|
What I really meant was to add a return path to the VAV system like the CBVAV system.
Right now, the air volume has to be set farely high, if the AHU air temperature is set nearer to the required zone temperture. With the by pass path, the fan volume can increase without increasing the zone air, as it is already at maximum for that condition which causes the ref set point to rise. Changing the coil size does not help, becsuse the ref temperature is fixed. The high added internal at the return air can not flow through the by-pass path and be cooled faster without increasing the zone air flow. With the bypass, the AHU fan outlet temperature can be set to just below the zone temperature, and thus does not require the reheat. Setting the fan temperature to 16 to 18°C would also meet the humidity control requirement, and does not require the reheat, if the air volume is allowed to go to a lower limit, using the damper control. ==================== You have shown many set point choices. I do not think many user can follow. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: RRaustad@xxxxxxxxxxxx Date: Fri, 18 Nov 2011 13:37:35 -0500 Subject: Re: [EnergyPlus_Support] Problem with results of a simulation
That would defeat the purpose of the CBVAV system. It's not that the
reference node temperature can't be maintained at some set point,
it's that the zones could over-cool.
If users chose to use a SetpointManager:SingleZone:Cooling and SetpointManager:SingleZone:Heating to control the air loop cooling and heating coil instead of using a constant supply air temperature, at least there would be one zone at the set point. Or if they used a SetpointManager:MultiZone:Heating:Average or SetpointManager:MultiZone:Cooling:Average to control each coil then all zones would be near the thermostat set point temperature (assuming all zones used the same temperature set point). O fcourse some zones would be higher and lower than the set point based on zone load diversity. On 11/10/2011 5:00 PM, YuanLu Li wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |