The sizing to a larger value of course would help.
I got this problem in 2008 with an Australia real VRV - VAV installation, and your answer was the CBVAV at that time for simulation purposes. I did not post this to the help desk, because I would never use this VAV system myself, because over cool and reheat combination is not really energy efficient. It may have running cost and comfort advantage. =========================== The maximum air volume is imposed by the sum of the active zone air volume, and not by the fan. The zones have different demands on different days. When the over cool level is at 12.5°C, the problem is less obvious. When the air loop temperature is set to say, 18°C instead of 12.8°C setpoint, and without reheat, many warnings appeared as setpoint value not met. I know that this is not the EPlus intented way the system should be designed, but the users are doing it. I like to set the air loop temperature fixed in between the cooling and heating dual band temperature. 12.5°C is too low as the air loop duct temperature, but can be the coil temperature. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: RRaustad@xxxxxxxxxxxx Date: Wed, 30 Nov 2011 13:58:43 -0500 Subject: Re: [EnergyPlus_Support] Re: SetpointManager:MixedAir and Economizer question
I have read a lot of your posts and you obviously know what you are
talking about. So I am a little confused.
What I do not understand is why we would want to try to get better performance out of a system that is obviously undersized? Of course if you increase the load to be greater than the system can handle, the zone temp will rise. Instead of using a bypass, how about sizing the system correctly in the first place. I must not fully understand what you are trying to say. Let me also add that I usually respond only to questions on the help desk. I do not typically answer questions on this forum but sometimes I can provide an answer very quickly and it doesn't take much of my time. On 11/30/2011 1:24 PM, YuanLu Li wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |