[EnergyPlus_Support] Correction re: VRF / VRV modeling
Dear Forum,
I know I've posted a couple of times about modeling a VRF / VRV system by using special inputs and post-processing on a water source heat pump system.
It's embarassing to find that I've posted incorrect information twice, I think, but I am posting now to correct it in case anyone was using the old information.
If this makes no sense, then you are not using my earler posts and can ignore it :)
The condensed story:
The WSHPs must be modeled with a very large COP (e.g., 1000) so that the compressor energy is essentially zero and only the zone load is passed to the chiller or boiler.
The chiller must be modeled with COP = 1.0 and boiler efficiency = 1.0. This results in the chiller and boiler using energy equal to the load. This energy can then be post-processed using the VRF part load performance.
p.s., E+ now can model the non-heat-recovery VRF systems all by itself. The heat recovery VRF systems are what I am discussing here.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/