[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: SetpointManager:MixedAir and Economizer question



After reading the io Ref. your suggestion did not make much sense. I applied it anyway and got the errors that I thought I would get.

The reference node must have a setpoint assigned to it by another setpoint manager.

The setpoint nodes are all the nodes to which the SetpointManager:MixedAir will assign the new calculated setpoint to.

This means the Reference Node should have a setpoint assigned by another manager = air delivery temperature (which should change for the heating and cooling case), as this is the setpoint which you are trying to hit. 

And none of the nodes in the SetpointNodeList may be set by other setpointmanagers as they will conflict.

In my current configuration I have Mixingbox,[Fan,dx cooling coil],hot water coil. With setpoint managers for cooling at the dx outlet node (12°C) and at the heating coil outlet (-99 to 34°C). The Setpoint assigned at the exit of my htg coil doubles as my delivery air setpoint temp and serves as the reference node for the SetpointManager:MixedAir. My SetpointManager:MixedAir Setpoint is only assigned to the exit of the Mixing box (but could also be assigned to the exit of the fan.)

I think James and I understand this object differently.

Pointers? Comments?

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> 1) put the reference node on any node that will not be controlled, use 
> the return node if you have to, or the fan outlet would also work
> 2) don't worry about upstream and downstream, just enter the fan 
> inlet/outlet node names and the manager will do the rest
> 
> What you are basically doing is calculating a set point at the reference 
> node, and then using the mixed air manager to adjust that calculated set 
> point by the fan heat. So when all is said and done, the outlet of the 
> air loop is at the same  temperature as the reference node set point 
> temperature
> 
> On 11/29/2011 11:50 AM, Jean marais wrote:
> >
> > Thanks James. A few more questions, if you'll indulge me...
> >
> > The referance node:
> > I assume one must be quite careful as to what setpoint is used on the 
> > reference node (usually the last node on the supply side). For 
> > example, if my last componant is a heating coil, I can't assign a 
> > fixed schedule 32degC with a setpoint manager on the htg coil exit 
> > node, if I plan heating and cooling all year round. I need to use, in 
> > this case a setpoint manager that can decrease the setpoint on this 
> > node during times of cooling. Right?
> >
> > The other setpoint nodes in the list:
> > How does the MixedAirSPmanager "know" on which node the fan sits, to 
> > deturmine upstream and down stream from it? I don't have it here. Is 
> > it an input field? I ask, because not just the fan takes or adds to 
> > the air stream. Maybe, it just looks at the setpoint on each node in 
> > the list (not the airstream temp), checks if it must be applied (eg. 
> > clg sp not applied if in heating mode), and estimates the energy put 
> > in or out at these nodes. Using this information, it sets the setpoint 
> > at the exit of the mixing box, then the controller tries to control 
> > the damper to match. Right?
> >
> > Please explain "exception 1". My guess is that if the downstream htg 
> > coil exit node was included, the manager would see it as a second fan 
> > and (if outside had cold air) possibly introduce more than nessecary 
> > ODA, which the poor htg coil would have to heat up. This all becomes 
> > hellishly complicated considering econimizers and other factors.
> >
> > 
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/