeriodControl:SpecialDays,
> Memorial Day, !- Name
> Last Monday in May, !- Start Date
> 1, !- Duration {days}
> Holiday; !- Special Day Type
>
> RunPeriodControl:SpecialDays,
> Labor Day, !- Name
> 1st Monday in September, !- Start Date
> 1, !- Duration {days}
> Holiday; !- Special Day Type
>
> RunPeriodControl:SpecialDays,
> Columbus Day, !- Name
> 2nd Monday in October, !- Start Date
> 1, !- Duration {days}
> Holiday; !- Special Day Type
>
> RunPeriodControl:SpecialDays,
> Thanksgiving, !- Name
> 4th Thursday in November,!- Start Date
> 1, !- Duration {days}
> Holiday; !- Special Day Type
>
> RunPeriodControl:DaylightSavingTime,
> 1st Sunday in April, !- Start Date
> Last Sunday in October; !- End Date
>
> Site:GroundTemperature:BuildingSurface,18,18,18,18,18,18,18,18,18,18,18,18;
> Site:GroundTemperature:Shallow,13,13,13,13,13,13,13,13,13,13,13,13;
> Site:GroundTemperature:Deep,16,16,16,16,16,16,16,16,16,16,16,16;
>
> Schedule:Compact,
> Office Lights Schedule, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays, !- Field 2
> Until: 05:00, 0.05, !- Field 4
> Until: 07:00, 0.1, !- Field 6
> Until: 08:00, 0.3, !- Field 8
> Until: 17:00, 0.9, !- Field 10
> Until: 18:00, 0.5, !- Field 12
> Until: 20:00, 0.3, !- Field 14
> Until: 22:00, 0.2, !- Field 16
> Until: 23:00, 0.1, !- Field 18
> Until: 24:00, 0.05, !- Field 20
> For: SummerDesignDay, !- Field 21
> Until: 24:00, 1.0, !- Field 23
> For: Saturday, !- Field 24
> Until: 06:00, 0.05, !- Field 26
> Until: 08:00, 0.1, !- Field 28
> Until: 12:00, 0.3, !- Field 30
> Until: 17:00, 0.15, !- Field 32
> Until: 24:00, 0.05, !- Field 34
> For: WinterDesignDay, !- Field 35
> Until: 24:00, 0.0, !- Field 37
> For: Sunday Holidays AllOtherDays, !- Field 38
> Until: 24:00, 0.05; !- Field 40
>
> Schedule:Compact,
> Office Equipment Schedule, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays, !- Field 2
> Until: 08:00, 0.40, !- Field 4
> Until: 12:00, 0.90, !- Field 6
> Until: 13:00, 0.80, !- Field 8
> Until: 17:00, 0.90, !- Field 10
> Until: 18:00, 0.50, !- Field 12
> Until: 24:00, 0.40, !- Field 14
> For: SummerDesignDay, !- Field 15
> Until: 24:00, 1.0, !- Field 17
> For: Saturday, !- Field 18
> Until: 06:00, 0.30, !- Field 20
> Until: 08:00, 0.4, !- Field 22
> Until: 12:00, 0.5, !- Field 24
> Until: 17:00, 0.35, !- Field 26
> Until: 24:00, 0.30, !- Field 28
> For: WinterDesignDay, !- Field 29
> Until: 24:00, 0.0, !- Field 31
> For: Sunday Holidays AllOtherDays, !- Field 32
> Until: 24:00, 0.30; !- Field 34
>
> Schedule:Compact,
> Office Occupancy Schedule, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays, !- Field 2
> Until: 06:00, 0.0, !- Field 4
> Until: 07:00, 0.1, !- Field 6
> Until: 08:00, 0.2, !- Field 8
> Until: 12:00, 0.95, !- Field 10
> Until: 13:00, 0.5, !- Field 12
> Until: 17:00, 0.95, !- Field 14
> Until: 18:00, 0.3, !- Field 16
> Until: 20:00, 0.1, !- Field 18
> Until: 24:00, 0.05, !- Field 20
> For: SummerDesignDay, !- Field 21
> Until: 06:00, 0.0, !- Field 23
> Until: 22:00, 1.0, !- Field 25
> Until: 24:00, 0.05, !- Field 27
> For: Saturday, !- Field 28
> Until: 06:00, 0.0, !- Field 30
> Until: 08:00, 0.1, !- Field 32
> Until: 12:00, 0.3, !- Field 34
> Until: 17:00, 0.1, !- Field 36
> Until: 19:00, 0.0, !- Field 38
> Until: 24:00, 0.0, !- Field 40
> For: WinterDesignDay, !- Field 41
> Until: 24:00, 0.0, !- Field 43
> For: Sunday Holidays AllOtherDays, !- Field 44
> Until: 06:00, 0.0, !- Field 46
> Until: 18:00, 0.0, !- Field 48
> Until: 24:00, 0.0; !- Field 50
>
> Schedule:Compact,
> Infiltration Schedule, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays SummerDesignDay, !- Field 2
> Until: 06:00, 1.0, !- Field 4
> Until: 22:00, 0.0, !- Field 6
> Until: 24:00, 1.0, !- Field 8
> For: Saturday WinterDesignDay, !- Field 9
> Until: 06:00, 1.0, !- Field 11
> Until: 18:00, 0.0, !- Field 13
> Until: 24:00, 1.0, !- Field 15
> For: Sunday Holidays AllOtherDays, !- Field 16
> Until: 24:00, 1.0; !- Field 18
>
> Schedule:Compact,
> Hours of Operation Schedule, !- Name
> On/Off, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays SummerDesignDay, !- Field 2
> Until: 06:00, 0.0, !- Field 4
> Until: 22:00, 1.0, !- Field 6
> Until: 24:00, 0.0, !- Field 8
> For: Saturday WinterDesignDay, !- Field 9
> Until: 06:00, 0.0, !- Field 11
> Until: 18:00, 1.0, !- Field 13
> Until: 24:00, 0.0, !- Field 15
> For: Sunday Holidays AllOtherDays, !- Field 16
> Until: 24:00, 0.0; !- Field 18
>
> Schedule:Compact,
> Always On, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 1.0; !- Field 4
>
> Schedule:Compact,
> Always Off, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 0.0; !- Field 4
>
> Schedule:Compact,
> Office Activity Schedule,!- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 120.; !- Field 4
>
> Schedule:Compact,
> Office Work Eff. Schedule, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 0.0; !- Field 4
>
> Schedule:Compact,
> Office Clothing Schedule,!- Name
> Any Number, !- Schedule Type Limits Name
> Through: 04/30, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 1.0, !- Field 4
> Through: 09/30, !- Field 5
> For: AllDays, !- Field 6
> Until: 24:00, 0.5, !- Field 8
> Through: 12/31, !- Field 9
> For: AllDays, !- Field 10
> Until: 24:00, 1.0; !- Field 12
>
> ScheduleTypeLimits,
> Any Number; !- Name
>
> ScheduleTypeLimits,
> Fraction, !- Name
> 0.0, !- Lower Limit Value
> 1.0, !- Upper Limit Value
> CONTINUOUS; !- Numeric Type
>
> ScheduleTypeLimits,
> Temperature, !- Name
> -60, !- Lower Limit Value
> 200, !- Upper Limit Value
> CONTINUOUS; !- Numeric Type
>
> ScheduleTypeLimits,
> On/Off, !- Name
> 0, !- Lower Limit Value
> 1, !- Upper Limit Value
> DISCRETE; !- Numeric Type
>
> ScheduleTypeLimits,
> Control Type, !- Name
> 0, !- Lower Limit Value
> 4, !- Upper Limit Value
> DISCRETE; !- Numeric Type
>
> ScheduleTypeLimits,
> Humidity, !- Name
> 10, !- Lower Limit Value
> 90, !- Upper Limit Value
> CONTINUOUS; !- Numeric Type
>
> ScheduleTypeLimits,
> HVACTemplate Any Number; !- Name
>
> Material,
> F08 Metal surface, !- Name
> Smooth, !- Roughness
> 0.0008, !- Thickness {m}
> 45.28, !- Conductivity {W/m-K}
> 7824, !- Density {kg/m3}
> 500; !- Specific Heat {J/kg-K}
>
> Material,
> I01 25mm insulation board, !- Name
> MediumRough, !- Roughness
> 0.0254, !- Thickness {m}
> 0.03, !- Conductivity {W/m-K}
> 43, !- Density {kg/m3}
> 1210; !- Specific Heat {J/kg-K}
>
> Material,
> I02 50mm insulation board, !- Name
> MediumRough, !- Roughness
> 0.0508, !- Thickness {m}
> 0.03, !- Conductivity {W/m-K}
> 43, !- Density {kg/m3}
> 1210; !- Specific Heat {J/kg-K}
>
> Material,
> G01a 19mm gypsum board, !- Name
> MediumSmooth, !- Roughness
> 0.019, !- Thickness {m}
> 0.16, !- Conductivity {W/m-K}
> 800, !- Density {kg/m3}
> 1090; !- Specific Heat {J/kg-K}
>
> Material,
> M11 100mm lightweight concrete, !- Name
> MediumRough, !- Roughness
> 0.1016, !- Thickness {m}
> 0.53, !- Conductivity {W/m-K}
> 1280, !- Density {kg/m3}
> 840; !- Specific Heat {J/kg-K}
>
> Material,
> F16 Acoustic tile, !- Name
> MediumSmooth, !- Roughness
> 0.0191, !- Thickness {m}
> 0.06, !- Conductivity {W/m-K}
> 368, !- Density {kg/m3}
> 590; !- Specific Heat {J/kg-K}
>
> Material,
> M01 100mm brick, !- Name
> MediumRough, !- Roughness
> 0.1016, !- Thickness {m}
> 0.89, !- Conductivity {W/m-K}
> 1920, !- Density {kg/m3}
> 790; !- Specific Heat {J/kg-K}
>
> Material,
> M15 200mm heavyweight concrete, !- Name
> MediumRough, !- Roughness
> 0.2032, !- Thickness {m}
> 1.95, !- Conductivity {W/m-K}
> 2240, !- Density {kg/m3}
> 900; !- Specific Heat {J/kg-K}
>
> Material,
> M05 200mm concrete block,!- Name
> MediumRough, !- Roughness
> 0.2032, !- Thickness {m}
> 1.11, !- Conductivity {W/m-K}
> 800, !- Density {kg/m3}
> 920; !- Specific Heat {J/kg-K}
>
> Material,
> G05 25mm wood, !- Name
> MediumSmooth, !- Roughness
> 0.0254, !- Thickness {m}
> 0.15, !- Conductivity {W/m-K}
> 608, !- Density {kg/m3}
> 1630; !- Specific Heat {J/kg-K}
>
> Material:AirGap,
> F04 Wall air space resistance, !- Name
> 0.15; !- Thermal Resistance {m2-K/W}
>
> Material:AirGap,
> F05 Ceiling air space resistance, !- Name
> 0.18; !- Thermal Resistance {m2-K/W}
>
> WindowMaterial:Glazing,
> Clear 3mm, !- Name
> SpectralAverage, !- Optical Data Type
> , !- Window Glass Spectral Data Set Name
> 0.003, !- Thickness {m}
> 0.837, !- Solar Transmittance at Normal Incidence
> 0.075, !- Front Side Solar Reflectance at Normal Incidence
> 0.075, !- Back Side Solar Reflectance at Normal Incidence
> 0.898, !- Visible Transmittance at Normal Incidence
> 0.081, !- Front Side Visible Reflectance at Normal Incidence
> 0.081, !- Back Side Visible Reflectance at Normal Incidence
> 0, !- Infrared Transmittance at Normal Incidence
> 0.84, !- Front Side Infrared Hemispherical Emissivity
> 0.84, !- Back Side Infrared Hemispherical Emissivity
> 0.9; !- Conductivity {W/m-K}
>
> WindowMaterial:Gas,
> Air 13mm, !- Name
> Air, !- Gas Type
> 0.0127; !- Thickness {m}
>
> Construction,
> Exterior Floor, !- Name
> M11 100mm lightweight concrete; !- Outside Layer
>
> Construction,
> Interior Floor, !- Name
> M11 100mm lightweight concrete; !- Outside Layer
>
> Construction,
> Exterior Wall, !- Name
> M15 200mm heavyweight concrete; !- Outside Layer
>
> Construction,
> Interior Wall, !- Name
> M15 200mm heavyweight concrete; !- Outside Layer
>
> Construction,
> Exterior Roof, !- Name
> M11 100mm lightweight concrete; !- Outside Layer
>
> Construction,
> Interior Ceiling, !- Name
> M11 100mm lightweight concrete, !- Outside Layer
> F05 Ceiling air space resistance, !- Layer 2
> F16 Acoustic tile; !- Layer 3
>
> Construction,
> Exterior Window, !- Name
> Clear 3mm; !- Outside Layer
>
> Construction,
> Interior Window, !- Name
> Clear 3mm; !- Outside Layer
>
> Construction,
> Exterior Door, !- Name
> F08 Metal surface, !- Outside Layer
> I01 25mm insulation board; !- Layer 2
>
> Construction,
> Interior Door, !- Name
> G05 25mm wood; !- Outside Layer
>
> GlobalGeometryRules,
> UpperLeftCorner, !- Starting Vertex Position
> Counterclockwise, !- Vertex Entry Direction
> Relative; !- Coordinate System
>
> Zone,
> GARAGE, !- Name
> 0.0, !- Direction of Relative North {deg}
> 2.728383, 6.651413, 0.0, !- X,Y,Z {m}
> , !- Type
> 1, !- Multiplier
> 5.18134730989933, !- Ceiling Height {m}
> autocalculate; !- Volume {m3}
>
> Zone,
> CONFERENCE, !- Name
> 0.0, !- Direction of Relative North {deg}
> 23.25624, 8.5344, 0.0, !- X,Y,Z {m}
> , !- Type
> 1, !- Multiplier
> 5.18134730989933, !- Ceiling Height {m}
> autocalculate; !- Volume {m3}
>
> Zone,
> EAST, !- Name
> 0.0, !- Direction of Relative North {deg}
> 23.25624, 12.8016, -9.139744, !- X,Y,Z {m}
> , !- Type
> 1, !- Multiplier
> 5.18134730989933, !- Ceiling Height {m}
> autocalculate; !- Volume {m3}
>
> Zone,
> OPEN, !- Name
> 0.0, !- Direction of Relative North {deg}
> 14.0208, 8.5344, 0.0, !- X,Y,Z {m}
> , !- Type
> 1, !- Multiplier
> 5.18134730989933, !- Ceiling Height {m}
> autocalculate; !- Volume {m3}
>
> BuildingSurface:Detailed,
> 41702B, !- Name
> Floor, !- Surface Type
> Exterior Floor, !- Construction Name
> GARAGE, !- Zone Name
> Ground, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> , !- View Factor to Ground
> 6, !- Number of Vertices
> 11.292417000000, 6.150187000000, 0.000000000000,
> !- X,Y,Z 1 {m}
> 11.292417000000, -6.651413000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 1.843617000000, -6.651413000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 1.843617000000, -2.993813000000, 0.000000000000,
> !- X,Y,Z 4 {m}
> -2.728383000000, -2.993813000000, 0.000000000000,
> !- X,Y,Z 5 {m}
> -2.728383000000, 6.150187000000, 0.000000000000;
> !- X,Y,Z 6 {m}
>
> BuildingSurface:Detailed,
> F0B313, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> GARAGE, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> 1.843617000000, -2.993813000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> 1.843617000000, -2.993813000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 1.843617000000, -6.651413000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 1.843617000000, -6.651413000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> A6D260, !- Name
> Wall, !- Surface Type
> Exterior Door, !- Construction Name
> GARAGE, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> 11.292417000000, 6.150187000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> 11.292417000000, 6.150187000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> -2.728383000000, 6.150187000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> -2.728383000000, 6.150187000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> 5B4348, !- Name
> Roof, !- Surface Type
> Exterior Roof, !- Construction Name
> GARAGE, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 6, !- Number of Vertices
> -2.728383000000, 6.150187000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> -2.728383000000, -2.993813000000, 5.232400000000,
> !- X,Y,Z 2 {m}
> 1.843617000000, -2.993813000000, 5.232400000000,
> !- X,Y,Z 3 {m}
> 1.843617000000, -6.651413000000, 5.232400000000,
> !- X,Y,Z 4 {m}
> 11.292417000000, -6.651413000000, 5.232400000000,
> !- X,Y,Z 5 {m}
> 11.292417000000, 6.150187000000, 5.232400000000;
> !- X,Y,Z 6 {m}
>
> BuildingSurface:Detailed,
> 943349, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> GARAGE, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> -2.728383000000, -2.993813000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> -2.728383000000, -2.993813000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 1.843617000000, -2.993813000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 1.843617000000, -2.993813000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> DF5EE9, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> GARAGE, !- Zone Name
> Adiabatic, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> -2.728383000000, 6.150187000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> -2.728383000000, 6.150187000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> -2.728383000000, -2.993813000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> -2.728383000000, -2.993813000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> 36D5CB, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> GARAGE, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> 1.843617000000, -6.651413000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> 1.843617000000, -6.651413000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 11.292417000000, -6.651413000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 11.292417000000, -6.651413000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> GarageWestI, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> GARAGE, !- Zone Name
> Surface, !- Outside Boundary Condition
> OpenWestI, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 11.292417000000, -6.651413000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> 11.292417000000, -6.651413000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 11.292417000000, 1.882987000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 11.292417000000, 1.882987000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> BC4DDA, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> GARAGE, !- Zone Name
> Surface, !- Outside Boundary Condition
> 2996F2, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> 11.292417000000, 1.882987000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> 11.292417000000, 1.882987000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 11.292417000000, 6.150187000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 11.292417000000, 6.150187000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> E22B2D, !- Name
> Floor, !- Surface Type
> Exterior Floor, !- Construction Name
> CONFERENCE, !- Zone Name
> Ground, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> 0.000000000000, 4.267200000000, 0.000000000000,
> !- X,Y,Z 1 {m}
> 0.000000000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> -9.235440000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> -9.235440000000, 4.267200000000, 0.000000000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> ConferenceNorthI, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> CONFERENCE, !- Zone Name
> Surface, !- Outside Boundary Condition
> OpenNorthI, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> -9.235440000000, 0.000000000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> -9.235440000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 0.000000000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 0.000000000000, 0.000000000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> ConferenceWestII, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> CONFERENCE, !- Zone Name
> Surface, !- Outside Boundary Condition
> OpenWestII, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 0.000000000000, 0.000000000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> 0.000000000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 0.000000000000, 4.267200000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 0.000000000000, 4.267200000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> 15E59E, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> CONFERENCE, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> 0.000000000000, 4.267200000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> 0.000000000000, 4.267200000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> -9.235440000000, 4.267200000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> -9.235440000000, 4.267200000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> 2996F2, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> CONFERENCE, !- Zone Name
> Surface, !- Outside Boundary Condition
> BC4DDA, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> -9.235440000000, 4.267200000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> -9.235440000000, 4.267200000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> -9.235440000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> -9.235440000000, 0.000000000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> 4F35AD, !- Name
> Roof, !- Surface Type
> Exterior Roof, !- Construction Name
> CONFERENCE, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> -9.235440000000, 4.267200000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> -9.235440000000, 0.000000000000, 5.232400000000,
> !- X,Y,Z 2 {m}
> 0.000000000000, 0.000000000000, 5.232400000000,
> !- X,Y,Z 3 {m}
> 0.000000000000, 4.267200000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> 72C969, !- Name
> Floor, !- Surface Type
> Exterior Floor, !- Construction Name
> EAST, !- Zone Name
> Ground, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> , !- View Factor to Ground
> 6, !- Number of Vertices
> 9.296400000000, 0.000000000000, 9.139744000000,
> !- X,Y,Z 1 {m}
> 9.296400000000, -12.769850000000, 9.139744000000,
> !- X,Y,Z 2 {m}
> 5.029200000000, -12.769850000000, 9.139744000000,
> !- X,Y,Z 3 {m}
> 5.029200000000, -4.267200000000, 9.139744000000,
> !- X,Y,Z 4 {m}
> 1.371600000000, -4.267200000000, 9.139744000000,
> !- X,Y,Z 5 {m}
> 1.371600000000, 0.000000000000, 9.139744000000;
> !- X,Y,Z 6 {m}
>
> BuildingSurface:Detailed,
> EastNorthIII, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> EAST, !- Zone Name
> Surface, !- Outside Boundary Condition
> OpenNorthIII, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 1.371600000000, -4.267200000000, 14.372144000000,
> !- X,Y,Z 1 {m}
> 1.371600000000, -4.267200000000, 9.139744000000,
> !- X,Y,Z 2 {m}
> 5.029200000000, -4.267200000000, 9.139744000000,
> !- X,Y,Z 3 {m}
> 5.029200000000, -4.267200000000, 14.372144000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> CE0365, !- Name
> Roof, !- Surface Type
> Exterior Roof, !- Construction Name
> EAST, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 6, !- Number of Vertices
> 1.371600000000, 0.000000000000, 14.372144000000,
> !- X,Y,Z 1 {m}
> 1.371600000000, -4.267200000000, 14.372144000000,
> !- X,Y,Z 2 {m}
> 5.029200000000, -4.267200000000, 14.372144000000,
> !- X,Y,Z 3 {m}
> 5.029200000000, -12.769850000000, 14.372144000000,
> !- X,Y,Z 4 {m}
> 9.296400000000, -12.769850000000, 14.372144000000,
> !- X,Y,Z 5 {m}
> 9.296400000000, 0.000000000000, 14.372144000000;
> !- X,Y,Z 6 {m}
>
> BuildingSurface:Detailed,
> 3474E0, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> EAST, !- Zone Name
> Adiabatic, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 9.296400000000, -12.769850000000, 14.372144000000,
> !- X,Y,Z 1 {m}
> 9.296400000000, -12.769850000000, 9.139744000000,
> !- X,Y,Z 2 {m}
> 9.296400000000, 0.000000000000, 9.139744000000,
> !- X,Y,Z 3 {m}
> 9.296400000000, 0.000000000000, 14.372144000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> EastEastII, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> EAST, !- Zone Name
> Surface, !- Outside Boundary Condition
> OpenEastII, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 1.371600000000, 0.000000000000, 14.372144000000,
> !- X,Y,Z 1 {m}
> 1.371600000000, 0.000000000000, 9.139744000000,
> !- X,Y,Z 2 {m}
> 1.371600000000, -4.267200000000, 9.139744000000,
> !- X,Y,Z 3 {m}
> 1.371600000000, -4.267200000000, 14.372144000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> E84069, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> EAST, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> 9.296400000000, 0.000000000000, 14.372144000000,
> !- X,Y,Z 1 {m}
> 9.296400000000, 0.000000000000, 9.139744000000,
> !- X,Y,Z 2 {m}
> 1.371600000000, 0.000000000000, 9.139744000000,
> !- X,Y,Z 3 {m}
> 1.371600000000, 0.000000000000, 14.372144000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> EastEastI, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> EAST, !- Zone Name
> Surface, !- Outside Boundary Condition
> OpenEastI, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 5.029200000000, -4.267200000000, 14.372144000000,
> !- X,Y,Z 1 {m}
> 5.029200000000, -4.267200000000, 9.139744000000,
> !- X,Y,Z 2 {m}
> 5.029200000000, -12.769850000000, 9.139744000000,
> !- X,Y,Z 3 {m}
> 5.029200000000, -12.769850000000, 14.372144000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> 198B2D, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> EAST, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> 5.029200000000, -12.769850000000, 14.372144000000,
> !- X,Y,Z 1 {m}
> 5.029200000000, -12.769850000000, 9.139744000000,
> !- X,Y,Z 2 {m}
> 9.296400000000, -12.769850000000, 9.139744000000,
> !- X,Y,Z 3 {m}
> 9.296400000000, -12.769850000000, 14.372144000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> 872F05, !- Name
> Floor, !- Surface Type
> Exterior Floor, !- Construction Name
> OPEN, !- Zone Name
> Ground, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> , !- View Factor to Ground
> 8, !- Number of Vertices
> 10.607040000000, 4.267200000000, 0.000000000000,
> !- X,Y,Z 1 {m}
> 10.607040000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 14.264640000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 14.264640000000, -8.502650000000, 0.000000000000,
> !- X,Y,Z 4 {m}
> 0.000000000000, -8.502650000000, 0.000000000000,
> !- X,Y,Z 5 {m}
> 0.000000000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 6 {m}
> 9.235440000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 7 {m}
> 9.235440000000, 4.267200000000, 0.000000000000;
> !- X,Y,Z 8 {m}
>
> BuildingSurface:Detailed,
> OpenWestI, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> OPEN, !- Zone Name
> Surface, !- Outside Boundary Condition
> GarageWestI, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 0.000000000000, 0.000000000000, 5.257800000000,
> !- X,Y,Z 1 {m}
> 0.000000000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 0.000000000000, -8.502650000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 0.000000000000, -8.502650000000, 5.257800000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> D48B11, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> OPEN, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> 10.607040000000, 4.267200000000, 5.257800000000,
> !- X,Y,Z 1 {m}
> 10.607040000000, 4.267200000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 9.235440000000, 4.267200000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 9.235440000000, 4.267200000000, 5.257800000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> OpenNorthIII, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> OPEN, !- Zone Name
> Surface, !- Outside Boundary Condition
> EastNorthIII, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 14.264640000000, 0.000000000000, 5.257800000000,
> !- X,Y,Z 1 {m}
> 14.264640000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 10.607040000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 10.607040000000, 0.000000000000, 5.257800000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> 675F2E, !- Name
> Wall, !- Surface Type
> Exterior Wall, !- Construction Name
> OPEN, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 4, !- Number of Vertices
> 0.000000000000, -8.502650000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> 0.000000000000, -8.502650000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 14.264640000000, -8.502650000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 14.264640000000, -8.502650000000, 5.232400000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> OpenNorthI, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> OPEN, !- Zone Name
> Surface, !- Outside Boundary Condition
> ConferenceNorthI, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 9.235440000000, 0.000000000000, 5.257800000000,
> !- X,Y,Z 1 {m}
> 9.235440000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 0.000000000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 0.000000000000, 0.000000000000, 5.257800000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> OpenEastII, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> OPEN, !- Zone Name
> Surface, !- Outside Boundary Condition
> EastEastII, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 10.607040000000, 0.000000000000, 5.257800000000,
> !- X,Y,Z 1 {m}
> 10.607040000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 10.607040000000, 4.267200000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 10.607040000000, 4.267200000000, 5.257800000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> 2C5CED, !- Name
> Roof, !- Surface Type
> Exterior Roof, !- Construction Name
> OPEN, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> , !- View Factor to Ground
> 8, !- Number of Vertices
> 0.000000000000, 0.000000000000, 5.232400000000,
> !- X,Y,Z 1 {m}
> 0.000000000000, -8.502650000000, 5.232400000000,
> !- X,Y,Z 2 {m}
> 14.264640000000, -8.502650000000, 5.232400000000,
> !- X,Y,Z 3 {m}
> 14.264640000000, 0.000000000000, 5.232400000000,
> !- X,Y,Z 4 {m}
> 10.607040000000, 0.000000000000, 5.232400000000,
> !- X,Y,Z 5 {m}
> 10.607040000000, 4.267200000000, 5.232400000000,
> !- X,Y,Z 6 {m}
> 9.235440000000, 4.267200000000, 5.232400000000,
> !- X,Y,Z 7 {m}
> 9.235440000000, 0.000000000000, 5.232400000000;
> !- X,Y,Z 8 {m}
>
> BuildingSurface:Detailed,
> OpenWestII, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> OPEN, !- Zone Name
> Surface, !- Outside Boundary Condition
> ConferenceWestII, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 9.235440000000, 4.267200000000, 5.257800000000,
> !- X,Y,Z 1 {m}
> 9.235440000000, 4.267200000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 9.235440000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 9.235440000000, 0.000000000000, 5.257800000000;
> !- X,Y,Z 4 {m}
>
> BuildingSurface:Detailed,
> OpenEastI, !- Name
> Wall, !- Surface Type
> Interior Wall, !- Construction Name
> OPEN, !- Zone Name
> Surface, !- Outside Boundary Condition
> EastEastI, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 14.264640000000, -8.502650000000, 5.257800000000,
> !- X,Y,Z 1 {m}
> 14.264640000000, -8.502650000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 14.264640000000, 0.000000000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 14.264640000000, 0.000000000000, 5.257800000000;
> !- X,Y,Z 4 {m}
>
> FenestrationSurface:Detailed,
> 494B51, !- Name
> Door, !- Surface Type
> Exterior Door, !- Construction Name
> A6D260, !- Building Surface Name
> , !- Outside Boundary Condition Object
> , !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> , !- Multiplier
> 4, !- Number of Vertices
> 7.939617000000, 6.150187000000, 3.657600000000,
> !- X,Y,Z 1 {m}
> 7.939617000000, 6.150187000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 1.843617000000, 6.150187000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 1.843617000000, 6.150187000000, 3.657600000000;
> !- X,Y,Z 4 {m}
>
> FenestrationSurface:Detailed,
> 30D092, !- Name
> Door, !- Surface Type
> Exterior Door, !- Construction Name
> 36D5CB, !- Building Surface Name
> , !- Outside Boundary Condition Object
> , !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> , !- Multiplier
> 4, !- Number of Vertices
> 3.612983845015, -6.651413000000, 2.438400000000,
> !- X,Y,Z 1 {m}
> 3.612983845015, -6.651413000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 4.832183845015, -6.651413000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 4.832183845015, -6.651413000000, 2.438400000000;
> !- X,Y,Z 4 {m}
>
> FenestrationSurface:Detailed,
> 4094D5, !- Name
> Door, !- Surface Type
> Exterior Door, !- Construction Name
> A6D260, !- Building Surface Name
> , !- Outside Boundary Condition Object
> , !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> , !- Multiplier
> 4, !- Number of Vertices
> 1.234017000000, 6.150187000000, 2.438400000000,
> !- X,Y,Z 1 {m}
> 1.234017000000, 6.150187000000, 0.000000000000,
> !- X,Y,Z 2 {m}
> 0.014817000000, 6.150187000000, 0.000000000000,
> !- X,Y,Z 3 {m}
> 0.014817000000, 6.150187000000, 2.438400000000;
> !- X,Y,Z 4 {m}
>
> FenestrationSurface:Detailed,
> 1BEA1A, !- Name
> Window, !- Surface Type
> Exterior Window, !- Construction Name
> 675F2E, !- Building Surface Name
> , !- Outside Boundary Condition Object
> , !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> , !- Multiplier
> 4, !- Number of Vertices
> 0.985668176342, -8.502650000000, 3.077199612370,
> !- X,Y,Z 1 {m}
> 0.985668176342, -8.502650000000, 2.396162112370,
> !- X,Y,Z 2 {m}
> 3.711405676342, -8.502650000000, 2.396162112370,
> !- X,Y,Z 3 {m}
> 3.711405676342, -8.502650000000, 3.077199612370;
> !- X,Y,Z 4 {m}
>
> FenestrationSurface:Detailed,
> EF8DAA, !- Name
> Window, !- Surface Type
> Exterior Window, !- Construction Name
> 675F2E, !- Building Surface Name
> , !- Outside Boundary Condition Object
> , !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> , !- Multiplier
> 4, !- Number of Vertices
> 5.977537354277, -8.502650000000, 3.026059274809,
> !- X,Y,Z 1 {m}
> 5.977537354277, -8.502650000000, 2.329146774809,
> !- X,Y,Z 2 {m}
> 8.871549854277, -8.502650000000, 2.329146774809,
> !- X,Y,Z 3 {m}
> 8.871549854277, -8.502650000000, 3.026059274809;
> !- X,Y,Z 4 {m}
>
> FenestrationSurface:Detailed,
> C2C493, !- Name
> Window, !- Surface Type
> Exterior Window, !- Construction Name
> 675F2E, !- Building Surface Name
> , !- Outside Boundary Condition Object
> , !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> , !- Multiplier
> 4, !- Number of Vertices
> 11.307758181583, -8.502650000000, 3.012231231344,
> !- X,Y,Z 1 {m}
> 11.307758181583, -8.502650000000, 2.288331231344,
> !- X,Y,Z 2 {m}
> 13.689008181583, -8.502650000000, 2.288331231344,
> !- X,Y,Z 3 {m}
> 13.689008181583, -8.502650000000, 3.012231231344;
> !- X,Y,Z 4 {m}
>
> People,
> GARAGEPPL, !- Name
> GARAGE, !- Zone or ZoneList Name
> Always On, !- Number of People Schedule Name
> People, !- Number of People Calculation Method
> 1, !- Number of People
> , !- People per Zone Floor Area {person/m2}
> , !- Zone Floor Area per Person {m2/person}
> 0.3, !- Fraction Radiant
> autocalculate, !- Sensible Heat Fraction
> Office Activity Schedule,!- Activity Level Schedule Name
> 3.82E-08, !- Carbon Dioxide Generation Rate {m3/s-W}
> No, !- Enable ASHRAE 55 Comfort Warnings
> ZoneAveraged; !- Mean Radiant Temperature Calculation Type
>
> People,
> CONFPPL, !- Name
> CONFERENCE, !- Zone or ZoneList Name
> Always On, !- Number of People Schedule Name
> People, !- Number of People Calculation Method
> 1, !- Number of People
> , !- People per Zone Floor Area {person/m2}
> , !- Zone Floor Area per Person {m2/person}
> 0.3, !- Fraction Radiant
> autocalculate, !- Sensible Heat Fraction
> Office Activity Schedule,!- Activity Level Schedule Name
> 3.82E-08, !- Carbon Dioxide Generation Rate {m3/s-W}
> No, !- Enable ASHRAE 55 Comfort Warnings
> ZoneAveraged; !- Mean Radiant Temperature Calculation Type
>
> People,
> EASTPPL, !- Name
> EAST, !- Zone or ZoneList Name
> Always On, !- Number of People Schedule Name
> People, !- Number of People Calculation Method
> 1, !- Number of People
> , !- People per Zone Floor Area {person/m2}
> , !- Zone Floor Area per Person {m2/person}
> 0.3, !- Fraction Radiant
> autocalculate, !- Sensible Heat Fraction
> Office Activity Schedule,!- Activity Level Schedule Name
> 3.82E-08, !- Carbon Dioxide Generation Rate {m3/s-W}
> No, !- Enable ASHRAE 55 Comfort Warnings
> ZoneAveraged; !- Mean Radiant Temperature Calculation Type
>
> People,
> OPENPPL, !- Name
> OPEN, !- Zone or ZoneList Name
> Always On, !- Number of People Schedule Name
> People, !- Number of People Calculation Method
> 1, !- Number of People
> , !- People per Zone Floor Area {person/m2}
> , !- Zone Floor Area per Person {m2/person}
> 0.3, !- Fraction Radiant
> autocalculate, !- Sensible Heat Fraction
> Office Activity Schedule,!- Activity Level Schedule Name
> 3.82E-08, !- Carbon Dioxide Generation Rate {m3/s-W}
> No, !- Enable ASHRAE 55 Comfort Warnings
> ZoneAveraged; !- Mean Radiant Temperature Calculation Type
>
> Lights,
> EASTLIGHTS, !- Name
> EAST, !- Zone or ZoneList Name
> Office Lights Schedule, !- Schedule Name
> Watts/Area, !- Design Level Calculation Method
> , !- Lighting Level {W}
> 5.38248051935761, !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> , !- Return Air Fraction
> , !- Fraction Radiant
> , !- Fraction Visible
> 1, !- Fraction Replaceable
> General, !- End-Use Subcategory
> No; !- Return Air Fraction Calculated from Plenum Temperature
>
> Lights,
> CONFLIGHTS, !- Name
> CONFERENCE, !- Zone or ZoneList Name
> Office Lights Schedule, !- Schedule Name
> Watts/Area, !- Design Level Calculation Method
> , !- Lighting Level {W}
> 5.38248051935761, !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> , !- Return Air Fraction
> , !- Fraction Radiant
> , !- Fraction Visible
> 1, !- Fraction Replaceable
> General, !- End-Use Subcategory
> No; !- Return Air Fraction Calculated from Plenum Temperature
>
> Lights,
> OPENLIGHTS, !- Name
> OPEN, !- Zone or ZoneList Name
> Office Lights Schedule, !- Schedule Name
> Watts/Area, !- Design Level Calculation Method
> , !- Lighting Level {W}
> 5.38248051935761, !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> , !- Return Air Fraction
> , !- Fraction Radiant
> , !- Fraction Visible
> 1, !- Fraction Replaceable
> General, !- End-Use Subcategory
> No; !- Return Air Fraction Calculated from Plenum Temperature
>
> ElectricEquipment,
> Humidifier, !- Name
> EAST, !- Zone or ZoneList Name
> Always On, !- Schedule Name
> EquipmentLevel, !- Design Level Calculation Method
> 100, !- Design Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> , !- Fraction Latent
> , !- Fraction Radiant
> , !- Fraction Lost
> General; !- End-Use Subcategory
>
> ElectricEquipment,
> Aquarium, !- Name
> EAST, !- Zone or ZoneList Name
> Always On, !- Schedule Name
> EquipmentLevel, !- Design Level Calculation Method
> 3000, !- Design Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> , !- Fraction Latent
> , !- Fraction Radiant
> , !- Fraction Lost
> General; !- End-Use Subcategory
>
> ElectricEquipment,
> Computers, !- Name
> OPEN, !- Zone or ZoneList Name
> Office Equipment Schedule, !- Schedule Name
> EquipmentLevel, !- Design Level Calculation Method
> 1000, !- Design Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> , !- Fraction Latent
> , !- Fraction Radiant
> , !- Fraction Lost
> General; !- End-Use Subcategory
>
> ElectricEquipment,
> Freezers, !- Name
> OPEN, !- Zone or ZoneList Name
> Always On, !- Schedule Name
> EquipmentLevel, !- Design Level Calculation Method
> 2760, !- Design Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> , !- Fraction Latent
> , !- Fraction Radiant
> , !- Fraction Lost
> General; !- End-Use Subcategory
>
> GasEquipment,
> InsulationLoss, !- Name
> GARAGE, !- Zone or ZoneList Name
> Always On, !- Schedule Name
> Watts/Area, !- Design Level Calculation Method
> , !- Design Level {W}
> 26.8175004435692, !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/Person}
> , !- Fraction Latent
> , !- Fraction Radiant
> , !- Fraction Lost
> , !- Carbon Dioxide Generation Rate {m3/s-W}
> General; !- End-Use Subcategory
>
> Schedule:Compact,
> ON, !- Name
> FRACTION, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 1.00; !- Field 4
>
> Schedule:Compact,
> SEASONAL RESET SUPPLY AIR TEMP SCH, !- Name
> TEMPERATURE, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 13; !- Field 4
>
> Schedule:Compact,
> HEATING COIL SUPPLY AIR TEMP SCH, !- Name
> TEMPERATURE, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 60.00; !- Field 4
>
> Schedule:Compact,
> CW LOOP TEMP SCHEDULE, !- Name
> TEMPERATURE, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 6.67; !- Field 4
>
> Schedule:Compact,
> HW LOOP TEMP SCHEDULE, !- Name
> TEMPERATURE, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 80.00; !- Field 4
>
> Schedule:Compact,
> HEATING COOLING SETPOINTS, !- Name
> TEMPERATURE, !- Schedule Type Limits Name
> Through: 3/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 7:00, 22, !- Field 4
> Until: 17:00, 22.00, !- Field 6
> Until: 24:00, 22, !- Field 8
> Through: 9/30, !- Field 9
> For: AllDays, !- Field 10
> Until: 7:00, 22, !- Field 12
> Until: 17:00, 22, !- Field 14
> Until: 24:00, 22, !- Field 16
> Through: 12/31, !- Field 17
> For: AllDays, !- Field 18
> Until: 7:00, 22, !- Field 20
> Until: 17:00, 22.00, !- Field 22
> Until: 24:00, 22; !- Field 24
>
> Schedule:Compact,
> ZONE CONTROL TYPE SCHED, !- Name
> CONTROL TYPE, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00, 4; !- Field 4
>
> Version,6.0;
>
> Building,
> NRRA, !- Name
> 0, !- North Axis {deg}
> Suburbs, !- Terrain
> 3.9999999E-02, !- Loads Convergence Tolerance Value
> 0.4000000, !- Temperature Convergence Tolerance Value {deltaC}
> FullInteriorAndExterior, !- Solar Distribution
> 25; !- Maximum Number of Warmup Days
>
> Timestep,4;
> SurfaceConvectionAlgorithm:Inside,TARP;
> SurfaceConvectionAlgorithm:Outside,DOE-2;
> HeatBalanceAlgorithm,ConductionTransferFunction;
>
> SimulationControl,
> Yes, !- Do Zone Sizing Calculation
> Yes, !- Do System Sizing Calculation
> Yes, !- Do Plant Sizing Calculation
> No, !- Run Simulation for Sizing Periods
> Yes; !- Run Simulation for Weather File Run Periods
>
> NodeList,
> Zone Equipment Inlet Node List, !- Name
> Main Hot Air Inlet, !- Node 1 Name
> Main Cold Air Inlet; !- Node 2 Name
>
> NodeList,
> Air Loop Outlet Node List, !- Name
> Heating Coil Outlet Node,!- Node 1 Name
> Cooling Coil Outlet Node;!- Node 2 Name
>
> NodeList,
> Chilled Water Loop Setpoint Node List, !- Name
> CW Supply Outlet Node; !- Node 1 Name
>
> NodeList,
> Hot Water Loop Setpoint Node List, !- Name
> HW Supply Outlet Node; !- Node 1 Name
>
> NodeList,
> Zone1Inlets, !- Name
> Zone 1 Dual Duct Outlet; !- Node 1 Name
>
> NodeList,
> Zone2Inlets, !- Name
> Zone 2 Dual Duct Outlet; !- Node 1 Name
>
> NodeList,
> Zone3Inlets, !- Name
> Zone 3 Dual Duct Outlet; !- Node 1 Name
>
> NodeList,
> Cooling Coil Supply Air Temp Nodes, !- Name
> Cooling Coil Outlet Node;!- Node 1 Name
>
> NodeList,
> Heating Coil Supply Air Temp Nodes, !- Name
> Heating Coil Outlet Node;!- Node 1 Name
>
> BranchList,
> Dual Duct Air Loop Branches, !- Name
> Air Loop Main Branch, !- Branch 1 Name
> Heating Coil Air Sys Branch, !- Branch 2 Name
> Cooling Coil Air Sys Branch; !- Branch 3 Name
>
> BranchList,
> Cooling Supply Side Branches, !- Name
> CW Pump Branch, !- Branch 1 Name
> Purchased Cooling Branch,!- Branch 2 Name
> Supply Bypass Branch, !- Branch 3 Name
> Cooling Supply Outlet; !- Branch 4 Name
>
> BranchList,
> Cooling Demand Side Branches, !- Name
> Cooling Demand Inlet, !- Branch 1 Name
> Cooling Coil Branch, !- Branch 2 Name
> Demand Bypass Branch, !- Branch 3 Name
> Cooling Demand Outlet; !- Branch 4 Name
>
> BranchList,
> Heating Supply Side Branches, !- Name
> Heating Supply Inlet Branch, !- Branch 1 Name
> Heating Purchased Hot Water Branch, !- Branch 2 Name
> Heating Supply Bypass Branch, !- Branch 3 Name
> Heating Supply Outlet Branch; !- Branch 4 Name
>
> BranchList,
> Heating Demand Side Branches, !- Name
> Reheat Inlet Branch, !- Branch 1 Name
> Heating Coil Branch, !- Branch 2 Name
> Reheat Bypass Branch, !- Branch 3 Name
> Reheat Outlet Branch; !- Branch 4 Name
>
> ConnectorList,
> Dual Duct Connectors, !- Name
> Connector:Splitter, !- Connector 1 Object Type
> DualDuctAirSplitter; !- Connector 1 Name
>
> ConnectorList,
> Cooling Supply Side Connectors, !- Name
> Connector:Splitter, !- Connector 1 Object Type
> CW Loop Splitter, !- Connector 1 Name
> Connector:Mixer, !- Connector 2 Object Type
> CW Loop Mixer; !- Connector 2 Name
>
> ConnectorList,
> Cooling Demand Side Connectors, !- Name
> Connector:Splitter, !- Connector 1 Object Type
> CW Demand Splitter, !- Connector 1 Name
> Connector:Mixer, !- Connector 2 Object Type
> CW Demand Mixer; !- Connector 2 Name
>
> ConnectorList,
> Heating Supply Side Connectors, !- Name
> Connector:Splitter, !- Connector 1 Object Type
> Heating Supply Splitter, !- Connector 1 Name
> Connector:Mixer, !- Connector 2 Object Type
> Heating Supply Mixer; !- Connector 2 Name
>
> ConnectorList,
> Heating Demand Side Connectors, !- Name
> Connector:Splitter, !- Connector 1 Object Type
> Reheat Splitter, !- Connector 1 Name
> Connector:Mixer, !- Connector 2 Object Type
> Reheat Mixer; !- Connector 2 Name
>
> Branch,
> Air Loop Main Branch, !- Name
> 1.3, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Fan:ConstantVolume, !- Component 1 Object Type
> SupplyFan, !- Component 1 Name
> Supply Fan Inlet Node, !- Component 1 Inlet Node Name
> Supply Fan Outlet Node, !- Component 1 Outlet Node Name
> PASSIVE; !- Component 1 Branch Control Type
>
> Branch,
> Heating Coil Air Sys Branch, !- Name
> 1.3, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Coil:Heating:Water, !- Component 1 Object Type
> Main Heating Coil, !- Component 1 Name
> Heating Coil Inlet Node, !- Component 1 Inlet Node Name
> Heating Coil Outlet Node,!- Component 1 Outlet Node Name
> ACTIVE; !- Component 1 Branch Control Type
>
> Branch,
> Cooling Coil Air Sys Branch, !- Name
> 1.3, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Coil:Cooling:Water, !- Component 1 Object Type
> Main Cooling Coil, !- Component 1 Name
> Cooling Coil Inlet Node, !- Component 1 Inlet Node Name
> Cooling Coil Outlet Node,!- Component 1 Outlet Node Name
> ACTIVE; !- Component 1 Branch Control Type
>
> Branch,
> Cooling Demand Inlet, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pipe:Adiabatic, !- Component 1 Object Type
> Demand Side Inlet Pipe, !- Component 1 Name
> CW Demand Inlet Node, !- Component 1 Inlet Node Name
> CW Demand Entrance Pipe Outlet Node, !- Component 1 Outlet Node Name
> PASSIVE; !- Component 1 Branch Control Type
>
> Branch,
> Cooling Coil Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Coil:Cooling:Water, !- Component 1 Object Type
> Main Cooling Coil, !- Component 1 Name
> Cooling Coil Water Inlet Node, !- Component 1 Inlet Node Name
> Cooling Coil Water Outlet Node, !- Component 1 Outlet Node Name
> Active; !- Component 1 Branch Control Type
>
> Branch,
> Demand Bypass Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pipe:Adiabatic, !- Component 1 Object Type
> Demand Side Bypass, !- Component 1 Name
> CW Demand Bypass Inlet Node, !- Component 1 Inlet Node Name
> CW Demand Bypass Outlet Node, !- Component 1 Outlet Node Name
> BYPASS; !- Component 1 Branch Control Type
>
> Branch,
> Cooling Demand Outlet, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pipe:Adiabatic, !- Component 1 Object Type
> CW Demand Side Outlet Pipe, !- Component 1 Name
> CW Demand Exit Pipe Inlet Node, !- Component 1 Inlet Node Name
> CW Demand Outlet Node, !- Component 1 Outlet Node Name
> PASSIVE; !- Component 1 Branch Control Type
>
> Branch,
> Cooling Supply Outlet, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pipe:Adiabatic, !- Component 1 Object Type
> Supply Side Outlet Pipe, !- Component 1 Name
> Supply Side Exit Pipe Inlet Node, !- Component 1 Inlet Node Name
> CW Supply Outlet Node, !- Component 1 Outlet Node Name
> PASSIVE; !- Component 1 Branch Control Type
>
> Branch,
> CW Pump Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pump:VariableSpeed, !- Component 1 Object Type
> Circ Pump, !- Component 1 Name
> CW Supply Inlet Node, !- Component 1 Inlet Node Name
> CW Pump Outlet Node, !- Component 1 Outlet Node Name
> Active; !- Component 1 Branch Control Type
>
> Branch,
> Purchased Cooling Branch,!- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> DistrictCooling, !- Component 1 Object Type
> Purchased Cooling, !- Component 1 Name
> Purchased Cooling Inlet Node, !- Component 1 Inlet Node Name
> Purchased Cooling Outlet Node, !- Component 1 Outlet Node Name
> Active; !- Component 1 Branch Control Type
>
> Branch,
> Supply Bypass Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pipe:Adiabatic, !- Component 1 Object Type
> Supply Side Bypass, !- Component 1 Name
> CW Supply Bypass Inlet Node, !- Component 1 Inlet Node Name
> CW Supply Bypass Outlet Node, !- Component 1 Outlet Node Name
> BYPASS; !- Component 1 Branch Control Type
>
> Branch,
> Heating Supply Inlet Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pump:VariableSpeed, !- Component 1 Object Type
> HW Circ Pump, !- Component 1 Name
> HW Supply Inlet Node, !- Component 1 Inlet Node Name
> HW Pump Outlet Node, !- Component 1 Outlet Node Name
> ACTIVE; !- Component 1 Branch Control Type
>
> Branch,
> Heating Purchased Hot Water Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> DistrictHeating, !- Component 1 Object Type
> Purchased Heating, !- Component 1 Name
> Purchased Heat Inlet Node, !- Component 1 Inlet Node Name
> Purchased Heat Outlet Node, !- Component 1 Outlet Node Name
> ACTIVE; !- Component 1 Branch Control Type
>
> Branch,
> Heating Supply Bypass Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pipe:Adiabatic, !- Component 1 Object Type
> Heating Supply Side Bypass, !- Component 1 Name
> Heating Supply Bypass Inlet Node, !- Component 1 Inlet Node Name
> Heating Supply Bypass Outlet Node, !- Component 1 Outlet Node Name
> BYPASS; !- Component 1 Branch Control Type
>
> Branch,
> Heating Supply Outlet Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pipe:Adiabatic, !- Component 1 Object Type
> Heating Supply Outlet, !- Component 1 Name
> Heating Supply Exit Pipe Inlet Node, !- Component 1 Inlet Node Name
> HW Supply Outlet Node, !- Component 1 Outlet Node Name
> PASSIVE; !- Component 1 Branch Control Type
>
> Branch,
> Reheat Inlet Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pipe:Adiabatic, !- Component 1 Object Type
> Reheat Inlet Pipe, !- Component 1 Name
> HW Demand Inlet Node, !- Component 1 Inlet Node Name
> HW Demand Entrance Pipe Outlet Node, !- Component 1 Outlet Node Name
> PASSIVE; !- Component 1 Branch Control Type
>
> Branch,
> Reheat Outlet Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pipe:Adiabatic, !- Component 1 Object Type
> Reheat Outlet Pipe, !- Component 1 Name
> HW Demand Exit Pipe Inlet Node, !- Component 1 Inlet Node Name
> HW Demand Outlet Node, !- Component 1 Outlet Node Name
> PASSIVE; !- Component 1 Branch Control Type
>
> Branch,
> Heating Coil Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Coil:Heating:Water, !- Component 1 Object Type
> Main Heating Coil, !- Component 1 Name
> Heating Coil Water Inlet,!- Component 1 Inlet Node Name
> Heating Coil Water Outlet, !- Component 1 Outlet Node Name
> ACTIVE; !- Component 1 Branch Control Type
>
> Branch,
> Reheat Bypass Branch, !- Name
> 0, !- Maximum Flow Rate {m3/s}
> , !- Pressure Drop Curve Name
> Pipe:Adiabatic, !- Component 1 Object Type
> Reheat Bypass, !- Component 1 Name
> Reheat Bypass Inlet Node,!- Component 1 Inlet Node Name
> Reheat Bypass Outlet Node, !- Component 1 Outlet Node Name
> BYPASS; !- Component 1 Branch Control Type
>
> Pipe:Adiabatic,
> Demand Side Inlet Pipe, !- Name
> CW Demand Inlet Node, !- Inlet Node Name
> CW Demand Entrance Pipe Outlet Node; !- Outlet Node Name
>
> Pipe:Adiabatic,
> Demand Side Bypass, !- Name
> CW Demand Bypass Inlet Node, !- Inlet Node Name
> CW Demand Bypass Outlet Node; !- Outlet Node Name
>
> Pipe:Adiabatic,
> CW Demand Side Outlet Pipe, !- Name
> CW Demand Exit Pipe Inlet Node, !- Inlet Node Name
> CW Demand Outlet Node; !- Outlet Node Name
>
> Pipe:Adiabatic,
> Supply Side Outlet Pipe, !- Name
> Supply Side Exit Pipe Inlet Node, !- Inlet Node Name
> CW Supply Outlet Node; !- Outlet Node Name
>
> Pipe:Adiabatic,
> Supply Side Bypass, !- Name
> CW Supply Bypass Inlet Node, !- Inlet Node Name
> CW Supply Bypass Outlet Node; !- Outlet Node Name
>
> Pipe:Adiabatic,
> Heating Supply Side Bypass, !- Name
> Heating Supply Bypass Inlet Node, !- Inlet Node Name
> Heating Supply Bypass Outlet Node; !- Outlet Node Name
>
> Pipe:Adiabatic,
> Heating Supply Outlet, !- Name
> Heating Supply Exit Pipe Inlet Node, !- Inlet Node Name
> HW Supply Outlet Node; !- Outlet Node Name
>
> Pipe:Adiabatic,
> Reheat Inlet Pipe, !- Name
> HW Demand Inlet Node, !- Inlet Node Name
> HW Demand Entrance Pipe Outlet Node; !- Outlet Node Name
>
> Pipe:Adiabatic,
> Reheat Outlet Pipe, !- Name
> HW Demand Exit Pipe Inlet Node, !- Inlet Node Name
> HW Demand Outlet Node; !- Outlet Node Name
>
> Pipe:Adiabatic,
> Reheat Bypass, !- Name
> Reheat Bypass Inlet Node,!- Inlet Node Name
> Reheat Bypass Outlet Node; !- Outlet Node Name
>
> PlantLoop,
> Chilled Water Loop, !- Name
> Water, !- Fluid Type
> CW Loop Operation, !- Plant Equipment Operation Scheme Name
> CW Supply Outlet Node, !- Loop Temperature Setpoint Node Name
> 98, !- Maximum Loop Temperature {C}
> 1, !- Minimum Loop Temperature {C}
> 0.0011, !- Maximum Loop Flow Rate {m3/s}
> 0, !- Minimum Loop Flow Rate {m3/s}
> autocalculate, !- Plant Loop Volume {m3}
> CW Supply Inlet Node, !- Plant Side Inlet Node Name
> CW Supply Outlet Node, !- Plant Side Outlet Node Name
> Cooling Supply Side Branches, !- Plant Side Branch List Name
> Cooling Supply Side Connectors, !- Plant Side Connector List Name
> CW Demand Inlet Node, !- Demand Side Inlet Node Name
> CW Demand Outlet Node, !- Demand Side Outlet Node Name
> Cooling Demand Side Branches, !- Demand Side Branch List Name
> Cooling Demand Side Connectors, !- Demand Side Connector List Name
> Optimal; !- Load Distribution Scheme
>
> PlantLoop,
> Hot Water Loop, !- Name
> Water, !- Fluid Type
> Hot Loop Operation, !- Plant Equipment Operation Scheme Name
> HW Supply Outlet Node, !- Loop Temperature Setpoint Node Name
> 100, !- Maximum Loop Temperature {C}
> 10, !- Minimum Loop Temperature {C}
> 0.0043, !- Maximum Loop Flow Rate {m3/s}
> 0, !- Minimum Loop Flow Rate {m3/s}
> autocalculate, !- Plant Loop Volume {m3}
> HW Supply Inlet Node, !- Plant Side Inlet Node Name
> HW Supply Outlet Node, !- Plant Side Outlet Node Name
> Heating Supply Side Branches, !- Plant Side Branch List Name
> Heating Supply Side Connectors, !- Plant Side Connector List Name
> HW Demand Inlet Node, !- Demand Side Inlet Node Name
> HW Demand Outlet Node, !- Demand Side Outlet Node Name
> Heating Demand Side Branches, !- Demand Side Branch List Name
> Heating Demand Side Connectors, !- Demand Side Connector List Name
> Optimal; !- Load Distribution Scheme
>
> PlantEquipmentOperationSchemes,
> CW Loop Operation, !- Name
> PlantEquipmentOperation:CoolingLoad, !- Control Scheme 1 Object Type
> Cooling, !- Control Scheme 1 Name
> Always On; !- Control Scheme 1 Schedule Name
>
> PlantEquipmentOperationSchemes,
> Hot Loop Operation, !- Name
> PlantEquipmentOperation:HeatingLoad, !- Control Scheme 1 Object Type
> Heating, !- Control Scheme 1 Name
> Always On; !- Control Scheme 1 Schedule Name
>
> PlantEquipmentOperation:CoolingLoad,
> Cooling, !- Name
> 0, !- Load Range 1 Lower Limit {W}
> 1000000, !- Load Range 1 Upper Limit {W}
> AllCool; !- Range 1 Equipment List Name
>
> PlantEquipmentOperation:HeatingLoad,
> Heating, !- Name
> 0, !- Load Range 1 Lower Limit {W}
> 1000000, !- Load Range 1 Upper Limit {W}
> AllHeat; !- Range 1 Equipment List Name
>
> PlantEquipmentList,
> AllCool, !- Name
> DistrictCooling, !- Equipment 1 Object Type
> Purchased Cooling; !- Equipment 1 Name
>
> PlantEquipmentList,
> AllHeat, !- Name
> DistrictHeating, !- Equipment 1 Object Type
> Purchased Heating; !- Equipment 1 Name
>
> Connector:Splitter,
> DualDuctAirSplitter, !- Name
> Air Loop Main Branch, !- Inlet Branch Name
> Heating Coil Air Sys Branch, !- Outlet Branch 1 Name
> Cooling Coil Air Sys Branch; !- Outlet Branch 2 Name
>
> Connector:Splitter,
> CW Loop Splitter, !- Name
> CW Pump Branch, !- Inlet Branch Name
> Purchased Cooling Branch,!- Outlet Branch 1 Name
> Supply Bypass Branch; !- Outlet Branch 2 Name
>
> Connector:Splitter,
> CW Demand Splitter, !- Name
> Cooling Demand Inlet, !- Inlet Branch Name
> Demand Bypass Branch, !- Outlet Branch 1 Name
> Cooling Coil Branch; !- Outlet Branch 2 Name
>
> Connector:Splitter,
> Reheat Splitter, !- Name
> Reheat Inlet Branch, !- Inlet Branch Name
> Heating Coil Branch, !- Outlet Branch 1 Name
> Reheat Bypass Branch; !- Outlet Branch 2 Name
>
> Connector:Splitter,
> Heating Supply Splitter, !- Name
> Heating Supply Inlet Branch, !- Inlet Branch Name
> Heating Purchased Hot Water Branch, !- Outlet Branch 1 Name
> Heating Supply Bypass Branch; !- Outlet Branch 2 Name
>
> Connector:Mixer,
> CW Loop Mixer, !- Name
> Cooling Supply Outlet, !- Outlet Branch Name
> Purchased Cooling Branch,!- Inlet Branch 1 Name
> Supply Bypass Branch; !- Inlet Branch 2 Name
>
> Connector:Mixer,
> CW Demand Mixer, !- Name
> Cooling Demand Outlet, !- Outlet Branch Name
> Cooling Coil Branch, !- Inlet Branch 1 Name
> Demand Bypass Branch; !- Inlet Branch 2 Name
>
> Connector:Mixer,
> Reheat Mixer, !- Name
> Reheat Outlet Branch, !- Outlet Branch Name
> Heating Coil Branch, !- Inlet Branch 1 Name
> Reheat Bypass Branch; !- Inlet Branch 2 Name
>
> Connector:Mixer,
> Heating Supply Mixer, !- Name
> Heating Supply Outlet Branch, !- Outlet Branch Name
> Heating Purchased Hot Water Branch, !- Inlet Branch 1 Name
> Heating Supply Bypass Branch; !- Inlet Branch 2 Name
>
> AirLoopHVAC,
> Main Dual Duct Air Loop, !- Name
> Dual Duct System 1 Controllers, !- Controller List Name
> Dual Duct System 1 Schedule List, !- Availability Manager List Name
> 1.3, !- Design Supply Air Flow Rate {m3/s}
> Dual Duct Air Loop Branches, !- Branch List Name
> Dual Duct Connectors, !- Connector List Name
> Supply Fan Inlet Node, !- Supply Side Inlet Node Name
> Return Air Mixer Outlet, !- Demand Side Outlet Node Name
> Zone Equipment Inlet Node List, !- Demand Side Inlet Node Names
> Air Loop Outlet Node List; !- Supply Side Outlet Node Names
>
> AirLoopHVAC:ControllerList,
> Dual Duct System 1 Controllers, !- Name
> Controller:WaterCoil, !- Controller 1 Object Type
> Main Cooling Coil Controller, !- Controller 1 Name
> Controller:WaterCoil, !- Controller 2 Object Type
> Main Heating Coil Controller; !- Controller 2 Name
>
> AvailabilityManagerAssignmentList,
> Dual Duct System 1 Schedule List, !- Name
> AvailabilityManager:Scheduled, !- Availability Manager 1 Object Type
> Dual Duct System 1 Schedule; !- Availability Manager 1 Name
>
> AvailabilityManager:Scheduled,
> Dual Duct System 1 Schedule, !- Name
> Always On; !- Schedule Name
>
> SetpointManager:Scheduled,
> Chilled Water Loop Setpoint Manager, !- Name
> Temperature, !- Control Variable
> CW Loop Temp Schedule, !- Schedule Name
> Chilled Water Loop Setpoint Node List; !- Setpoint Node or NodeList Name
>
> SetpointManager:Scheduled,
> Hot Water Loop Setpoint Manager, !- Name
> Temperature, !- Control Variable
> HW Loop Temp Schedule, !- Schedule Name
> Hot Water Loop Setpoint Node List; !- Setpoint Node or NodeList Name
>
> SetpointManager:Scheduled,
> Supply Air Temp Manager, !- Name
> Temperature, !- Control Variable
> Seasonal Reset Supply Air Temp Sch, !- Schedule Name
> Cooling Coil Supply Air Temp Nodes; !- Setpoint Node or NodeList Name
>
> SetpointManager:Scheduled,
> Heating Coil Supply Air Temp Manager, !- Name
> Temperature, !- Control Variable
> Heating Coil Supply Air Temp Sch, !- Schedule Name
> Heating Coil Supply Air Temp Nodes; !- Setpoint Node or NodeList Name
>
> Controller:WaterCoil,
> Main Cooling Coil Controller, !- Name
> Temperature, !- Control Variable
> Normal, !- Action
> FLOW, !- Actuator Variable
> Cooling Coil Outlet Node,!- Sensor Node Name
> Cooling Coil Water Inlet Node, !- Actuator Node Name
> 0.001, !- Controller Convergence Tolerance {deltaC}
> 0.0011, !- Maximum Actuated Flow {m3/s}
> 0.0; !- Minimum Actuated Flow {m3/s}
>
> Controller:WaterCoil,
> Main Heating Coil Controller, !- Name
> Temperature, !- Control Variable
> Normal, !- Action
> FLOW, !- Actuator Variable
> Heating Coil Outlet Node,!- Sensor Node Name
> Heating Coil Water Inlet,!- Actuator Node Name
> 0.001, !- Controller Convergence Tolerance {deltaC}
> 0.0043, !- Maximum Actuated Flow {m3/s}
> 0.0; !- Minimum Actuated Flow {m3/s}
>
> ZoneHVAC:EquipmentConnections,
> CONFERENCE, !- Zone Name
> Zone1Equipment, !- Zone Conditioning Equipment List Name
> Zone1Inlets, !- Zone Air Inlet Node or NodeList Name
> , !- Zone Air Exhaust Node or NodeList Name
> Zone 1 Node, !- Zone Air Node Name
> Zone 1 Outlet Node; !- Zone Return Air Node Name
>
> ZoneHVAC:EquipmentConnections,
> EAST, !- Zone Name
> Zone2Equipment, !- Zone Conditioning Equipment List Name
> Zone2Inlets, !- Zone Air Inlet Node or NodeList Name
> , !- Zone Air Exhaust Node or NodeList Name
> Zone 2 Node, !- Zone Air Node Name
> Zone 2 Outlet Node; !- Zone Return Air Node Name
>
> ZoneHVAC:EquipmentConnections,
> OPEN, !- Zone Name
> Zone3Equipment, !- Zone Conditioning Equipment List Name
> Zone3Inlets, !- Zone Air Inlet Node or NodeList Name
> , !- Zone Air Exhaust Node or NodeList Name
> Zone 3 Node, !- Zone Air Node Name
> Zone 3 Outlet Node; !- Zone Return Air Node Name
>
> ZoneHVAC:EquipmentList,
> Zone1Equipment, !- Name
> ZoneHVAC:AirDistributionUnit, !- Zone Equipment 1 Object Type
> Zone1DualDuct, !- Zone Equipment 1 Name
> 1, !- Zone Equipment 1 Cooling Sequence
> 1; !- Zone Equipment 1 Heating or No-Load Sequence
>
> ZoneHVAC:EquipmentList,
> Zone2Equipment, !- Name
> ZoneHVAC:AirDistributionUnit, !- Zone Equipment 1 Object Type
> Zone2DualDuct, !- Zone Equipment 1 Name
> 1, !- Zone Equipment 1 Cooling Sequence
> 1; !- Zone Equipment 1 Heating or No-Load Sequence
>
> ZoneHVAC:EquipmentList,
> Zone3Equipment, !- Name
> ZoneHVAC:AirDistributionUnit, !- Zone Equipment 1 Object Type
> Zone3DualDuct, !- Zone Equipment 1 Name
> 1, !- Zone Equipment 1 Cooling Sequence
> 1; !- Zone Equipment 1 Heating or No-Load Sequence
>
> ZoneHVAC:AirDistributionUnit,
> Zone1DualDuct, !- Name
> Zone 1 Dual Duct Outlet, !- Air Distribution Unit Outlet Node Name
> AirTerminal:DualDuct:ConstantVolume, !- Air Terminal Object Type
> Zone1MixDamp; !- Air Terminal Name
>
> ZoneHVAC:AirDistributionUnit,
> Zone2DualDuct, !- Name
> Zone 2 Dual Duct Outlet, !- Air Distribution Unit Outlet Node Name
> AirTerminal:DualDuct:ConstantVolume, !- Air Terminal Object Type
> Zone2MixDamp; !- Air Terminal Name
>
> ZoneHVAC:AirDistributionUnit,
> Zone3DualDuct, !- Name
> Zone 3 Dual Duct Outlet, !- Air Distribution Unit Outlet Node Name
> AirTerminal:DualDuct:ConstantVolume, !- Air Terminal Object Type
> Zone3MixDamp; !- Air Terminal Name
>
> AirTerminal:DualDuct:ConstantVolume,
> Zone1MixDamp, !- Name
> Always On, !- Availability Schedule Name
> Zone 1 Dual Duct Outlet, !- Air Outlet Node Name
> Zone 1 Dual Duct Hot Inlet, !- Hot Air Inlet Node Name
> Zone 1 Dual Duct Cold Inlet, !- Cold Air Inlet Node Name
> autosize; !- Maximum Air Flow Rate {m3/s}
>
> AirTerminal:DualDuct:ConstantVolume,
> Zone2MixDamp, !- Name
> Always On, !- Availability Schedule Name
> Zone 2 Dual Duct Outlet, !- Air Outlet Node Name
> Zone 2 Dual Duct Hot Inlet, !- Hot Air Inlet Node Name
> Zone 2 Dual Duct Cold Inlet, !- Cold Air Inlet Node Name
> autosize; !- Maximum Air Flow Rate {m3/s}
>
> AirTerminal:DualDuct:ConstantVolume,
> Zone3MixDamp, !- Name
> Always On, !- Availability Schedule Name
> Zone 3 Dual Duct Outlet, !- Air Outlet Node Name
> Zone 3 Dual Duct Hot Inlet, !- Hot Air Inlet Node Name
> Zone 3 Dual Duct Cold Inlet, !- Cold Air Inlet Node Name
> autosize; !- Maximum Air Flow Rate {m3/s}
>
> ZoneControl:Thermostat,
> Zone 1 Thermostat, !- Name
> CONFERENCE, !- Zone or ZoneList Name
> Zone Control Type Sched, !- Control Type Schedule Name
> ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type
> Heating Cooling Setpoint Sched; !- Control 1 Name
>
> ZoneControl:Thermostat,
> Zone 2 Thermostat, !- Name
> EAST, !- Zone or ZoneList Name
> Zone Control Type Sched, !- Control Type Schedule Name
> ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type
> Heating Cooling Setpoint Sched; !- Control 1 Name
>
> ZoneControl:Thermostat,
> Zone 3 Thermostat, !- Name
> OPEN, !- Zone or ZoneList Name
> Zone Control Type Sched, !- Control Type Schedule Name
> ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type
> Heating Cooling Setpoint Sched; !- Control 1 Name
>
> AirLoopHVAC:SupplyPath,
> HotAirSupplyPath, !- Name
> Main Hot Air Inlet, !- Supply Air Path Inlet Node Name
> AirLoopHVAC:ZoneSplitter,!- Component 1 Object Type
> ZoneHotAirSupplySplitter;!- Component 1 Name
>
> AirLoopHVAC:SupplyPath,
> ColdAirSupplyPath, !- Name
> Main Cold Air Inlet, !- Supply Air Path Inlet Node Name
> AirLoopHVAC:ZoneSplitter,!- Component 1 Object Type
> ZoneColdAirSupplySplitter; !- Component 1 Name
>
> AirLoopHVAC:ReturnPath,
> DualDuctReturnPath, !- Name
> Return Air Mixer Outlet, !- Return Air Path Outlet Node Name
> AirLoopHVAC:ZoneMixer, !- Component 1 Object Type
> ZoneReturnAirMixer; !- Component 1 Name
>
> AirLoopHVAC:ZoneSplitter,
> ZoneColdAirSupplySplitter, !- Name
> Main Cold Air Inlet, !- Inlet Node Name
> Zone 1 Dual Duct Cold Inlet, !- Outlet 1 Node Name
> Zone 2 Dual Duct Cold Inlet, !- Outlet 2 Node Name
> Zone 3 Dual Duct Cold Inlet; !- Outlet 3 Node Name
>
> AirLoopHVAC:ZoneSplitter,
> ZoneHotAirSupplySplitter,!- Name
> Main Hot Air Inlet, !- Inlet Node Name
> Zone 1 Dual Duct Hot Inlet, !- Outlet 1 Node Name
> Zone 2 Dual Duct Hot Inlet, !- Outlet 2 Node Name
> Zone 3 Dual Duct Hot Inlet; !- Outlet 3 Node Name
>
> AirLoopHVAC:ZoneMixer,
> ZoneReturnAirMixer, !- Name
> Return Air Mixer Outlet, !- Outlet Node Name
> Zone 1 Outlet Node, !- Inlet 1 Node Name
> Zone 2 Outlet Node, !- Inlet 2 Node Name
> Zone 3 Outlet Node; !- Inlet 3 Node Name
>
> DistrictCooling,
> Purchased Cooling, !- Name
> Purchased Cooling Inlet Node, !- Chilled Water Inlet Node Name
> Purchased Cooling Outlet Node, !- Chilled Water Outlet Node Name
> 999999999744375; !- Nominal Capacity {W}
>
> DistrictHeating,
> Purchased Heating, !- Name
> Purchased Heat Inlet Node, !- Hot Water Inlet Node Name
> Purchased Heat Outlet Node, !- Hot Water Outlet Node Name
> 999999999744375; !- Nominal Capacity {W}
>
> Pump:VariableSpeed,
> Circ Pump, !- Name
> CW Supply Inlet Node, !- Inlet Node Name
> CW Pump Outlet Node, !- Outlet Node Name
> 0.0011, !- Rated Flow Rate {m3/s}
> 300000, !- Rated Pump Head {Pa}
> 500, !- Rated Power Consumption {W}
> 0.87, !- Motor Efficiency
> 0.0, !- Fraction of Motor Inefficiencies to Fluid Stream
> 0, !- Coefficient 1 of the Part Load Performance Curve
> 1, !- Coefficient 2 of the Part Load Performance Curve
> 0, !- Coefficient 3 of the Part Load Performance Curve
> 0, !- Coefficient 4 of the Part Load Performance Curve
> 0, !- Minimum Flow Rate {m3/s}
> INTERMITTENT; !- Pump Control Type
>
> Pump:VariableSpeed,
> HW Circ Pump, !- Name
> HW Supply Inlet Node, !- Inlet Node Name
> HW Pump Outlet Node, !- Outlet Node Name
> 0.0043, !- Rated Flow Rate {m3/s}
> 300000, !- Rated Pump Head {Pa}
> 2000, !- Rated Power Consumption {W}
> 0.87, !- Motor Efficiency
> 0.0, !- Fraction of Motor Inefficiencies to Fluid Stream
> 0, !- Coefficient 1 of the Part Load Performance Curve
> 1, !- Coefficient 2 of the Part Load Performance Curve
> 0, !- Coefficient 3 of the Part Load Performance Curve
> 0, !- Coefficient 4 of the Part Load Performance Curve
> 0, !- Minimum Flow Rate {m3/s}
> INTERMITTENT; !- Pump Control Type
>
> Coil:Heating:Water,
> Main Heating Coil, !- Name
> Always On, !- Availability Schedule Name
> 1200.0, !- U-Factor Times Area Value {W/K}
> 0.0043, !- Maximum Water Flow Rate {m3/s}
> Heating Coil Water Inlet,!- Water Inlet Node Name
> Heating Coil Water Outlet, !- Water Outlet Node Name
> Heating Coil Inlet Node, !- Air Inlet Node Name
> Heating Coil Outlet Node,!- Air Outlet Node Name
> UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method
> autosize, !- Rated Capacity {W}
> 82.2, !- Rated Inlet Water Temperature {C}
> 16.6, !- Rated Inlet Air Temperature {C}
> 71.1, !- Rated Outlet Water Temperature {C}
> 32.2, !- Rated Outlet Air Temperature {C}
> ; !- Rated Ratio for Air and Water Convection
>
> Output:VariableDictionary,IDF,Name;
>
> OutputControl:Table:Style,
> HTML, !- Column Separator
> InchPound; !- Unit Conversion
>
> Output:Table:SummaryReports,
> AllSummary; !- Report 1 Name
>
Well I didn't mean for the IDF to actually print in the message, I tried attaching it as a file. How do you attach things for this message board?
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/