[EnergyPlus_Support] Re: IDF Review for no Cooling
I removed all but two of the Design Day Conditions, and adjusted the set points but I am still incompetent and cannot figure out why it will not call for cooling.
Below is the updated IDF:
!-Generator IDFEditor 1.38a
!-Option OriginalOrderTop UseSpecialFormat ViewInIPunits
!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
!- Use '!' comments if they need to be retained when using the IDFEditor.
ThermostatSetpoint:DualSetpoint,
Heating Cooling Setpoint Sched, !- Name
Heating Setpoints, !- Heating Setpoint Temperature Schedule Name
Cooling Setpoints; !- Cooling Setpoint Temperature Schedule Name
Output:Variable,*,System Node Setpoint Temp,Hourly;
Schedule:Compact,
Cooling Setpoints, !- Name
Temperature, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 23; !- Field 4
Output:Variable,*,Zone/Sys Thermostat Heating Setpoint,Hourly;
Sizing:Plant,
Chilled Water Loop, !- Plant or Condenser Loop Name
Cooling, !- Loop Type
7.22222241354578, !- Design Loop Exit Temperature {C}
6.66666684327303; !- Loop Design Temperature Difference {deltaC}
Sizing:Plant,
Hot Water Loop, !- Plant or Condenser Loop Name
Heating, !- Loop Type
82.2222244003673, !- Design Loop Exit Temperature {C}
11.111111405455; !- Loop Design Temperature Difference {deltaC}
Sizing:System,
Main Dual Duct Air Loop, !- AirLoop Name
Sensible, !- Type of Load to Size On
autosize, !- Design Outdoor Air Flow Rate {m3/s}
1, !- Minimum System Air Flow Ratio
29.4444452244559, !- Preheat Design Temperature {C}
0.008, !- Preheat Design Humidity Ratio {kg-H2O/kg-Air}
11.0000002914005, !- Precool Design Temperature {C}
0.008, !- Precool Design Humidity Ratio {kg-H2O/kg-Air}
12.7777781162733, !- Central Cooling Design Supply Air Temperature {C}
29.4444452244559, !- Central Heating Design Supply Air Temperature {C}
NonCoincident, !- Sizing Option
No, !- 100% Outdoor Air in Cooling
No, !- 100% Outdoor Air in Heating
0.008, !- Central Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-Air}
0.008, !- Central Heating Design Supply Air Humidity Ratio {kg-H2O/kg-Air}
DesignDay, !- Cooling Design Air Flow Method
, !- Cooling Design Air Flow Rate {m3/s}
DesignDay, !- Heating Design Air Flow Method
; !- Heating Design Air Flow Rate {m3/s}
Sizing:Zone,
CONFERENCE, !- Zone Name
12.7777781162733, !- Zone Cooling Design Supply Air Temperature {C}
50, !- Zone Heating Design Supply Air Temperature {C}
0.008, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
Flow/Zone, !- Outdoor Air Method
0, !- Outdoor Air Flow per Person {m3/s}
0, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
0, !- Outdoor Air Flow per Zone {m3/s}
1, !- Zone Heating Sizing Factor
1, !- Zone Cooling Sizing Factor
DesignDay, !- Cooling Design Air Flow Method
0, !- Cooling Design Air Flow Rate {m3/s}
, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
0, !- Cooling Minimum Air Flow Fraction
DesignDay, !- Heating Design Air Flow Method
0, !- Heating Design Air Flow Rate {m3/s}
, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
, !- Heating Maximum Air Flow {m3/s}
0; !- Heating Maximum Air Flow Fraction
Sizing:Zone,
EAST, !- Zone Name
12.7777781162733, !- Zone Cooling Design Supply Air Temperature {C}
50, !- Zone Heating Design Supply Air Temperature {C}
0.008, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
Flow/Zone, !- Outdoor Air Method
0, !- Outdoor Air Flow per Person {m3/s}
0, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
0, !- Outdoor Air Flow per Zone {m3/s}
1, !- Zone Heating Sizing Factor
1, !- Zone Cooling Sizing Factor
DesignDay, !- Cooling Design Air Flow Method
0, !- Cooling Design Air Flow Rate {m3/s}
, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
0, !- Cooling Minimum Air Flow Fraction
DesignDay, !- Heating Design Air Flow Method
0, !- Heating Design Air Flow Rate {m3/s}
, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
, !- Heating Maximum Air Flow {m3/s}
0; !- Heating Maximum Air Flow Fraction
Sizing:Zone,
OPEN, !- Zone Name
12.7777781162733, !- Zone Cooling Design Supply Air Temperature {C}
50, !- Zone Heating Design Supply Air Temperature {C}
0.008, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
Flow/Zone, !- Outdoor Air Method
0, !- Outdoor Air Flow per Person {m3/s}
0, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
0, !- Outdoor Air Flow per Zone {m3/s}
1, !- Zone Heating Sizing Factor
1, !- Zone Cooling Sizing Factor
DesignDay, !- Cooling Design Air Flow Method
0, !- Cooling Design Air Flow Rate {m3/s}
, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
0, !- Cooling Minimum Air Flow Fraction
DesignDay, !- Heating Design Air Flow Method
0, !- Heating Design Air Flow Rate {m3/s}
, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
, !- Heating Maximum Air Flow {m3/s}
0; !- Heating Maximum Air Flow Fraction
Coil:Cooling:Water,
Main Cooling Coil, !- Name
Always On, !- Availability Schedule Name
autosize, !- Design Water Flow Rate {m3/s}
autosize, !- Design Air Flow Rate {m3/s}
autosize, !- Design Inlet Water Temperature {C}
autosize, !- Design Inlet Air Temperature {C}
autosize, !- Design Outlet Air Temperature {C}
autosize, !- Design Inlet Air Humidity Ratio {kg-H2O/kg-air}
autosize, !- Design Outlet Air Humidity Ratio {kg-H2O/kg-air}
Cooling Coil Water Inlet Node, !- Water Inlet Node Name
Cooling Coil Water Outlet Node, !- Water Outlet Node Name
Cooling Coil Inlet Node, !- Air Inlet Node Name
Cooling Coil Outlet Node,!- Air Outlet Node Name
SimpleAnalysis, !- Type of Analysis
CrossFlow; !- Heat Exchanger Configuration
Output:Diagnostics,
DisplayUnusedSchedules, !- Key 1
DisplayExtraWarnings; !- Key 2
Fan:ConstantVolume,
SupplyFan, !- Name
Always On, !- Availability Schedule Name
0.7, !- Fan Efficiency
996.355860658514, !- Pressure Rise {Pa}
autosize, !- Maximum Flow Rate {m3/s}
0.9, !- Motor Efficiency
0, !- Motor In Airstream Fraction
Supply Fan Inlet Node, !- Air Inlet Node Name
Supply Fan Outlet Node, !- Air Outlet Node Name
General; !- End-Use Subcategory
Output:SQLite,
SimpleAndTabular; !- Option Type
Output:Variable,*,Zone/Sys Thermostat Cooling Setpoint,Hourly;
Output:Variable,*,System Node Temp,Hourly;
Output:Variable,*,Outdoor Dry Bulb,Hourly;
Output:Variable,*,Zone/Sys Sensible Load Predicted,Hourly;
Output:Variable,*,Zone/Sys Air Temperature,Hourly;
Output:Meter,DistrictHeating:Facility ,Monthly;
Output:Meter,Cooling:DistrictCooling,Monthly;
Output:Meter,Electricity:Building,Monthly;
Site:Location,
Lincoln Municipal Arpt_NE_USA Design_Conditions, !- Name
40.83, !- Latitude {deg}
-96.77, !- Longitude {deg}
-6.0, !- Time Zone {hr}
357.00; !- Elevation {m}
SizingPeriod:DesignDay,
Lincoln Municipal Arpt Ann Htg Wind 99% Condns WS=>MCDB, !- Name
-4, !- Maximum Dry-Bulb Temperature {C}
0.0, !- Daily Temperature Range {deltaC}
-4, !- Humidity Indicating Conditions at Maximum Dry-Bulb
97109., !- Barometric Pressure {Pa}
12.1, !- Wind Speed {m/s}
350, !- Wind Direction {deg}
0.00, !- Sky Clearness
0, !- Rain Indicator
0, !- Snow Indicator
21, !- Day of Month
1, !- Month
WinterDesignDay, !- Day Type
0, !- Daylight Saving Time Indicator
WetBulb; !- Humidity Indicating Type
SizingPeriod:DesignDay,
Lincoln Municipal Arpt Ann Clg .4% Condns DB=>MWB, !- Name
36.2, !- Maximum Dry-Bulb Temperature {C}
12.1, !- Daily Temperature Range {deltaC}
23.9, !- Humidity Indicating Conditions at Maximum Dry-Bulb
97109., !- Barometric Pressure {Pa}
6.6, !- Wind Speed {m/s}
180, !- Wind Direction {deg}
1.00, !- Sky Clearness
0, !- Rain Indicator
0, !- Snow Indicator
21, !- Day of Month
7, !- Month
SummerDesignDay, !- Day Type
0, !- Daylight Saving Time Indicator
WetBulb; !- Humidity Indicating Type
RunPeriod,
, !- Name
1, !- Begin Month
1, !- Begin Day of Month
12, !- End Month
31, !- End Day of Month
USEWEATHERFILE, !- Day of Week for Start Day
Yes, !- Use Weather File Holidays and Special Days
Yes, !- Use Weather File Daylight Saving Period
No, !- Apply Weekend Holiday Rule
Yes, !- Use Weather File Rain Indicators
Yes, !- Use Weather File Snow Indicators
1; !- Number of Times Runperiod to be Repeated
RunPeriodControl:SpecialDays,
New Years Day, !- Name
January 1, !- Start Date
1, !- Duration {days}
Holiday; !- Special Day Type
RunPeriodControl:SpecialDays,
Veterans Day, !- Name
November 11, !- Start Date
1, !- Duration {days}
Holiday; !- Special Day Type
RunPeriodControl:SpecialDays,
Christmas, !- Name
December 25, !- Start Date
1, !- Duration {days}
Holiday; !- Special Day Type
RunPeriodControl:SpecialDays,
Independence Day, !- Name
July 4, !- Start Date
1, !- Duration {days}
Holiday; !- Special Day Type
RunPeriodControl:SpecialDays,
MLK Day, !- Name
3rd Monday in January, !- Start Date
1, !- Duration {days}
Holiday; !- Special Day Type
RunPeriodControl:SpecialDays,
Presidents Day, !- Name
3rd Monday in February, !- Start Date
1, !- Duration {days}
Holiday; !- Special Day Type
RunPeriodControl:SpecialDays,
Memorial Day, !- Name
Last Monday in May, !- Start Date
1, !- Duration {days}
Holiday; !- Special Day Type
RunPeriodControl:SpecialDays,
Labor Day, !- Name
1st Monday in September, !- Start Date
1, !- Duration {days}
Holiday; !- Special Day Type
RunPeriodControl:SpecialDays,
Columbus Day, !- Name
2nd Monday in October, !- Start Date
1, !- Duration {days}
Holiday; !- Special Day Type
RunPeriodControl:SpecialDays,
Thanksgiving, !- Name
4th Thursday in November,!- Start Date
1, !- Duration {days}
Holiday; !- Special Day Type
RunPeriodControl:DaylightSavingTime,
1st Sunday in April, !- Start Date
Last Sunday in October; !- End Date
Site:GroundTemperature:BuildingSurface,18,18,18,18,18,18,18,18,18,18,18,18;
Site:GroundTemperature:Shallow,13,13,13,13,13,13,13,13,13,13,13,13;
Site:GroundTemperature:Deep,16,16,16,16,16,16,16,16,16,16,16,16;
Schedule:Compact,
Office Lights Schedule, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays, !- Field 2
Until: 05:00, 0.05, !- Field 4
Until: 07:00, 0.1, !- Field 6
Until: 08:00, 0.3, !- Field 8
Until: 17:00, 0.9, !- Field 10
Until: 18:00, 0.5, !- Field 12
Until: 20:00, 0.3, !- Field 14
Until: 22:00, 0.2, !- Field 16
Until: 23:00, 0.1, !- Field 18
Until: 24:00, 0.05, !- Field 20
For: SummerDesignDay, !- Field 21
Until: 24:00, 1.0, !- Field 23
For: Saturday, !- Field 24
Until: 06:00, 0.05, !- Field 26
Until: 08:00, 0.1, !- Field 28
Until: 12:00, 0.3, !- Field 30
Until: 17:00, 0.15, !- Field 32
Until: 24:00, 0.05, !- Field 34
For: WinterDesignDay, !- Field 35
Until: 24:00, 0.0, !- Field 37
For: Sunday Holidays AllOtherDays, !- Field 38
Until: 24:00, 0.05; !- Field 40
Schedule:Compact,
Office Equipment Schedule, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays, !- Field 2
Until: 08:00, 0.40, !- Field 4
Until: 12:00, 0.90, !- Field 6
Until: 13:00, 0.80, !- Field 8
Until: 17:00, 0.90, !- Field 10
Until: 18:00, 0.50, !- Field 12
Until: 24:00, 0.40, !- Field 14
For: SummerDesignDay, !- Field 15
Until: 24:00, 1.0, !- Field 17
For: Saturday, !- Field 18
Until: 06:00, 0.30, !- Field 20
Until: 08:00, 0.4, !- Field 22
Until: 12:00, 0.5, !- Field 24
Until: 17:00, 0.35, !- Field 26
Until: 24:00, 0.30, !- Field 28
For: WinterDesignDay, !- Field 29
Until: 24:00, 0.0, !- Field 31
For: Sunday Holidays AllOtherDays, !- Field 32
Until: 24:00, 0.30; !- Field 34
Schedule:Compact,
Office Occupancy Schedule, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays, !- Field 2
Until: 06:00, 0.0, !- Field 4
Until: 07:00, 0.1, !- Field 6
Until: 08:00, 0.2, !- Field 8
Until: 12:00, 0.95, !- Field 10
Until: 13:00, 0.5, !- Field 12
Until: 17:00, 0.95, !- Field 14
Until: 18:00, 0.3, !- Field 16
Until: 20:00, 0.1, !- Field 18
Until: 24:00, 0.05, !- Field 20
For: SummerDesignDay, !- Field 21
Until: 06:00, 0.0, !- Field 23
Until: 22:00, 1.0, !- Field 25
Until: 24:00, 0.05, !- Field 27
For: Saturday, !- Field 28
Until: 06:00, 0.0, !- Field 30
Until: 08:00, 0.1, !- Field 32
Until: 12:00, 0.3, !- Field 34
Until: 17:00, 0.1, !- Field 36
Until: 19:00, 0.0, !- Field 38
Until: 24:00, 0.0, !- Field 40
For: WinterDesignDay, !- Field 41
Until: 24:00, 0.0, !- Field 43
For: Sunday Holidays AllOtherDays, !- Field 44
Until: 06:00, 0.0, !- Field 46
Until: 18:00, 0.0, !- Field 48
Until: 24:00, 0.0; !- Field 50
Schedule:Compact,
Infiltration Schedule, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays SummerDesignDay, !- Field 2
Until: 06:00, 1.0, !- Field 4
Until: 22:00, 0.0, !- Field 6
Until: 24:00, 1.0, !- Field 8
For: Saturday WinterDesignDay, !- Field 9
Until: 06:00, 1.0, !- Field 11
Until: 18:00, 0.0, !- Field 13
Until: 24:00, 1.0, !- Field 15
For: Sunday Holidays AllOtherDays, !- Field 16
Until: 24:00, 1.0; !- Field 18
Schedule:Compact,
Hours of Operation Schedule, !- Name
On/Off, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays SummerDesignDay, !- Field 2
Until: 06:00, 0.0, !- Field 4
Until: 22:00, 1.0, !- Field 6
Until: 24:00, 0.0, !- Field 8
For: Saturday WinterDesignDay, !- Field 9
Until: 06:00, 0.0, !- Field 11
Until: 18:00, 1.0, !- Field 13
Until: 24:00, 0.0, !- Field 15
For: Sunday Holidays AllOtherDays, !- Field 16
Until: 24:00, 0.0; !- Field 18
Schedule:Compact,
Always On, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 1.0; !- Field 4
Schedule:Compact,
Always Off, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 0.0; !- Field 4
Schedule:Compact,
Office Activity Schedule,!- Name
Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 120.; !- Field 4
Schedule:Compact,
Office Work Eff. Schedule, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 0.0; !- Field 4
Schedule:Compact,
Office Clothing Schedule,!- Name
Any Number, !- Schedule Type Limits Name
Through: 04/30, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 1.0, !- Field 4
Through: 09/30, !- Field 5
For: AllDays, !- Field 6
Until: 24:00, 0.5, !- Field 8
Through: 12/31, !- Field 9
For: AllDays, !- Field 10
Until: 24:00, 1.0; !- Field 12
ScheduleTypeLimits,
Any Number; !- Name
ScheduleTypeLimits,
Fraction, !- Name
0.0, !- Lower Limit Value
1.0, !- Upper Limit Value
CONTINUOUS; !- Numeric Type
ScheduleTypeLimits,
Temperature, !- Name
-60, !- Lower Limit Value
200, !- Upper Limit Value
CONTINUOUS; !- Numeric Type
ScheduleTypeLimits,
On/Off, !- Name
0, !- Lower Limit Value
1, !- Upper Limit Value
DISCRETE; !- Numeric Type
ScheduleTypeLimits,
Control Type, !- Name
0, !- Lower Limit Value
4, !- Upper Limit Value
DISCRETE; !- Numeric Type
ScheduleTypeLimits,
Humidity, !- Name
10, !- Lower Limit Value
90, !- Upper Limit Value
CONTINUOUS; !- Numeric Type
ScheduleTypeLimits,
HVACTemplate Any Number; !- Name
Material,
F08 Metal surface, !- Name
Smooth, !- Roughness
0.0008, !- Thickness {m}
45.28, !- Conductivity {W/m-K}
7824, !- Density {kg/m3}
500; !- Specific Heat {J/kg-K}
Material,
I01 25mm insulation board, !- Name
MediumRough, !- Roughness
0.0254, !- Thickness {m}
0.03, !- Conductivity {W/m-K}
43, !- Density {kg/m3}
1210; !- Specific Heat {J/kg-K}
Material,
I02 50mm insulation board, !- Name
MediumRough, !- Roughness
0.0508, !- Thickness {m}
0.03, !- Conductivity {W/m-K}
43, !- Density {kg/m3}
1210; !- Specific Heat {J/kg-K}
Material,
G01a 19mm gypsum board, !- Name
MediumSmooth, !- Roughness
0.019, !- Thickness {m}
0.16, !- Conductivity {W/m-K}
800, !- Density {kg/m3}
1090; !- Specific Heat {J/kg-K}
Material,
M11 100mm lightweight concrete, !- Name
MediumRough, !- Roughness
0.1016, !- Thickness {m}
0.53, !- Conductivity {W/m-K}
1280, !- Density {kg/m3}
840; !- Specific Heat {J/kg-K}
Material,
F16 Acoustic tile, !- Name
MediumSmooth, !- Roughness
0.0191, !- Thickness {m}
0.06, !- Conductivity {W/m-K}
368, !- Density {kg/m3}
590; !- Specific Heat {J/kg-K}
Material,
M01 100mm brick, !- Name
MediumRough, !- Roughness
0.1016, !- Thickness {m}
0.89, !- Conductivity {W/m-K}
1920, !- Density {kg/m3}
790; !- Specific Heat {J/kg-K}
Material,
M15 200mm heavyweight concrete, !- Name
MediumRough, !- Roughness
0.2032, !- Thickness {m}
1.95, !- Conductivity {W/m-K}
2240, !- Density {kg/m3}
900; !- Specific Heat {J/kg-K}
Material,
M05 200mm concrete block,!- Name
MediumRough, !- Roughness
0.2032, !- Thickness {m}
1.11, !- Conductivity {W/m-K}
800, !- Density {kg/m3}
920; !- Specific Heat {J/kg-K}
Material,
G05 25mm wood, !- Name
MediumSmooth, !- Roughness
0.0254, !- Thickness {m}
0.15, !- Conductivity {W/m-K}
608, !- Density {kg/m3}
1630; !- Specific Heat {J/kg-K}
Material:AirGap,
F04 Wall air space resistance, !- Name
0.15; !- Thermal Resistance {m2-K/W}
Material:AirGap,
F05 Ceiling air space resistance, !- Name
0.18; !- Thermal Resistance {m2-K/W}
WindowMaterial:Glazing,
Clear 3mm, !- Name
SpectralAverage, !- Optical Data Type
, !- Window Glass Spectral Data Set Name
0.003, !- Thickness {m}
0.837, !- Solar Transmittance at Normal Incidence
0.075, !- Front Side Solar Reflectance at Normal Incidence
0.075, !- Back Side Solar Reflectance at Normal Incidence
0.898, !- Visible Transmittance at Normal Incidence
0.081, !- Front Side Visible Reflectance at Normal Incidence
0.081, !- Back Side Visible Reflectance at Normal Incidence
0, !- Infrared Transmittance at Normal Incidence
0.84, !- Front Side Infrared Hemispherical Emissivity
0.84, !- Back Side Infrared Hemispherical Emissivity
0.9; !- Conductivity {W/m-K}
WindowMaterial:Gas,
Air 13mm, !- Name
Air, !- Gas Type
0.0127; !- Thickness {m}
Construction,
Exterior Floor, !- Name
M11 100mm lightweight concrete; !- Outside Layer
Construction,
Interior Floor, !- Name
M11 100mm lightweight concrete; !- Outside Layer
Construction,
Exterior Wall, !- Name
M15 200mm heavyweight concrete; !- Outside Layer
Construction,
Interior Wall, !- Name
M15 200mm heavyweight concrete; !- Outside Layer
Construction,
Exterior Roof, !- Name
M11 100mm lightweight concrete; !- Outside Layer
Construction,
Interior Ceiling, !- Name
M11 100mm lightweight concrete, !- Outside Layer
F05 Ceiling air space resistance, !- Layer 2
F16 Acoustic tile; !- Layer 3
Construction,
Exterior Window, !- Name
Clear 3mm; !- Outside Layer
Construction,
Interior Window, !- Name
Clear 3mm; !- Outside Layer
Construction,
Exterior Door, !- Name
F08 Metal surface, !- Outside Layer
I01 25mm insulation board; !- Layer 2
Construction,
Interior Door, !- Name
G05 25mm wood; !- Outside Layer
GlobalGeometryRules,
UpperLeftCorner, !- Starting Vertex Position
Counterclockwise, !- Vertex Entry Direction
Relative; !- Coordinate System
Zone,
GARAGE, !- Name
0.0, !- Direction of Relative North {deg}
2.728383, 6.651413, 0.0, !- X,Y,Z {m}
, !- Type
1, !- Multiplier
5.18134730989933, !- Ceiling Height {m}
autocalculate; !- Volume {m3}
Zone,
CONFERENCE, !- Name
0.0, !- Direction of Relative North {deg}
23.25624, 8.5344, 0.0, !- X,Y,Z {m}
, !- Type
1, !- Multiplier
5.18134730989933, !- Ceiling Height {m}
autocalculate; !- Volume {m3}
Zone,
EAST, !- Name
0.0, !- Direction of Relative North {deg}
23.25624, 12.8016, -9.139744, !- X,Y,Z {m}
, !- Type
1, !- Multiplier
5.18134730989933, !- Ceiling Height {m}
autocalculate; !- Volume {m3}
Zone,
OPEN, !- Name
0.0, !- Direction of Relative North {deg}
14.0208, 8.5344, 0.0, !- X,Y,Z {m}
, !- Type
1, !- Multiplier
5.18134730989933, !- Ceiling Height {m}
autocalculate; !- Volume {m3}
BuildingSurface:Detailed,
41702B, !- Name
Floor, !- Surface Type
Exterior Floor, !- Construction Name
GARAGE, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- View Factor to Ground
6, !- Number of Vertices
11.292417000000, 6.150187000000, 0.000000000000,
!- X,Y,Z 1 {m}
11.292417000000, -6.651413000000, 0.000000000000,
!- X,Y,Z 2 {m}
1.843617000000, -6.651413000000, 0.000000000000,
!- X,Y,Z 3 {m}
1.843617000000, -2.993813000000, 0.000000000000,
!- X,Y,Z 4 {m}
-2.728383000000, -2.993813000000, 0.000000000000,
!- X,Y,Z 5 {m}
-2.728383000000, 6.150187000000, 0.000000000000;
!- X,Y,Z 6 {m}
BuildingSurface:Detailed,
F0B313, !- Name
Wall, !- Surface Type
Exterior Wall, !- Construction Name
GARAGE, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
1.843617000000, -2.993813000000, 5.232400000000,
!- X,Y,Z 1 {m}
1.843617000000, -2.993813000000, 0.000000000000,
!- X,Y,Z 2 {m}
1.843617000000, -6.651413000000, 0.000000000000,
!- X,Y,Z 3 {m}
1.843617000000, -6.651413000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
A6D260, !- Name
Wall, !- Surface Type
Exterior Door, !- Construction Name
GARAGE, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
11.292417000000, 6.150187000000, 5.232400000000,
!- X,Y,Z 1 {m}
11.292417000000, 6.150187000000, 0.000000000000,
!- X,Y,Z 2 {m}
-2.728383000000, 6.150187000000, 0.000000000000,
!- X,Y,Z 3 {m}
-2.728383000000, 6.150187000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
5B4348, !- Name
Roof, !- Surface Type
Exterior Roof, !- Construction Name
GARAGE, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
6, !- Number of Vertices
-2.728383000000, 6.150187000000, 5.232400000000,
!- X,Y,Z 1 {m}
-2.728383000000, -2.993813000000, 5.232400000000,
!- X,Y,Z 2 {m}
1.843617000000, -2.993813000000, 5.232400000000,
!- X,Y,Z 3 {m}
1.843617000000, -6.651413000000, 5.232400000000,
!- X,Y,Z 4 {m}
11.292417000000, -6.651413000000, 5.232400000000,
!- X,Y,Z 5 {m}
11.292417000000, 6.150187000000, 5.232400000000;
!- X,Y,Z 6 {m}
BuildingSurface:Detailed,
943349, !- Name
Wall, !- Surface Type
Exterior Wall, !- Construction Name
GARAGE, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
-2.728383000000, -2.993813000000, 5.232400000000,
!- X,Y,Z 1 {m}
-2.728383000000, -2.993813000000, 0.000000000000,
!- X,Y,Z 2 {m}
1.843617000000, -2.993813000000, 0.000000000000,
!- X,Y,Z 3 {m}
1.843617000000, -2.993813000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
DF5EE9, !- Name
Wall, !- Surface Type
Exterior Wall, !- Construction Name
GARAGE, !- Zone Name
Adiabatic, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
-2.728383000000, 6.150187000000, 5.232400000000,
!- X,Y,Z 1 {m}
-2.728383000000, 6.150187000000, 0.000000000000,
!- X,Y,Z 2 {m}
-2.728383000000, -2.993813000000, 0.000000000000,
!- X,Y,Z 3 {m}
-2.728383000000, -2.993813000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
36D5CB, !- Name
Wall, !- Surface Type
Exterior Wall, !- Construction Name
GARAGE, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
1.843617000000, -6.651413000000, 5.232400000000,
!- X,Y,Z 1 {m}
1.843617000000, -6.651413000000, 0.000000000000,
!- X,Y,Z 2 {m}
11.292417000000, -6.651413000000, 0.000000000000,
!- X,Y,Z 3 {m}
11.292417000000, -6.651413000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
GarageWestI, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
GARAGE, !- Zone Name
Surface, !- Outside Boundary Condition
OpenWestI, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
11.292417000000, -6.651413000000, 5.232400000000,
!- X,Y,Z 1 {m}
11.292417000000, -6.651413000000, 0.000000000000,
!- X,Y,Z 2 {m}
11.292417000000, 1.882987000000, 0.000000000000,
!- X,Y,Z 3 {m}
11.292417000000, 1.882987000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
BC4DDA, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
GARAGE, !- Zone Name
Surface, !- Outside Boundary Condition
2996F2, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
11.292417000000, 1.882987000000, 5.232400000000,
!- X,Y,Z 1 {m}
11.292417000000, 1.882987000000, 0.000000000000,
!- X,Y,Z 2 {m}
11.292417000000, 6.150187000000, 0.000000000000,
!- X,Y,Z 3 {m}
11.292417000000, 6.150187000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
E22B2D, !- Name
Floor, !- Surface Type
Exterior Floor, !- Construction Name
CONFERENCE, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
0.000000000000, 4.267200000000, 0.000000000000,
!- X,Y,Z 1 {m}
0.000000000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 2 {m}
-9.235440000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 3 {m}
-9.235440000000, 4.267200000000, 0.000000000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
ConferenceNorthI, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
CONFERENCE, !- Zone Name
Surface, !- Outside Boundary Condition
OpenNorthI, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
-9.235440000000, 0.000000000000, 5.232400000000,
!- X,Y,Z 1 {m}
-9.235440000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 2 {m}
0.000000000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 3 {m}
0.000000000000, 0.000000000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
ConferenceWestII, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
CONFERENCE, !- Zone Name
Surface, !- Outside Boundary Condition
OpenWestII, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
0.000000000000, 0.000000000000, 5.232400000000,
!- X,Y,Z 1 {m}
0.000000000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 2 {m}
0.000000000000, 4.267200000000, 0.000000000000,
!- X,Y,Z 3 {m}
0.000000000000, 4.267200000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
15E59E, !- Name
Wall, !- Surface Type
Exterior Wall, !- Construction Name
CONFERENCE, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
0.000000000000, 4.267200000000, 5.232400000000,
!- X,Y,Z 1 {m}
0.000000000000, 4.267200000000, 0.000000000000,
!- X,Y,Z 2 {m}
-9.235440000000, 4.267200000000, 0.000000000000,
!- X,Y,Z 3 {m}
-9.235440000000, 4.267200000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
2996F2, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
CONFERENCE, !- Zone Name
Surface, !- Outside Boundary Condition
BC4DDA, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
-9.235440000000, 4.267200000000, 5.232400000000,
!- X,Y,Z 1 {m}
-9.235440000000, 4.267200000000, 0.000000000000,
!- X,Y,Z 2 {m}
-9.235440000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 3 {m}
-9.235440000000, 0.000000000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
4F35AD, !- Name
Roof, !- Surface Type
Exterior Roof, !- Construction Name
CONFERENCE, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
-9.235440000000, 4.267200000000, 5.232400000000,
!- X,Y,Z 1 {m}
-9.235440000000, 0.000000000000, 5.232400000000,
!- X,Y,Z 2 {m}
0.000000000000, 0.000000000000, 5.232400000000,
!- X,Y,Z 3 {m}
0.000000000000, 4.267200000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
72C969, !- Name
Floor, !- Surface Type
Exterior Floor, !- Construction Name
EAST, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- View Factor to Ground
6, !- Number of Vertices
9.296400000000, 0.000000000000, 9.139744000000,
!- X,Y,Z 1 {m}
9.296400000000, -12.769850000000, 9.139744000000,
!- X,Y,Z 2 {m}
5.029200000000, -12.769850000000, 9.139744000000,
!- X,Y,Z 3 {m}
5.029200000000, -4.267200000000, 9.139744000000,
!- X,Y,Z 4 {m}
1.371600000000, -4.267200000000, 9.139744000000,
!- X,Y,Z 5 {m}
1.371600000000, 0.000000000000, 9.139744000000;
!- X,Y,Z 6 {m}
BuildingSurface:Detailed,
EastNorthIII, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
EAST, !- Zone Name
Surface, !- Outside Boundary Condition
OpenNorthIII, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
1.371600000000, -4.267200000000, 14.372144000000,
!- X,Y,Z 1 {m}
1.371600000000, -4.267200000000, 9.139744000000,
!- X,Y,Z 2 {m}
5.029200000000, -4.267200000000, 9.139744000000,
!- X,Y,Z 3 {m}
5.029200000000, -4.267200000000, 14.372144000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
CE0365, !- Name
Roof, !- Surface Type
Exterior Roof, !- Construction Name
EAST, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
6, !- Number of Vertices
1.371600000000, 0.000000000000, 14.372144000000,
!- X,Y,Z 1 {m}
1.371600000000, -4.267200000000, 14.372144000000,
!- X,Y,Z 2 {m}
5.029200000000, -4.267200000000, 14.372144000000,
!- X,Y,Z 3 {m}
5.029200000000, -12.769850000000, 14.372144000000,
!- X,Y,Z 4 {m}
9.296400000000, -12.769850000000, 14.372144000000,
!- X,Y,Z 5 {m}
9.296400000000, 0.000000000000, 14.372144000000;
!- X,Y,Z 6 {m}
BuildingSurface:Detailed,
3474E0, !- Name
Wall, !- Surface Type
Exterior Wall, !- Construction Name
EAST, !- Zone Name
Adiabatic, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
9.296400000000, -12.769850000000, 14.372144000000,
!- X,Y,Z 1 {m}
9.296400000000, -12.769850000000, 9.139744000000,
!- X,Y,Z 2 {m}
9.296400000000, 0.000000000000, 9.139744000000,
!- X,Y,Z 3 {m}
9.296400000000, 0.000000000000, 14.372144000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
EastEastII, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
EAST, !- Zone Name
Surface, !- Outside Boundary Condition
OpenEastII, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
1.371600000000, 0.000000000000, 14.372144000000,
!- X,Y,Z 1 {m}
1.371600000000, 0.000000000000, 9.139744000000,
!- X,Y,Z 2 {m}
1.371600000000, -4.267200000000, 9.139744000000,
!- X,Y,Z 3 {m}
1.371600000000, -4.267200000000, 14.372144000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
E84069, !- Name
Wall, !- Surface Type
Exterior Wall, !- Construction Name
EAST, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
9.296400000000, 0.000000000000, 14.372144000000,
!- X,Y,Z 1 {m}
9.296400000000, 0.000000000000, 9.139744000000,
!- X,Y,Z 2 {m}
1.371600000000, 0.000000000000, 9.139744000000,
!- X,Y,Z 3 {m}
1.371600000000, 0.000000000000, 14.372144000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
EastEastI, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
EAST, !- Zone Name
Surface, !- Outside Boundary Condition
OpenEastI, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
5.029200000000, -4.267200000000, 14.372144000000,
!- X,Y,Z 1 {m}
5.029200000000, -4.267200000000, 9.139744000000,
!- X,Y,Z 2 {m}
5.029200000000, -12.769850000000, 9.139744000000,
!- X,Y,Z 3 {m}
5.029200000000, -12.769850000000, 14.372144000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
198B2D, !- Name
Wall, !- Surface Type
Exterior Wall, !- Construction Name
EAST, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
5.029200000000, -12.769850000000, 14.372144000000,
!- X,Y,Z 1 {m}
5.029200000000, -12.769850000000, 9.139744000000,
!- X,Y,Z 2 {m}
9.296400000000, -12.769850000000, 9.139744000000,
!- X,Y,Z 3 {m}
9.296400000000, -12.769850000000, 14.372144000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
872F05, !- Name
Floor, !- Surface Type
Exterior Floor, !- Construction Name
OPEN, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- View Factor to Ground
8, !- Number of Vertices
10.607040000000, 4.267200000000, 0.000000000000,
!- X,Y,Z 1 {m}
10.607040000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 2 {m}
14.264640000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 3 {m}
14.264640000000, -8.502650000000, 0.000000000000,
!- X,Y,Z 4 {m}
0.000000000000, -8.502650000000, 0.000000000000,
!- X,Y,Z 5 {m}
0.000000000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 6 {m}
9.235440000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 7 {m}
9.235440000000, 4.267200000000, 0.000000000000;
!- X,Y,Z 8 {m}
BuildingSurface:Detailed,
OpenWestI, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
OPEN, !- Zone Name
Surface, !- Outside Boundary Condition
GarageWestI, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
0.000000000000, 0.000000000000, 5.257800000000,
!- X,Y,Z 1 {m}
0.000000000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 2 {m}
0.000000000000, -8.502650000000, 0.000000000000,
!- X,Y,Z 3 {m}
0.000000000000, -8.502650000000, 5.257800000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
D48B11, !- Name
Wall, !- Surface Type
Exterior Wall, !- Construction Name
OPEN, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
10.607040000000, 4.267200000000, 5.257800000000,
!- X,Y,Z 1 {m}
10.607040000000, 4.267200000000, 0.000000000000,
!- X,Y,Z 2 {m}
9.235440000000, 4.267200000000, 0.000000000000,
!- X,Y,Z 3 {m}
9.235440000000, 4.267200000000, 5.257800000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
OpenNorthIII, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
OPEN, !- Zone Name
Surface, !- Outside Boundary Condition
EastNorthIII, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
14.264640000000, 0.000000000000, 5.257800000000,
!- X,Y,Z 1 {m}
14.264640000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 2 {m}
10.607040000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 3 {m}
10.607040000000, 0.000000000000, 5.257800000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
675F2E, !- Name
Wall, !- Surface Type
Exterior Wall, !- Construction Name
OPEN, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
4, !- Number of Vertices
0.000000000000, -8.502650000000, 5.232400000000,
!- X,Y,Z 1 {m}
0.000000000000, -8.502650000000, 0.000000000000,
!- X,Y,Z 2 {m}
14.264640000000, -8.502650000000, 0.000000000000,
!- X,Y,Z 3 {m}
14.264640000000, -8.502650000000, 5.232400000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
OpenNorthI, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
OPEN, !- Zone Name
Surface, !- Outside Boundary Condition
ConferenceNorthI, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
9.235440000000, 0.000000000000, 5.257800000000,
!- X,Y,Z 1 {m}
9.235440000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 2 {m}
0.000000000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 3 {m}
0.000000000000, 0.000000000000, 5.257800000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
OpenEastII, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
OPEN, !- Zone Name
Surface, !- Outside Boundary Condition
EastEastII, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
10.607040000000, 0.000000000000, 5.257800000000,
!- X,Y,Z 1 {m}
10.607040000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 2 {m}
10.607040000000, 4.267200000000, 0.000000000000,
!- X,Y,Z 3 {m}
10.607040000000, 4.267200000000, 5.257800000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
2C5CED, !- Name
Roof, !- Surface Type
Exterior Roof, !- Construction Name
OPEN, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- View Factor to Ground
8, !- Number of Vertices
0.000000000000, 0.000000000000, 5.232400000000,
!- X,Y,Z 1 {m}
0.000000000000, -8.502650000000, 5.232400000000,
!- X,Y,Z 2 {m}
14.264640000000, -8.502650000000, 5.232400000000,
!- X,Y,Z 3 {m}
14.264640000000, 0.000000000000, 5.232400000000,
!- X,Y,Z 4 {m}
10.607040000000, 0.000000000000, 5.232400000000,
!- X,Y,Z 5 {m}
10.607040000000, 4.267200000000, 5.232400000000,
!- X,Y,Z 6 {m}
9.235440000000, 4.267200000000, 5.232400000000,
!- X,Y,Z 7 {m}
9.235440000000, 0.000000000000, 5.232400000000;
!- X,Y,Z 8 {m}
BuildingSurface:Detailed,
OpenWestII, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
OPEN, !- Zone Name
Surface, !- Outside Boundary Condition
ConferenceWestII, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
9.235440000000, 4.267200000000, 5.257800000000,
!- X,Y,Z 1 {m}
9.235440000000, 4.267200000000, 0.000000000000,
!- X,Y,Z 2 {m}
9.235440000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 3 {m}
9.235440000000, 0.000000000000, 5.257800000000;
!- X,Y,Z 4 {m}
BuildingSurface:Detailed,
OpenEastI, !- Name
Wall, !- Surface Type
Interior Wall, !- Construction Name
OPEN, !- Zone Name
Surface, !- Outside Boundary Condition
EastEastI, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- View Factor to Ground
4, !- Number of Vertices
14.264640000000, -8.502650000000, 5.257800000000,
!- X,Y,Z 1 {m}
14.264640000000, -8.502650000000, 0.000000000000,
!- X,Y,Z 2 {m}
14.264640000000, 0.000000000000, 0.000000000000,
!- X,Y,Z 3 {m}
14.264640000000, 0.000000000000, 5.257800000000;
!- X,Y,Z 4 {m}
FenestrationSurface:Detailed,
494B51, !- Name
Door, !- Surface Type
Exterior Door, !- Construction Name
A6D260, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- View Factor to Ground
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
7.939617000000, 6.150187000000, 3.657600000000,
!- X,Y,Z 1 {m}
7.939617000000, 6.150187000000, 0.000000000000,
!- X,Y,Z 2 {m}
1.843617000000, 6.150187000000, 0.000000000000,
!- X,Y,Z 3 {m}
1.843617000000, 6.150187000000, 3.657600000000;
!- X,Y,Z 4 {m}
FenestrationSurface:Detailed,
30D092, !- Name
Door, !- Surface Type
Exterior Door, !- Construction Name
36D5CB, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- View Factor to Ground
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
3.612983845015, -6.651413000000, 2.438400000000,
!- X,Y,Z 1 {m}
3.612983845015, -6.651413000000, 0.000000000000,
!- X,Y,Z 2 {m}
4.832183845015, -6.651413000000, 0.000000000000,
!- X,Y,Z 3 {m}
4.832183845015, -6.651413000000, 2.438400000000;
!- X,Y,Z 4 {m}
FenestrationSurface:Detailed,
4094D5, !- Name
Door, !- Surface Type
Exterior Door, !- Construction Name
A6D260, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- View Factor to Ground
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
1.234017000000, 6.150187000000, 2.438400000000,
!- X,Y,Z 1 {m}
1.234017000000, 6.150187000000, 0.000000000000,
!- X,Y,Z 2 {m}
0.014817000000, 6.150187000000, 0.000000000000,
!- X,Y,Z 3 {m}
0.014817000000, 6.150187000000, 2.438400000000;
!- X,Y,Z 4 {m}
FenestrationSurface:Detailed,
1BEA1A, !- Name
Window, !- Surface Type
Exterior Window, !- Construction Name
675F2E, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- View Factor to Ground
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
0.985668176342, -8.502650000000, 3.077199612370,
!- X,Y,Z 1 {m}
0.985668176342, -8.502650000000, 2.396162112370,
!- X,Y,Z 2 {m}
3.711405676342, -8.502650000000, 2.396162112370,
!- X,Y,Z 3 {m}
3.711405676342, -8.502650000000, 3.077199612370;
!- X,Y,Z 4 {m}
FenestrationSurface:Detailed,
EF8DAA, !- Name
Window, !- Surface Type
Exterior Window, !- Construction Name
675F2E, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- View Factor to Ground
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
5.977537354277, -8.502650000000, 3.026059274809,
!- X,Y,Z 1 {m}
5.977537354277, -8.502650000000, 2.329146774809,
!- X,Y,Z 2 {m}
8.871549854277, -8.502650000000, 2.329146774809,
!- X,Y,Z 3 {m}
8.871549854277, -8.502650000000, 3.026059274809;
!- X,Y,Z 4 {m}
FenestrationSurface:Detailed,
C2C493, !- Name
Window, !- Surface Type
Exterior Window, !- Construction Name
675F2E, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- View Factor to Ground
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
11.307758181583, -8.502650000000, 3.012231231344,
!- X,Y,Z 1 {m}
11.307758181583, -8.502650000000, 2.288331231344,
!- X,Y,Z 2 {m}
13.689008181583, -8.502650000000, 2.288331231344,
!- X,Y,Z 3 {m}
13.689008181583, -8.502650000000, 3.012231231344;
!- X,Y,Z 4 {m}
People,
GARAGEPPL, !- Name
GARAGE, !- Zone or ZoneList Name
Always On, !- Number of People Schedule Name
People, !- Number of People Calculation Method
1, !- Number of People
, !- People per Zone Floor Area {person/m2}
, !- Zone Floor Area per Person {m2/person}
0.3, !- Fraction Radiant
autocalculate, !- Sensible Heat Fraction
Office Activity Schedule,!- Activity Level Schedule Name
3.82E-08, !- Carbon Dioxide Generation Rate {m3/s-W}
No, !- Enable ASHRAE 55 Comfort Warnings
ZoneAveraged; !- Mean Radiant Temperature Calculation Type
People,
CONFPPL, !- Name
CONFERENCE, !- Zone or ZoneList Name
Always On, !- Number of People Schedule Name
People, !- Number of People Calculation Method
1, !- Number of People
, !- People per Zone Floor Area {person/m2}
, !- Zone Floor Area per Person {m2/person}
0.3, !- Fraction Radiant
autocalculate, !- Sensible Heat Fraction
Office Activity Schedule,!- Activity Level Schedule Name
3.82E-08, !- Carbon Dioxide Generation Rate {m3/s-W}
No, !- Enable ASHRAE 55 Comfort Warnings
ZoneAveraged; !- Mean Radiant Temperature Calculation Type
People,
EASTPPL, !- Name
EAST, !- Zone or ZoneList Name
Always On, !- Number of People Schedule Name
People, !- Number of People Calculation Method
1, !- Number of People
, !- People per Zone Floor Area {person/m2}
, !- Zone Floor Area per Person {m2/person}
0.3, !- Fraction Radiant
autocalculate, !- Sensible Heat Fraction
Office Activity Schedule,!- Activity Level Schedule Name
3.82E-08, !- Carbon Dioxide Generation Rate {m3/s-W}
No, !- Enable ASHRAE 55 Comfort Warnings
ZoneAveraged; !- Mean Radiant Temperature Calculation Type
People,
OPENPPL, !- Name
OPEN, !- Zone or ZoneList Name
Always On, !- Number of People Schedule Name
People, !- Number of People Calculation Method
1, !- Number of People
, !- People per Zone Floor Area {person/m2}
, !- Zone Floor Area per Person {m2/person}
0.3, !- Fraction Radiant
autocalculate, !- Sensible Heat Fraction
Office Activity Schedule,!- Activity Level Schedule Name
3.82E-08, !- Carbon Dioxide Generation Rate {m3/s-W}
No, !- Enable ASHRAE 55 Comfort Warnings
ZoneAveraged; !- Mean Radiant Temperature Calculation Type
Lights,
EASTLIGHTS, !- Name
EAST, !- Zone or ZoneList Name
Office Lights Schedule, !- Schedule Name
Watts/Area, !- Design Level Calculation Method
, !- Lighting Level {W}
5.38248051935761, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/person}
, !- Return Air Fraction
, !- Fraction Radiant
, !- Fraction Visible
1, !- Fraction Replaceable
General, !- End-Use Subcategory
No; !- Return Air Fraction Calculated from Plenum Temperature
Lights,
CONFLIGHTS, !- Name
CONFERENCE, !- Zone or ZoneList Name
Office Lights Schedule, !- Schedule Name
Watts/Area, !- Design Level Calculation Method
, !- Lighting Level {W}
5.38248051935761, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/person}
, !- Return Air Fraction
, !- Fraction Radiant
, !- Fraction Visible
1, !- Fraction Replaceable
General, !- End-Use Subcategory
No; !- Return Air Fraction Calculated from Plenum Temperature
Lights,
OPENLIGHTS, !- Name
OPEN, !- Zone or ZoneList Name
Office Lights Schedule, !- Schedule Name
Watts/Area, !- Design Level Calculation Method
, !- Lighting Level {W}
5.38248051935761, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/person}
, !- Return Air Fraction
, !- Fraction Radiant
, !- Fraction Visible
1, !- Fraction Replaceable
General, !- End-Use Subcategory
No; !- Return Air Fraction Calculated from Plenum Temperature
ElectricEquipment,
Humidifier, !- Name
EAST, !- Zone or ZoneList Name
Always On, !- Schedule Name
EquipmentLevel, !- Design Level Calculation Method
100, !- Design Level {W}
, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/person}
, !- Fraction Latent
, !- Fraction Radiant
, !- Fraction Lost
General; !- End-Use Subcategory
ElectricEquipment,
Aquarium, !- Name
EAST, !- Zone or ZoneList Name
Always On, !- Schedule Name
EquipmentLevel, !- Design Level Calculation Method
3000, !- Design Level {W}
, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/person}
, !- Fraction Latent
, !- Fraction Radiant
, !- Fraction Lost
General; !- End-Use Subcategory
ElectricEquipment,
Computers, !- Name
OPEN, !- Zone or ZoneList Name
Office Equipment Schedule, !- Schedule Name
EquipmentLevel, !- Design Level Calculation Method
1000, !- Design Level {W}
, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/person}
, !- Fraction Latent
, !- Fraction Radiant
, !- Fraction Lost
General; !- End-Use Subcategory
ElectricEquipment,
Freezers, !- Name
OPEN, !- Zone or ZoneList Name
Always On, !- Schedule Name
EquipmentLevel, !- Design Level Calculation Method
2760, !- Design Level {W}
, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/person}
, !- Fraction Latent
, !- Fraction Radiant
, !- Fraction Lost
General; !- End-Use Subcategory
GasEquipment,
InsulationLoss, !- Name
GARAGE, !- Zone or ZoneList Name
Always On, !- Schedule Name
Watts/Area, !- Design Level Calculation Method
, !- Design Level {W}
26.8175004435692, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/Person}
, !- Fraction Latent
, !- Fraction Radiant
, !- Fraction Lost
, !- Carbon Dioxide Generation Rate {m3/s-W}
General; !- End-Use Subcategory
Schedule:Compact,
ON, !- Name
FRACTION, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 1.00; !- Field 4
Schedule:Compact,
SEASONAL RESET SUPPLY AIR TEMP SCH, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 13; !- Field 4
Schedule:Compact,
HEATING COIL SUPPLY AIR TEMP SCH, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 60.00; !- Field 4
Schedule:Compact,
CW LOOP TEMP SCHEDULE, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 6.67; !- Field 4
Schedule:Compact,
HW LOOP TEMP SCHEDULE, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 80.00; !- Field 4
Schedule:Compact,
Heating Setpoints, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 21; !- Field 4
Schedule:Compact,
ZONE CONTROL TYPE SCHED, !- Name
CONTROL TYPE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, 4; !- Field 4
Version,6.0;
Building,
NRRA, !- Name
0, !- North Axis {deg}
Suburbs, !- Terrain
3.9999999E-02, !- Loads Convergence Tolerance Value
0.4000000, !- Temperature Convergence Tolerance Value {deltaC}
FullInteriorAndExterior, !- Solar Distribution
25; !- Maximum Number of Warmup Days
Timestep,4;
SurfaceConvectionAlgorithm:Inside,TARP;
SurfaceConvectionAlgorithm:Outside,DOE-2;
HeatBalanceAlgorithm,ConductionTransferFunction;
SimulationControl,
Yes, !- Do Zone Sizing Calculation
Yes, !- Do System Sizing Calculation
Yes, !- Do Plant Sizing Calculation
No, !- Run Simulation for Sizing Periods
Yes; !- Run Simulation for Weather File Run Periods
NodeList,
Zone Equipment Inlet Node List, !- Name
Main Hot Air Inlet, !- Node 1 Name
Main Cold Air Inlet; !- Node 2 Name
NodeList,
Air Loop Outlet Node List, !- Name
Heating Coil Outlet Node,!- Node 1 Name
Cooling Coil Outlet Node;!- Node 2 Name
NodeList,
Chilled Water Loop Setpoint Node List, !- Name
CW Supply Outlet Node; !- Node 1 Name
NodeList,
Hot Water Loop Setpoint Node List, !- Name
HW Supply Outlet Node; !- Node 1 Name
NodeList,
Zone1Inlets, !- Name
Zone 1 Dual Duct Outlet; !- Node 1 Name
NodeList,
Zone2Inlets, !- Name
Zone 2 Dual Duct Outlet; !- Node 1 Name
NodeList,
Zone3Inlets, !- Name
Zone 3 Dual Duct Outlet; !- Node 1 Name
NodeList,
Cooling Coil Supply Air Temp Nodes, !- Name
Cooling Coil Outlet Node;!- Node 1 Name
NodeList,
Heating Coil Supply Air Temp Nodes, !- Name
Heating Coil Outlet Node;!- Node 1 Name
BranchList,
Dual Duct Air Loop Branches, !- Name
Air Loop Main Branch, !- Branch 1 Name
Heating Coil Air Sys Branch, !- Branch 2 Name
Cooling Coil Air Sys Branch; !- Branch 3 Name
BranchList,
Cooling Supply Side Branches, !- Name
CW Pump Branch, !- Branch 1 Name
Purchased Cooling Branch,!- Branch 2 Name
Supply Bypass Branch, !- Branch 3 Name
Cooling Supply Outlet; !- Branch 4 Name
BranchList,
Cooling Demand Side Branches, !- Name
Cooling Demand Inlet, !- Branch 1 Name
Cooling Coil Branch, !- Branch 2 Name
Demand Bypass Branch, !- Branch 3 Name
Cooling Demand Outlet; !- Branch 4 Name
BranchList,
Heating Supply Side Branches, !- Name
Heating Supply Inlet Branch, !- Branch 1 Name
Heating Purchased Hot Water Branch, !- Branch 2 Name
Heating Supply Bypass Branch, !- Branch 3 Name
Heating Supply Outlet Branch; !- Branch 4 Name
BranchList,
Heating Demand Side Branches, !- Name
Reheat Inlet Branch, !- Branch 1 Name
Heating Coil Branch, !- Branch 2 Name
Reheat Bypass Branch, !- Branch 3 Name
Reheat Outlet Branch; !- Branch 4 Name
ConnectorList,
Dual Duct Connectors, !- Name
Connector:Splitter, !- Connector 1 Object Type
DualDuctAirSplitter; !- Connector 1 Name
ConnectorList,
Cooling Supply Side Connectors, !- Name
Connector:Splitter, !- Connector 1 Object Type
CW Loop Splitter, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
CW Loop Mixer; !- Connector 2 Name
ConnectorList,
Cooling Demand Side Connectors, !- Name
Connector:Splitter, !- Connector 1 Object Type
CW Demand Splitter, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
CW Demand Mixer; !- Connector 2 Name
ConnectorList,
Heating Supply Side Connectors, !- Name
Connector:Splitter, !- Connector 1 Object Type
Heating Supply Splitter, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
Heating Supply Mixer; !- Connector 2 Name
ConnectorList,
Heating Demand Side Connectors, !- Name
Connector:Splitter, !- Connector 1 Object Type
Reheat Splitter, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
Reheat Mixer; !- Connector 2 Name
Branch,
Air Loop Main Branch, !- Name
1.3, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Fan:ConstantVolume, !- Component 1 Object Type
SupplyFan, !- Component 1 Name
Supply Fan Inlet Node, !- Component 1 Inlet Node Name
Supply Fan Outlet Node, !- Component 1 Outlet Node Name
PASSIVE; !- Component 1 Branch Control Type
Branch,
Heating Coil Air Sys Branch, !- Name
1.3, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Coil:Heating:Water, !- Component 1 Object Type
Main Heating Coil, !- Component 1 Name
Heating Coil Inlet Node, !- Component 1 Inlet Node Name
Heating Coil Outlet Node,!- Component 1 Outlet Node Name
ACTIVE; !- Component 1 Branch Control Type
Branch,
Cooling Coil Air Sys Branch, !- Name
1.3, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Coil:Cooling:Water, !- Component 1 Object Type
Main Cooling Coil, !- Component 1 Name
Cooling Coil Inlet Node, !- Component 1 Inlet Node Name
Cooling Coil Outlet Node,!- Component 1 Outlet Node Name
ACTIVE; !- Component 1 Branch Control Type
Branch,
Cooling Demand Inlet, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Demand Side Inlet Pipe, !- Component 1 Name
CW Demand Inlet Node, !- Component 1 Inlet Node Name
CW Demand Entrance Pipe Outlet Node, !- Component 1 Outlet Node Name
PASSIVE; !- Component 1 Branch Control Type
Branch,
Cooling Coil Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Coil:Cooling:Water, !- Component 1 Object Type
Main Cooling Coil, !- Component 1 Name
Cooling Coil Water Inlet Node, !- Component 1 Inlet Node Name
Cooling Coil Water Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Branch,
Demand Bypass Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Demand Side Bypass, !- Component 1 Name
CW Demand Bypass Inlet Node, !- Component 1 Inlet Node Name
CW Demand Bypass Outlet Node, !- Component 1 Outlet Node Name
BYPASS; !- Component 1 Branch Control Type
Branch,
Cooling Demand Outlet, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
CW Demand Side Outlet Pipe, !- Component 1 Name
CW Demand Exit Pipe Inlet Node, !- Component 1 Inlet Node Name
CW Demand Outlet Node, !- Component 1 Outlet Node Name
PASSIVE; !- Component 1 Branch Control Type
Branch,
Cooling Supply Outlet, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Supply Side Outlet Pipe, !- Component 1 Name
Supply Side Exit Pipe Inlet Node, !- Component 1 Inlet Node Name
CW Supply Outlet Node, !- Component 1 Outlet Node Name
PASSIVE; !- Component 1 Branch Control Type
Branch,
CW Pump Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pump:VariableSpeed, !- Component 1 Object Type
Circ Pump, !- Component 1 Name
CW Supply Inlet Node, !- Component 1 Inlet Node Name
CW Pump Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Branch,
Purchased Cooling Branch,!- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
DistrictCooling, !- Component 1 Object Type
Purchased Cooling, !- Component 1 Name
Purchased Cooling Inlet Node, !- Component 1 Inlet Node Name
Purchased Cooling Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Branch,
Supply Bypass Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Supply Side Bypass, !- Component 1 Name
CW Supply Bypass Inlet Node, !- Component 1 Inlet Node Name
CW Supply Bypass Outlet Node, !- Component 1 Outlet Node Name
BYPASS; !- Component 1 Branch Control Type
Branch,
Heating Supply Inlet Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pump:VariableSpeed, !- Component 1 Object Type
HW Circ Pump, !- Component 1 Name
HW Supply Inlet Node, !- Component 1 Inlet Node Name
HW Pump Outlet Node, !- Component 1 Outlet Node Name
ACTIVE; !- Component 1 Branch Control Type
Branch,
Heating Purchased Hot Water Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
DistrictHeating, !- Component 1 Object Type
Purchased Heating, !- Component 1 Name
Purchased Heat Inlet Node, !- Component 1 Inlet Node Name
Purchased Heat Outlet Node, !- Component 1 Outlet Node Name
ACTIVE; !- Component 1 Branch Control Type
Branch,
Heating Supply Bypass Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Heating Supply Side Bypass, !- Component 1 Name
Heating Supply Bypass Inlet Node, !- Component 1 Inlet Node Name
Heating Supply Bypass Outlet Node, !- Component 1 Outlet Node Name
BYPASS; !- Component 1 Branch Control Type
Branch,
Heating Supply Outlet Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Heating Supply Outlet, !- Component 1 Name
Heating Supply Exit Pipe Inlet Node, !- Component 1 Inlet Node Name
HW Supply Outlet Node, !- Component 1 Outlet Node Name
PASSIVE; !- Component 1 Branch Control Type
Branch,
Reheat Inlet Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Reheat Inlet Pipe, !- Component 1 Name
HW Demand Inlet Node, !- Component 1 Inlet Node Name
HW Demand Entrance Pipe Outlet Node, !- Component 1 Outlet Node Name
PASSIVE; !- Component 1 Branch Control Type
Branch,
Reheat Outlet Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Reheat Outlet Pipe, !- Component 1 Name
HW Demand Exit Pipe Inlet Node, !- Component 1 Inlet Node Name
HW Demand Outlet Node, !- Component 1 Outlet Node Name
PASSIVE; !- Component 1 Branch Control Type
Branch,
Heating Coil Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Coil:Heating:Water, !- Component 1 Object Type
Main Heating Coil, !- Component 1 Name
Heating Coil Water Inlet,!- Component 1 Inlet Node Name
Heating Coil Water Outlet, !- Component 1 Outlet Node Name
ACTIVE; !- Component 1 Branch Control Type
Branch,
Reheat Bypass Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Reheat Bypass, !- Component 1 Name
Reheat Bypass Inlet Node,!- Component 1 Inlet Node Name
Reheat Bypass Outlet Node, !- Component 1 Outlet Node Name
BYPASS; !- Component 1 Branch Control Type
Pipe:Adiabatic,
Demand Side Inlet Pipe, !- Name
CW Demand Inlet Node, !- Inlet Node Name
CW Demand Entrance Pipe Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
Demand Side Bypass, !- Name
CW Demand Bypass Inlet Node, !- Inlet Node Name
CW Demand Bypass Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
CW Demand Side Outlet Pipe, !- Name
CW Demand Exit Pipe Inlet Node, !- Inlet Node Name
CW Demand Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
Supply Side Outlet Pipe, !- Name
Supply Side Exit Pipe Inlet Node, !- Inlet Node Name
CW Supply Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
Supply Side Bypass, !- Name
CW Supply Bypass Inlet Node, !- Inlet Node Name
CW Supply Bypass Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
Heating Supply Side Bypass, !- Name
Heating Supply Bypass Inlet Node, !- Inlet Node Name
Heating Supply Bypass Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
Heating Supply Outlet, !- Name
Heating Supply Exit Pipe Inlet Node, !- Inlet Node Name
HW Supply Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
Reheat Inlet Pipe, !- Name
HW Demand Inlet Node, !- Inlet Node Name
HW Demand Entrance Pipe Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
Reheat Outlet Pipe, !- Name
HW Demand Exit Pipe Inlet Node, !- Inlet Node Name
HW Demand Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
Reheat Bypass, !- Name
Reheat Bypass Inlet Node,!- Inlet Node Name
Reheat Bypass Outlet Node; !- Outlet Node Name
PlantLoop,
Chilled Water Loop, !- Name
Water, !- Fluid Type
CW Loop Operation, !- Plant Equipment Operation Scheme Name
CW Supply Outlet Node, !- Loop Temperature Setpoint Node Name
98, !- Maximum Loop Temperature {C}
1, !- Minimum Loop Temperature {C}
0.0011, !- Maximum Loop Flow Rate {m3/s}
0, !- Minimum Loop Flow Rate {m3/s}
autocalculate, !- Plant Loop Volume {m3}
CW Supply Inlet Node, !- Plant Side Inlet Node Name
CW Supply Outlet Node, !- Plant Side Outlet Node Name
Cooling Supply Side Branches, !- Plant Side Branch List Name
Cooling Supply Side Connectors, !- Plant Side Connector List Name
CW Demand Inlet Node, !- Demand Side Inlet Node Name
CW Demand Outlet Node, !- Demand Side Outlet Node Name
Cooling Demand Side Branches, !- Demand Side Branch List Name
Cooling Demand Side Connectors, !- Demand Side Connector List Name
Optimal; !- Load Distribution Scheme
PlantLoop,
Hot Water Loop, !- Name
Water, !- Fluid Type
Hot Loop Operation, !- Plant Equipment Operation Scheme Name
HW Supply Outlet Node, !- Loop Temperature Setpoint Node Name
100, !- Maximum Loop Temperature {C}
10, !- Minimum Loop Temperature {C}
0.0043, !- Maximum Loop Flow Rate {m3/s}
0, !- Minimum Loop Flow Rate {m3/s}
autocalculate, !- Plant Loop Volume {m3}
HW Supply Inlet Node, !- Plant Side Inlet Node Name
HW Supply Outlet Node, !- Plant Side Outlet Node Name
Heating Supply Side Branches, !- Plant Side Branch List Name
Heating Supply Side Connectors, !- Plant Side Connector List Name
HW Demand Inlet Node, !- Demand Side Inlet Node Name
HW Demand Outlet Node, !- Demand Side Outlet Node Name
Heating Demand Side Branches, !- Demand Side Branch List Name
Heating Demand Side Connectors, !- Demand Side Connector List Name
Optimal; !- Load Distribution Scheme
PlantEquipmentOperationSchemes,
CW Loop Operation, !- Name
PlantEquipmentOperation:CoolingLoad, !- Control Scheme 1 Object Type
Cooling, !- Control Scheme 1 Name
Always On; !- Control Scheme 1 Schedule Name
PlantEquipmentOperationSchemes,
Hot Loop Operation, !- Name
PlantEquipmentOperation:HeatingLoad, !- Control Scheme 1 Object Type
Heating, !- Control Scheme 1 Name
Always On; !- Control Scheme 1 Schedule Name
PlantEquipmentOperation:CoolingLoad,
Cooling, !- Name
0, !- Load Range 1 Lower Limit {W}
1000000, !- Load Range 1 Upper Limit {W}
AllCool; !- Range 1 Equipment List Name
PlantEquipmentOperation:HeatingLoad,
Heating, !- Name
0, !- Load Range 1 Lower Limit {W}
1000000, !- Load Range 1 Upper Limit {W}
AllHeat; !- Range 1 Equipment List Name
PlantEquipmentList,
AllCool, !- Name
DistrictCooling, !- Equipment 1 Object Type
Purchased Cooling; !- Equipment 1 Name
PlantEquipmentList,
AllHeat, !- Name
DistrictHeating, !- Equipment 1 Object Type
Purchased Heating; !- Equipment 1 Name
Connector:Splitter,
DualDuctAirSplitter, !- Name
Air Loop Main Branch, !- Inlet Branch Name
Heating Coil Air Sys Branch, !- Outlet Branch 1 Name
Cooling Coil Air Sys Branch; !- Outlet Branch 2 Name
Connector:Splitter,
CW Loop Splitter, !- Name
CW Pump Branch, !- Inlet Branch Name
Purchased Cooling Branch,!- Outlet Branch 1 Name
Supply Bypass Branch; !- Outlet Branch 2 Name
Connector:Splitter,
CW Demand Splitter, !- Name
Cooling Demand Inlet, !- Inlet Branch Name
Demand Bypass Branch, !- Outlet Branch 1 Name
Cooling Coil Branch; !- Outlet Branch 2 Name
Connector:Splitter,
Reheat Splitter, !- Name
Reheat Inlet Branch, !- Inlet Branch Name
Heating Coil Branch, !- Outlet Branch 1 Name
Reheat Bypass Branch; !- Outlet Branch 2 Name
Connector:Splitter,
Heating Supply Splitter, !- Name
Heating Supply Inlet Branch, !- Inlet Branch Name
Heating Purchased Hot Water Branch, !- Outlet Branch 1 Name
Heating Supply Bypass Branch; !- Outlet Branch 2 Name
Connector:Mixer,
CW Loop Mixer, !- Name
Cooling Supply Outlet, !- Outlet Branch Name
Purchased Cooling Branch,!- Inlet Branch 1 Name
Supply Bypass Branch; !- Inlet Branch 2 Name
Connector:Mixer,
CW Demand Mixer, !- Name
Cooling Demand Outlet, !- Outlet Branch Name
Cooling Coil Branch, !- Inlet Branch 1 Name
Demand Bypass Branch; !- Inlet Branch 2 Name
Connector:Mixer,
Reheat Mixer, !- Name
Reheat Outlet Branch, !- Outlet Branch Name
Heating Coil Branch, !- Inlet Branch 1 Name
Reheat Bypass Branch; !- Inlet Branch 2 Name
Connector:Mixer,
Heating Supply Mixer, !- Name
Heating Supply Outlet Branch, !- Outlet Branch Name
Heating Purchased Hot Water Branch, !- Inlet Branch 1 Name
Heating Supply Bypass Branch; !- Inlet Branch 2 Name
AirLoopHVAC,
Main Dual Duct Air Loop, !- Name
Dual Duct System 1 Controllers, !- Controller List Name
Dual Duct System 1 Schedule List, !- Availability Manager List Name
1.3, !- Design Supply Air Flow Rate {m3/s}
Dual Duct Air Loop Branches, !- Branch List Name
Dual Duct Connectors, !- Connector List Name
Supply Fan Inlet Node, !- Supply Side Inlet Node Name
Return Air Mixer Outlet, !- Demand Side Outlet Node Name
Zone Equipment Inlet Node List, !- Demand Side Inlet Node Names
Air Loop Outlet Node List; !- Supply Side Outlet Node Names
AirLoopHVAC:ControllerList,
Dual Duct System 1 Controllers, !- Name
Controller:WaterCoil, !- Controller 1 Object Type
Main Cooling Coil Controller, !- Controller 1 Name
Controller:WaterCoil, !- Controller 2 Object Type
Main Heating Coil Controller; !- Controller 2 Name
AvailabilityManagerAssignmentList,
Dual Duct System 1 Schedule List, !- Name
AvailabilityManager:Scheduled, !- Availability Manager 1 Object Type
Dual Duct System 1 Schedule; !- Availability Manager 1 Name
AvailabilityManager:Scheduled,
Dual Duct System 1 Schedule, !- Name
Always On; !- Schedule Name
SetpointManager:Scheduled,
Chilled Water Loop Setpoint Manager, !- Name
Temperature, !- Control Variable
CW Loop Temp Schedule, !- Schedule Name
Chilled Water Loop Setpoint Node List; !- Setpoint Node or NodeList Name
SetpointManager:Scheduled,
Hot Water Loop Setpoint Manager, !- Name
Temperature, !- Control Variable
HW Loop Temp Schedule, !- Schedule Name
Hot Water Loop Setpoint Node List; !- Setpoint Node or NodeList Name
SetpointManager:Scheduled,
Supply Air Temp Manager, !- Name
Temperature, !- Control Variable
Seasonal Reset Supply Air Temp Sch, !- Schedule Name
Cooling Coil Supply Air Temp Nodes; !- Setpoint Node or NodeList Name
SetpointManager:Scheduled,
Heating Coil Supply Air Temp Manager, !- Name
Temperature, !- Control Variable
Heating Coil Supply Air Temp Sch, !- Schedule Name
Heating Coil Supply Air Temp Nodes; !- Setpoint Node or NodeList Name
Controller:WaterCoil,
Main Cooling Coil Controller, !- Name
Temperature, !- Control Variable
Normal, !- Action
FLOW, !- Actuator Variable
Cooling Coil Outlet Node,!- Sensor Node Name
Cooling Coil Water Inlet Node, !- Actuator Node Name
0.001, !- Controller Convergence Tolerance {deltaC}
0.0011, !- Maximum Actuated Flow {m3/s}
0.0; !- Minimum Actuated Flow {m3/s}
Controller:WaterCoil,
Main Heating Coil Controller, !- Name
Temperature, !- Control Variable
Normal, !- Action
FLOW, !- Actuator Variable
Heating Coil Outlet Node,!- Sensor Node Name
Heating Coil Water Inlet,!- Actuator Node Name
0.001, !- Controller Convergence Tolerance {deltaC}
0.0043, !- Maximum Actuated Flow {m3/s}
0.0; !- Minimum Actuated Flow {m3/s}
ZoneHVAC:EquipmentConnections,
CONFERENCE, !- Zone Name
Zone1Equipment, !- Zone Conditioning Equipment List Name
Zone1Inlets, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
Zone 1 Node, !- Zone Air Node Name
Zone 1 Outlet Node; !- Zone Return Air Node Name
ZoneHVAC:EquipmentConnections,
EAST, !- Zone Name
Zone2Equipment, !- Zone Conditioning Equipment List Name
Zone2Inlets, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
Zone 2 Node, !- Zone Air Node Name
Zone 2 Outlet Node; !- Zone Return Air Node Name
ZoneHVAC:EquipmentConnections,
OPEN, !- Zone Name
Zone3Equipment, !- Zone Conditioning Equipment List Name
Zone3Inlets, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
Zone 3 Node, !- Zone Air Node Name
Zone 3 Outlet Node; !- Zone Return Air Node Name
ZoneHVAC:EquipmentList,
Zone1Equipment, !- Name
ZoneHVAC:AirDistributionUnit, !- Zone Equipment 1 Object Type
Zone1DualDuct, !- Zone Equipment 1 Name
1, !- Zone Equipment 1 Cooling Sequence
1; !- Zone Equipment 1 Heating or No-Load Sequence
ZoneHVAC:EquipmentList,
Zone2Equipment, !- Name
ZoneHVAC:AirDistributionUnit, !- Zone Equipment 1 Object Type
Zone2DualDuct, !- Zone Equipment 1 Name
1, !- Zone Equipment 1 Cooling Sequence
1; !- Zone Equipment 1 Heating or No-Load Sequence
ZoneHVAC:EquipmentList,
Zone3Equipment, !- Name
ZoneHVAC:AirDistributionUnit, !- Zone Equipment 1 Object Type
Zone3DualDuct, !- Zone Equipment 1 Name
1, !- Zone Equipment 1 Cooling Sequence
1; !- Zone Equipment 1 Heating or No-Load Sequence
ZoneHVAC:AirDistributionUnit,
Zone1DualDuct, !- Name
Zone 1 Dual Duct Outlet, !- Air Distribution Unit Outlet Node Name
AirTerminal:DualDuct:ConstantVolume, !- Air Terminal Object Type
Zone1MixDamp; !- Air Terminal Name
ZoneHVAC:AirDistributionUnit,
Zone2DualDuct, !- Name
Zone 2 Dual Duct Outlet, !- Air Distribution Unit Outlet Node Name
AirTerminal:DualDuct:ConstantVolume, !- Air Terminal Object Type
Zone2MixDamp; !- Air Terminal Name
ZoneHVAC:AirDistributionUnit,
Zone3DualDuct, !- Name
Zone 3 Dual Duct Outlet, !- Air Distribution Unit Outlet Node Name
AirTerminal:DualDuct:ConstantVolume, !- Air Terminal Object Type
Zone3MixDamp; !- Air Terminal Name
AirTerminal:DualDuct:ConstantVolume,
Zone1MixDamp, !- Name
Always On, !- Availability Schedule Name
Zone 1 Dual Duct Outlet, !- Air Outlet Node Name
Zone 1 Dual Duct Hot Inlet, !- Hot Air Inlet Node Name
Zone 1 Dual Duct Cold Inlet, !- Cold Air Inlet Node Name
autosize; !- Maximum Air Flow Rate {m3/s}
AirTerminal:DualDuct:ConstantVolume,
Zone2MixDamp, !- Name
Always On, !- Availability Schedule Name
Zone 2 Dual Duct Outlet, !- Air Outlet Node Name
Zone 2 Dual Duct Hot Inlet, !- Hot Air Inlet Node Name
Zone 2 Dual Duct Cold Inlet, !- Cold Air Inlet Node Name
autosize; !- Maximum Air Flow Rate {m3/s}
AirTerminal:DualDuct:ConstantVolume,
Zone3MixDamp, !- Name
Always On, !- Availability Schedule Name
Zone 3 Dual Duct Outlet, !- Air Outlet Node Name
Zone 3 Dual Duct Hot Inlet, !- Hot Air Inlet Node Name
Zone 3 Dual Duct Cold Inlet, !- Cold Air Inlet Node Name
autosize; !- Maximum Air Flow Rate {m3/s}
ZoneControl:Thermostat,
Zone 1 Thermostat, !- Name
CONFERENCE, !- Zone or ZoneList Name
Zone Control Type Sched, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type
Heating Cooling Setpoint Sched; !- Control 1 Name
ZoneControl:Thermostat,
Zone 2 Thermostat, !- Name
EAST, !- Zone or ZoneList Name
Zone Control Type Sched, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type
Heating Cooling Setpoint Sched; !- Control 1 Name
ZoneControl:Thermostat,
Zone 3 Thermostat, !- Name
OPEN, !- Zone or ZoneList Name
Zone Control Type Sched, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type
Heating Cooling Setpoint Sched; !- Control 1 Name
AirLoopHVAC:SupplyPath,
HotAirSupplyPath, !- Name
Main Hot Air Inlet, !- Supply Air Path Inlet Node Name
AirLoopHVAC:ZoneSplitter,!- Component 1 Object Type
ZoneHotAirSupplySplitter;!- Component 1 Name
AirLoopHVAC:SupplyPath,
ColdAirSupplyPath, !- Name
Main Cold Air Inlet, !- Supply Air Path Inlet Node Name
AirLoopHVAC:ZoneSplitter,!- Component 1 Object Type
ZoneColdAirSupplySplitter; !- Component 1 Name
AirLoopHVAC:ReturnPath,
DualDuctReturnPath, !- Name
Return Air Mixer Outlet, !- Return Air Path Outlet Node Name
AirLoopHVAC:ZoneMixer, !- Component 1 Object Type
ZoneReturnAirMixer; !- Component 1 Name
AirLoopHVAC:ZoneSplitter,
ZoneColdAirSupplySplitter, !- Name
Main Cold Air Inlet, !- Inlet Node Name
Zone 1 Dual Duct Cold Inlet, !- Outlet 1 Node Name
Zone 2 Dual Duct Cold Inlet, !- Outlet 2 Node Name
Zone 3 Dual Duct Cold Inlet; !- Outlet 3 Node Name
AirLoopHVAC:ZoneSplitter,
ZoneHotAirSupplySplitter,!- Name
Main Hot Air Inlet, !- Inlet Node Name
Zone 1 Dual Duct Hot Inlet, !- Outlet 1 Node Name
Zone 2 Dual Duct Hot Inlet, !- Outlet 2 Node Name
Zone 3 Dual Duct Hot Inlet; !- Outlet 3 Node Name
AirLoopHVAC:ZoneMixer,
ZoneReturnAirMixer, !- Name
Return Air Mixer Outlet, !- Outlet Node Name
Zone 1 Outlet Node, !- Inlet 1 Node Name
Zone 2 Outlet Node, !- Inlet 2 Node Name
Zone 3 Outlet Node; !- Inlet 3 Node Name
DistrictCooling,
Purchased Cooling, !- Name
Purchased Cooling Inlet Node, !- Chilled Water Inlet Node Name
Purchased Cooling Outlet Node, !- Chilled Water Outlet Node Name
999999999744375; !- Nominal Capacity {W}
DistrictHeating,
Purchased Heating, !- Name
Purchased Heat Inlet Node, !- Hot Water Inlet Node Name
Purchased Heat Outlet Node, !- Hot Water Outlet Node Name
999999999744375; !- Nominal Capacity {W}
Pump:VariableSpeed,
Circ Pump, !- Name
CW Supply Inlet Node, !- Inlet Node Name
CW Pump Outlet Node, !- Outlet Node Name
0.0011, !- Rated Flow Rate {m3/s}
300000, !- Rated Pump Head {Pa}
500, !- Rated Power Consumption {W}
0.87, !- Motor Efficiency
0.0, !- Fraction of Motor Inefficiencies to Fluid Stream
0, !- Coefficient 1 of the Part Load Performance Curve
1, !- Coefficient 2 of the Part Load Performance Curve
0, !- Coefficient 3 of the Part Load Performance Curve
0, !- Coefficient 4 of the Part Load Performance Curve
0, !- Minimum Flow Rate {m3/s}
INTERMITTENT; !- Pump Control Type
Pump:VariableSpeed,
HW Circ Pump, !- Name
HW Supply Inlet Node, !- Inlet Node Name
HW Pump Outlet Node, !- Outlet Node Name
0.0043, !- Rated Flow Rate {m3/s}
300000, !- Rated Pump Head {Pa}
2000, !- Rated Power Consumption {W}
0.87, !- Motor Efficiency
0.0, !- Fraction of Motor Inefficiencies to Fluid Stream
0, !- Coefficient 1 of the Part Load Performance Curve
1, !- Coefficient 2 of the Part Load Performance Curve
0, !- Coefficient 3 of the Part Load Performance Curve
0, !- Coefficient 4 of the Part Load Performance Curve
0, !- Minimum Flow Rate {m3/s}
INTERMITTENT; !- Pump Control Type
Coil:Heating:Water,
Main Heating Coil, !- Name
Always On, !- Availability Schedule Name
1200.0, !- U-Factor Times Area Value {W/K}
0.0043, !- Maximum Water Flow Rate {m3/s}
Heating Coil Water Inlet,!- Water Inlet Node Name
Heating Coil Water Outlet, !- Water Outlet Node Name
Heating Coil Inlet Node, !- Air Inlet Node Name
Heating Coil Outlet Node,!- Air Outlet Node Name
UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method
autosize, !- Rated Capacity {W}
82.2, !- Rated Inlet Water Temperature {C}
16.6, !- Rated Inlet Air Temperature {C}
71.1, !- Rated Outlet Water Temperature {C}
32.2, !- Rated Outlet Air Temperature {C}
; !- Rated Ratio for Air and Water Convection
Output:VariableDictionary,IDF,Name;
OutputControl:Table:Style,
HTML, !- Column Separator
InchPound; !- Unit Conversion
Output:Table:SummaryReports,
AllSummary; !- Report 1 Name
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote:
>
>
> I have not run your IDF yet. I am going to remove some of the designDay objects. Only two would be needed. I do not have the weather file either, although it is not needed for DesignDay sizing. You should change the schedule as Karen suggested first.
>
> Dr. Li
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> From: matthew.sverre.anderson@...
> Date: Mon, 14 Nov 2011 19:16:40 +0000
> Subject: [EnergyPlus_Support] Re: IDF Review for no Cooling
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> I am currently doing some other things at work and will try that a little later. Is that why there is no cooling occurring in this IDF?
>
>
>
> Is there anyway you could troubleshoot the IDF Dr. Li?
>
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@> wrote:
>
> >
>
> >
>
> > You can set a wider dead band for the un-occupied period. Heating set point must be lower than the cooling set point, so that they do not overlap. The dead band may be as little as 0.1°F. Otherwice, you can set them to any temperature. If I wanted to turn off the cooling completely, I simply set the cooling set point to 98°F for that zone. If you have water system, you may still need the seasonal control for the plants., so that the water system will be freeze.
>
> >
>
> > Dr. Li
>
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>
> > From: matthew.sverre.anderson@
>
> > Date: Mon, 14 Nov 2011 18:39:01 +0000
>
> > Subject: [EnergyPlus_Support] Re: IDF Review for no Cooling
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> > So do something like set a cooling set point to 74, Heating to 70 for a mean set point of 72 with a 2 degree deadband?
>
> >
>
> >
>
> >
>
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@> wrote:
>
> >
>
> > >
>
> >
>
> > > HEATING COOLING SETPOINTS is the schedule name for both your heating setpoint and your cooling setpoint. I recommend using 2 seperate schedules to achieve a dead band.
>
> >
>
> > >
>
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/