Thanks again Jason, 
About match surface. I was curious that why you said match the [top floor] floor to the [ground floor] ceiling and the [mid floor] floor to the [mid floor] ceiling.

I thought [top floor] floor match to [mid floor]ceiling , and [mid floor] floor to [ground floor] ceiling. 

Could explain the concept behind? 




--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jason Kirkpatrick <jason.alan.kirkpatrick@...> wrote:
>
> You've got the floor elevation approach correct. Also, yes you can use
> whatever constructions are actually on the project, but understand that if
> you are using 'adiabatic' as a boundary condition for the [top floor]
> floor, [mid floor] floor and ceiling, and [ground floor] ceiling, you will
> not get any heat transfer through those surfaces. If you want some heat
> transfer but not too detailed, use the otherside coefficients type of
> boundary condition. if you want accurate heat transfer through these
> surfaces and are willing to put in the detail, you can match the [top
> floor] floor to the [ground floor] ceiling and the [mid floor] floor to the
> [mid floor] ceiling.
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/