Re: [EnergyPlus_Support] Incorrect Floor and Roof drawing (dxf)



Perhaps version 5 just didn't detect the problem.




At 10:39 AM 12/16/2011, eplusven wrote:
>Hi All,
>
>I am facing a problem where my building walls out put correct, 
>however floor and roof are going wrong. I checked all possibilities 
>such as reversing coordinates, chnaging vertex order from anti clok 
>to clockwise, I still couln't fix this problem. The same geometry 
>was output correct in EnergyPlus5, but not in EnergyPlus 6 or 7. Can 
>anyone shed some ideas on it, please.
>
>Thanks & regards
>-Ven
>
>Here is the complete IDF V.6
>
>
>
>!-Generator IDFEditor 1.38a
>!-Option SortedOrder
>
>!-NOTE: All comments with '!-' are ignored by the IDFEditor and are 
>generated automatically.
>!-      Use '!' comments if they need to be retained when using the IDFEditor.
>
>
>!-   ===========  ALL OBJECTS IN CLASS: VERSION ===========
>
>Version,
>     6.0;                     !- Version Identifier
>
>
>!-   ===========  ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========
>
>SimulationControl,
>     Yes,                     !- Do Zone Sizing Calculation
>     Yes,                     !- Do System Sizing Calculation
>     Yes,                     !- Do Plant Sizing Calculation
>     No,                      !- Run Simulation for Sizing Periods
>     Yes;                     !- Run Simulation for Weather File Run Periods
>
>
>!-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========
>
>Building,
>     Building1,               !- Name
>     ,                        !- North Axis {deg}
>     ,                        !- Terrain
>     0.04,                    !- Loads Convergence Tolerance Value
>     0.4,                     !- Temperature Convergence Tolerance 
> Value {deltaC}
>     ,                        !- Solar Distribution
>     ;                        !- Maximum Number of Warmup Days
>
>
>!-   ===========  ALL OBJECTS IN CLASS: SHADOWCALCULATION ===========
>
>ShadowCalculation,
>     ;                        !- Calculation Frequency
>
>
>!-   ===========  ALL OBJECTS IN CLASS: 
>SURFACECONVECTIONALGORITHM:INSIDE ===========
>
>SurfaceConvectionAlgorithm:Inside,
>     ;                        !- Algorithm
>
>
>!-   ===========  ALL OBJECTS IN CLASS: 
>SURFACECONVECTIONALGORITHM:OUTSIDE ===========
>
>SurfaceConvectionAlgorithm:Outside,
>     ;                        !- Algorithm
>
>
>!-   ===========  ALL OBJECTS IN CLASS: HEATBALANCEALGORITHM ===========
>
>HeatBalanceAlgorithm,
>     ;                        !- Algorithm
>
>
>!-   ===========  ALL OBJECTS IN CLASS: TIMESTEP ===========
>
>Timestep,
>     1;                       !- Number of Timesteps per Hour
>
>
>!-   ===========  ALL OBJECTS IN CLASS: SITE:LOCATION ===========
>
>Site:Location,
>     City,                    !- Name
>     0,                       !- Latitude {deg}
>     0,                       !- Longitude {deg}
>     0,                       !- Time Zone {hr}
>     0;                       !- Elevation {m}
>
>
>!-   ===========  ALL OBJECTS IN CLASS: SIZINGPERIOD:DESIGNDAY ===========
>
>SizingPeriod:DesignDay,
>     WinterDD,                !- Name
>     -12.3,                   !- Maximum Dry-Bulb Temperature {C}
>     0,                       !- Daily Temperature Range {deltaC}
>     -12.3,                   !- Humidity Indicating Conditions at 
> Maximum Dry-Bulb
>     100547,                  !- Barometric Pressure {Pa}
>     4,                       !- Wind Speed {m/s}
>     330,                     !- Wind Direction {deg}
>     0,                       !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day of Month
>     1,                       !- Month
>     WinterDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     WetBulb;                 !- Humidity Indicating Type
>
>SizingPeriod:DesignDay,
>     SummerDD,                !- Name
>     33.6,                    !- Maximum Dry-Bulb Temperature {C}
>     10,                      !- Daily Temperature Range {deltaC}
>     23.6,                    !- Humidity Indicating Conditions at 
> Maximum Dry-Bulb
>     100547,                  !- Barometric Pressure {Pa}
>     4.7,                     !- Wind Speed {m/s}
>     250,                     !- Wind Direction {deg}
>     1,                       !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day of Month
>     7,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     WetBulb;                 !- Humidity Indicating Type
>
>
>!-   ===========  ALL OBJECTS IN CLASS: RUNPERIOD ===========
>
>RunPeriod,
>     RP,                      !- Name
>     1,                       !- Begin Month
>     1,                       !- Begin Day of Month
>     12,                      !- End Month
>     31,                      !- End Day of Month
>     ,                        !- Day of Week for Start Day
>     ,                        !- Use Weather File Holidays and Special Days
>     ,                        !- Use Weather File Daylight Saving Period
>     ,                        !- Apply Weekend Holiday Rule
>     ,                        !- Use Weather File Rain Indicators
>     ;                        !- Use Weather File Snow Indicators
>
>
>!-   ===========  ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========
>
>ScheduleTypeLimits,
>     Fraction,                !- Name
>     0,                       !- Lower Limit Value
>     1,                       !- Upper Limit Value
>     Continuous;              !- Numeric Type
>
>ScheduleTypeLimits,
>     AnyNumber;               !- Name
>
>ScheduleTypeLimits,
>     OnOff,                   !- Name
>     0,                       !- Lower Limit Value
>     1,                       !- Upper Limit Value
>     Discrete;                !- Numeric Type
>
>
>!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========
>
>Schedule:Compact,
>     DefaultAlwaysOn,         !- Name
>     OnOff,                   !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays ,           !- Field 2
>     Until: 24:0,             !- Field 3
>     1;                       !- Field 4
>
>Schedule:Compact,
>     Occupancy week day schedule,  !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekends Holiday ,  !- Field 2
>     Until: 1:0,              !- Field 3
>     0,                       !- Field 4
>     Until: 2:0,              !- Field 5
>     0,                       !- Field 6
>     Until: 3:0,              !- Field 7
>     0,                       !- Field 8
>     Until: 4:0,              !- Field 9
>     0,                       !- Field 10
>     Until: 5:0,              !- Field 11
>     0,                       !- Field 12
>     Until: 6:0,              !- Field 13
>     0,                       !- Field 14
>     Until: 7:0,              !- Field 15
>     0.5,                     !- Field 16
>     Until: 8:0,              !- Field 17
>     0.5,                     !- Field 18
>     Until: 9:0,              !- Field 19
>     0.9,                     !- Field 20
>     Until: 10:0,             !- Field 21
>     0.9,                     !- Field 22
>     Until: 11:0,             !- Field 23
>     0.9,                     !- Field 24
>     Until: 12:0,             !- Field 25
>     0.9,                     !- Field 26
>     Until: 13:0,             !- Field 27
>     0.9,                     !- Field 28
>     Until: 14:0,             !- Field 29
>     0.9,                     !- Field 30
>     Until: 15:0,             !- Field 31
>     0.9,                     !- Field 32
>     Until: 16:0,             !- Field 33
>     0.9,                     !- Field 34
>     Until: 17:0,             !- Field 35
>     0.9,                     !- Field 36
>     Until: 18:0,             !- Field 37
>     0.9,                     !- Field 38
>     Until: 19:0,             !- Field 39
>     0.9,                     !- Field 40
>     Until: 20:0,             !- Field 41
>     0.9,                     !- Field 42
>     Until: 21:0,             !- Field 43
>     0,                       !- Field 44
>     Until: 22:0,             !- Field 45
>     0,                       !- Field 46
>     Until: 23:0,             !- Field 47
>     0,                       !- Field 48
>     Until: 24:0,             !- Field 49
>     0,                       !- Field 50
>     For: Weekdays ,          !- Field 51
>     Until: 1:0,              !- Field 52
>     0,                       !- Field 53
>     Until: 2:0,              !- Field 54
>     0,                       !- Field 55
>     Until: 3:0,              !- Field 56
>     0,                       !- Field 57
>     Until: 4:0,              !- Field 58
>     0,                       !- Field 59
>     Until: 5:0,              !- Field 60
>     0,                       !- Field 61
>     Until: 6:0,              !- Field 62
>     0,                       !- Field 63
>     Until: 7:0,              !- Field 64
>     0.5,                     !- Field 65
>     Until: 8:0,              !- Field 66
>     0.5,                     !- Field 67
>     Until: 9:0,              !- Field 68
>     0.9,                     !- Field 69
>     Until: 10:0,             !- Field 70
>     0.9,                     !- Field 71
>     Until: 11:0,             !- Field 72
>     0.9,                     !- Field 73
>     Until: 12:0,             !- Field 74
>     0.9,                     !- Field 75
>     Until: 13:0,             !- Field 76
>     0.9,                     !- Field 77
>     Until: 14:0,             !- Field 78
>     0.9,                     !- Field 79
>     Until: 15:0,             !- Field 80
>     0.9,                     !- Field 81
>     Until: 16:0,             !- Field 82
>     0.9,                     !- Field 83
>     Until: 17:0,             !- Field 84
>     0.9,                     !- Field 85
>     Until: 18:0,             !- Field 86
>     0.9,                     !- Field 87
>     Until: 19:0,             !- Field 88
>     0.9,                     !- Field 89
>     Until: 20:0,             !- Field 90
>     0.9,                     !- Field 91
>     Until: 21:0,             !- Field 92
>     0,                       !- Field 93
>     Until: 22:0,             !- Field 94
>     0,                       !- Field 95
>     Until: 23:0,             !- Field 96
>     0,                       !- Field 97
>     Until: 24:0,             !- Field 98
>     0;                       !- Field 99
>
>Schedule:Compact,
>     PeopleOfficeActivity,    !- Name
>     AnyNumber,               !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays ,           !- Field 2
>     Until: 24:0,             !- Field 3
>     131.8;                   !- Field 4
>
>Schedule:Compact,
>     Interior lighting weekday schedule,  !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekends Holiday ,  !- Field 2
>     Until: 1:0,              !- Field 3
>     0.01,                    !- Field 4
>     Until: 2:0,              !- Field 5
>     0.01,                    !- Field 6
>     Until: 3:0,              !- Field 7
>     0.01,                    !- Field 8
>     Until: 4:0,              !- Field 9
>     0.01,                    !- Field 10
>     Until: 5:0,              !- Field 11
>     0.01,                    !- Field 12
>     Until: 6:0,              !- Field 13
>     0.01,                    !- Field 14
>     Until: 7:0,              !- Field 15
>     0.5,                     !- Field 16
>     Until: 8:0,              !- Field 17
>     0.5,                     !- Field 18
>     Until: 9:0,              !- Field 19
>     0.9,                     !- Field 20
>     Until: 10:0,             !- Field 21
>     0.9,                     !- Field 22
>     Until: 11:0,             !- Field 23
>     0.9,                     !- Field 24
>     Until: 12:0,             !- Field 25
>     0.9,                     !- Field 26
>     Until: 13:0,             !- Field 27
>     0.9,                     !- Field 28
>     Until: 14:0,             !- Field 29
>     0.9,                     !- Field 30
>     Until: 15:0,             !- Field 31
>     0.9,                     !- Field 32
>     Until: 16:0,             !- Field 33
>     0.9,                     !- Field 34
>     Until: 17:0,             !- Field 35
>     0.9,                     !- Field 36
>     Until: 18:0,             !- Field 37
>     0.9,                     !- Field 38
>     Until: 19:0,             !- Field 39
>     0.9,                     !- Field 40
>     Until: 20:0,             !- Field 41
>     0.9,                     !- Field 42
>     Until: 21:0,             !- Field 43
>     0.01,                    !- Field 44
>     Until: 22:0,             !- Field 45
>     0.01,                    !- Field 46
>     Until: 23:0,             !- Field 47
>     0.01,                    !- Field 48
>     Until: 24:0,             !- Field 49
>     0.01,                    !- Field 50
>     For: Weekdays ,          !- Field 51
>     Until: 1:0,              !- Field 52
>     0.01,                    !- Field 53
>     Until: 2:0,              !- Field 54
>     0.01,                    !- Field 55
>     Until: 3:0,              !- Field 56
>     0.01,                    !- Field 57
>     Until: 4:0,              !- Field 58
>     0.01,                    !- Field 59
>     Until: 5:0,              !- Field 60
>     0.01,                    !- Field 61
>     Until: 6:0,              !- Field 62
>     0.01,                    !- Field 63
>     Until: 7:0,              !- Field 64
>     0.5,                     !- Field 65
>     Until: 8:0,              !- Field 66
>     0.5,                     !- Field 67
>     Until: 9:0,              !- Field 68
>     0.9,                     !- Field 69
>     Until: 10:0,             !- Field 70
>     0.9,                     !- Field 71
>     Until: 11:0,             !- Field 72
>     0.9,                     !- Field 73
>     Until: 12:0,             !- Field 74
>     0.9,                     !- Field 75
>     Until: 13:0,             !- Field 76
>     0.9,                     !- Field 77
>     Until: 14:0,             !- Field 78
>     0.9,                     !- Field 79
>     Until: 15:0,             !- Field 80
>     0.9,                     !- Field 81
>     Until: 16:0,             !- Field 82
>     0.9,                     !- Field 83
>     Until: 17:0,             !- Field 84
>     0.9,                     !- Field 85
>     Until: 18:0,             !- Field 86
>     0.9,                     !- Field 87
>     Until: 19:0,             !- Field 88
>     0.9,                     !- Field 89
>     Until: 20:0,             !- Field 90
>     0.9,                     !- Field 91
>     Until: 21:0,             !- Field 92
>     0.01,                    !- Field 93
>     Until: 22:0,             !- Field 94
>     0.01,                    !- Field 95
>     Until: 23:0,             !- Field 96
>     0.01,                    !- Field 97
>     Until: 24:0,             !- Field 98
>     0.01;                    !- Field 99
>
>Schedule:Compact,
>     Equipment schedule weekday,  !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekends Holiday ,  !- Field 2
>     Until: 1:0,              !- Field 3
>     0.05,                    !- Field 4
>     Until: 2:0,              !- Field 5
>     0.05,                    !- Field 6
>     Until: 3:0,              !- Field 7
>     0.05,                    !- Field 8
>     Until: 4:0,              !- Field 9
>     0.05,                    !- Field 10
>     Until: 5:0,              !- Field 11
>     0.05,                    !- Field 12
>     Until: 6:0,              !- Field 13
>     0.05,                    !- Field 14
>     Until: 7:0,              !- Field 15
>     0.5,                     !- Field 16
>     Until: 8:0,              !- Field 17
>     0.5,                     !- Field 18
>     Until: 9:0,              !- Field 19
>     0.9,                     !- Field 20
>     Until: 10:0,             !- Field 21
>     0.9,                     !- Field 22
>     Until: 11:0,             !- Field 23
>     0.9,                     !- Field 24
>     Until: 12:0,             !- Field 25
>     0.9,                     !- Field 26
>     Until: 13:0,             !- Field 27
>     0.9,                     !- Field 28
>     Until: 14:0,             !- Field 29
>     0.9,                     !- Field 30
>     Until: 15:0,             !- Field 31
>     0.9,                     !- Field 32
>     Until: 16:0,             !- Field 33
>     0.9,                     !- Field 34
>     Until: 17:0,             !- Field 35
>     0.9,                     !- Field 36
>     Until: 18:0,             !- Field 37
>     0.9,                     !- Field 38
>     Until: 19:0,             !- Field 39
>     0.9,                     !- Field 40
>     Until: 20:0,             !- Field 41
>     0.9,                     !- Field 42
>     Until: 21:0,             !- Field 43
>     0.05,                    !- Field 44
>     Until: 22:0,             !- Field 45
>     0.05,                    !- Field 46
>     Until: 23:0,             !- Field 47
>     0.05,                    !- Field 48
>     Until: 24:0,             !- Field 49
>     0.05,                    !- Field 50
>     For: Weekdays ,          !- Field 51
>     Until: 1:0,              !- Field 52
>     0.05,                    !- Field 53
>     Until: 2:0,              !- Field 54
>     0.05,                    !- Field 55
>     Until: 3:0,              !- Field 56
>     0.05,                    !- Field 57
>     Until: 4:0,              !- Field 58
>     0.05,                    !- Field 59
>     Until: 5:0,              !- Field 60
>     0.05,                    !- Field 61
>     Until: 6:0,              !- Field 62
>     0.05,                    !- Field 63
>     Until: 7:0,              !- Field 64
>     0.5,                     !- Field 65
>     Until: 8:0,              !- Field 66
>     0.5,                     !- Field 67
>     Until: 9:0,              !- Field 68
>     0.9,                     !- Field 69
>     Until: 10:0,             !- Field 70
>     0.9,                     !- Field 71
>     Until: 11:0,             !- Field 72
>     0.9,                     !- Field 73
>     Until: 12:0,             !- Field 74
>     0.9,                     !- Field 75
>     Until: 13:0,             !- Field 76
>     0.9,                     !- Field 77
>     Until: 14:0,             !- Field 78
>     0.9,                     !- Field 79
>     Until: 15:0,             !- Field 80
>     0.9,                     !- Field 81
>     Until: 16:0,             !- Field 82
>     0.9,                     !- Field 83
>     Until: 17:0,             !- Field 84
>     0.9,                     !- Field 85
>     Until: 18:0,             !- Field 86
>     0.9,                     !- Field 87
>     Until: 19:0,             !- Field 88
>     0.9,                     !- Field 89
>     Until: 20:0,             !- Field 90
>     0.9,                     !- Field 91
>     Until: 21:0,             !- Field 92
>     0.05,                    !- Field 93
>     Until: 22:0,             !- Field 94
>     0.05,                    !- Field 95
>     Until: 23:0,             !- Field 96
>     0.05,                    !- Field 97
>     Until: 24:0,             !- Field 98
>     0.05;                    !- Field 99
>
>Schedule:Compact,
>     Exterior lighting schedule weekday,  !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekends Holiday ,  !- Field 2
>     Until: 1:0,              !- Field 3
>     1,                       !- Field 4
>     Until: 2:0,              !- Field 5
>     1,                       !- Field 6
>     Until: 3:0,              !- Field 7
>     1,                       !- Field 8
>     Until: 4:0,              !- Field 9
>     1,                       !- Field 10
>     Until: 5:0,              !- Field 11
>     1,                       !- Field 12
>     Until: 6:0,              !- Field 13
>     1,                       !- Field 14
>     Until: 7:0,              !- Field 15
>     0,                       !- Field 16
>     Until: 8:0,              !- Field 17
>     0,                       !- Field 18
>     Until: 9:0,              !- Field 19
>     0,                       !- Field 20
>     Until: 10:0,             !- Field 21
>     0,                       !- Field 22
>     Until: 11:0,             !- Field 23
>     0,                       !- Field 24
>     Until: 12:0,             !- Field 25
>     0,                       !- Field 26
>     Until: 13:0,             !- Field 27
>     0,                       !- Field 28
>     Until: 14:0,             !- Field 29
>     0,                       !- Field 30
>     Until: 15:0,             !- Field 31
>     0,                       !- Field 32
>     Until: 16:0,             !- Field 33
>     0,                       !- Field 34
>     Until: 17:0,             !- Field 35
>     0,                       !- Field 36
>     Until: 18:0,             !- Field 37
>     0,                       !- Field 38
>     Until: 19:0,             !- Field 39
>     0,                       !- Field 40
>     Until: 20:0,             !- Field 41
>     0,                       !- Field 42
>     Until: 21:0,             !- Field 43
>     1,                       !- Field 44
>     Until: 22:0,             !- Field 45
>     1,                       !- Field 46
>     Until: 23:0,             !- Field 47
>     1,                       !- Field 48
>     Until: 24:0,             !- Field 49
>     1,                       !- Field 50
>     For: Weekdays ,          !- Field 51
>     Until: 1:0,              !- Field 52
>     1,                       !- Field 53
>     Until: 2:0,              !- Field 54
>     1,                       !- Field 55
>     Until: 3:0,              !- Field 56
>     1,                       !- Field 57
>     Until: 4:0,              !- Field 58
>     1,                       !- Field 59
>     Until: 5:0,              !- Field 60
>     1,                       !- Field 61
>     Until: 6:0,              !- Field 62
>     1,                       !- Field 63
>     Until: 7:0,              !- Field 64
>     0,                       !- Field 65
>     Until: 8:0,              !- Field 66
>     0,                       !- Field 67
>     Until: 9:0,              !- Field 68
>     0,                       !- Field 69
>     Until: 10:0,             !- Field 70
>     0,                       !- Field 71
>     Until: 11:0,             !- Field 72
>     0,                       !- Field 73
>     Until: 12:0,             !- Field 74
>     0,                       !- Field 75
>     Until: 13:0,             !- Field 76
>     0,                       !- Field 77
>     Until: 14:0,             !- Field 78
>     0,                       !- Field 79
>     Until: 15:0,             !- Field 80
>     0,                       !- Field 81
>     Until: 16:0,             !- Field 82
>     0,                       !- Field 83
>     Until: 17:0,             !- Field 84
>     0,                       !- Field 85
>     Until: 18:0,             !- Field 86
>     0,                       !- Field 87
>     Until: 19:0,             !- Field 88
>     0,                       !- Field 89
>     Until: 20:0,             !- Field 90
>     0,                       !- Field 91
>     Until: 21:0,             !- Field 92
>     1,                       !- Field 93
>     Until: 22:0,             !- Field 94
>     1,                       !- Field 95
>     Until: 23:0,             !- Field 96
>     1,                       !- Field 97
>     Until: 24:0,             !- Field 98
>     1;                       !- Field 99
>
>Schedule:Compact,
>     AirSideSystemAvailability,  !- Name
>     OnOff,                   !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays ,           !- Field 2
>     Until: 6:0,              !- Field 3
>     0,                       !- Field 4
>     Until: 20:0,             !- Field 5
>     1,                       !- Field 6
>     Until: 24:0,             !- Field 7
>     0;                       !- Field 8
>
>Schedule:Compact,
>     CoolingSchedule,         !- Name
>     AnyNumber,               !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays ,           !- Field 2
>     Until: 6:0,              !- Field 3
>     32.2222222222222,        !- Field 4
>     Until: 20:0,             !- Field 5
>     22.7777777777778,        !- Field 6
>     Until: 24:0,             !- Field 7
>     32.2222222222222;        !- Field 8
>
>Schedule:Compact,
>     HeatingSchedule,         !- Name
>     AnyNumber,               !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays ,           !- Field 2
>     Until: 6:0,              !- Field 3
>     12.7777777777778,        !- Field 4
>     Until: 20:0,             !- Field 5
>     21.6666666666667,        !- Field 6
>     Until: 24:0,             !- Field 7
>     12.7777777777778;        !- Field 8
>
>
>!-   ===========  ALL OBJECTS IN CLASS: MATERIAL ===========
>
>Material,
>     Stucco1IN,               !- Name
>     Smooth,                  !- Roughness
>     0.012,                   !- Thickness {m}
>     0.6918,                  !- Conductivity {W/m-K}
>     1858,                    !- Density {kg/m3}
>     837,                     !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.92,                    !- Solar Absorptance
>     0.92;                    !- Visible Absorptance
>
>Material,
>     ConcreteHW8IN,           !- Name
>     MediumRough,             !- Roughness
>     0.099,                   !- Thickness {m}
>     1.7296,                  !- Conductivity {W/m-K}
>     2243,                    !- Density {kg/m3}
>     837,                     !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.65,                    !- Solar Absorptance
>     0.65;                    !- Visible Absorptance
>
>Material,
>     WallInsulation,          !- Name
>     MediumRough,             !- Roughness
>     0.05645,                 !- Thickness {m}
>     0.0432,                  !- Conductivity {W/m-K}
>     91,                      !- Density {kg/m3}
>     837,                     !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.5,                     !- Solar Absorptance
>     0.5;                     !- Visible Absorptance
>
>Material,
>     Gypsum,                  !- Name
>     Smooth,                  !- Roughness
>     0.0127,                  !- Thickness {m}
>     0.16,                    !- Conductivity {W/m-K}
>     784.9,                   !- Density {kg/m3}
>     830,                     !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.92,                    !- Solar Absorptance
>     0.92;                    !- Visible Absorptance
>
>Material,
>     GP01GYPSUM,              !- Name
>     Smooth,                  !- Roughness
>     0.0127,                  !- Thickness {m}
>     0.16,                    !- Conductivity {W/m-K}
>     800,                     !- Density {kg/m3}
>     1090,                    !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.5;                     !- Visible Absorptance
>
>Material,
>     RoofMembrane,            !- Name
>     VeryRough,               !- Roughness
>     0.0095,                  !- Thickness {m}
>     0.16,                    !- Conductivity {W/m-K}
>     1121.29,                 !- Density {kg/m3}
>     1460,                    !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.7;                     !- Visible Absorptance
>
>Material,
>     RoofInsulation,          !- Name
>     MediumRough,             !- Roughness
>     0.124,                   !- Thickness {m}
>     0.049,                   !- Conductivity {W/m-K}
>     265,                     !- Density {kg/m3}
>     836.8,                   !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.7;                     !- Visible Absorptance
>
>Material,
>     MetalDecking,            !- Name
>     MediumSmooth,            !- Roughness
>     0.0015,                  !- Thickness {m}
>     45.006,                  !- Conductivity {W/m-K}
>     7680,                    !- Density {kg/m3}
>     418.4,                   !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.3;                     !- Visible Absorptance
>
>Material,
>     StdMATCC054MWCONCRETE,   !- Name
>     Rough,                   !- Roughness
>     0.1,                     !- Thickness {m}
>     0.858,                   !- Conductivity {W/m-K}
>     1968,                    !- Density {kg/m3}
>     836.8,                   !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.2;                     !- Visible Absorptance
>
>Material,
>     MATCC058HWCONCRETE,      !- Name
>     Rough,                   !- Roughness
>     0.2032,                  !- Thickness {m}
>     1.311,                   !- Conductivity {W/m-K}
>     2240,                    !- Density {kg/m3}
>     836.8,                   !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.7;                     !- Visible Absorptance
>
>Material,
>     StdWood6inch,            !- Name
>     MediumSmooth,            !- Roughness
>     0.15,                    !- Thickness {m}
>     0.12,                    !- Conductivity {W/m-K}
>     540,                     !- Density {kg/m3}
>     1210,                    !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.7;                     !- Visible Absorptance
>
>Material,
>     In35,                    !- Name
>     Rough,                   !- Roughness
>     0.050799999,             !- Thickness {m}
>     0.035,                   !- Conductivity {W/m-K}
>     29,                      !- Density {kg/m3}
>     1213,                    !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.5,                     !- Solar Absorptance
>     0.5;                     !- Visible Absorptance
>
>
>!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:NOMASS ===========
>
>Material:NoMass,
>     StdCP02CARPETPAD,        !- Name
>     VeryRough,               !- Roughness
>     0.21648,                 !- Thermal Resistance {m2-K/W}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.8;                     !- Visible Absorptance
>
>Material:NoMass,
>     CP02CARPETPAD,           !- Name
>     VeryRough,               !- Roughness
>     0.2165,                  !- Thermal Resistance {m2-K/W}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.8;                     !- Visible Absorptance
>
>
>!-   ===========  ALL OBJECTS IN CLASS: 
>WINDOWMATERIAL:SIMPLEGLAZINGSYSTEM ===========
>
>WindowMaterial:SimpleGlazingSystem,
>     TheoreticalGlass,        !- Name
>     7,                       !- U-Factor {W/m2-K}
>     0.249;                   !- Solar Heat Gain Coefficient
>
>
>!-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION ===========
>
>Construction,
>     Construct_Floor,         !- Name
>     StdMATCC054MWCONCRETE,   !- Outside Layer
>     StdCP02CARPETPAD;        !- Layer 2
>
>Construction,
>     Construct_ExterierWall,  !- Name
>     Stucco1IN,               !- Outside Layer
>     ConcreteHW8IN,           !- Layer 2
>     Gypsum;                  !- Layer 3
>
>Construction,
>     Construct_InterierWall,  !- Name
>     GP01GYPSUM,              !- Outside Layer
>     GP01GYPSUM;              !- Layer 2
>
>Construction,
>     Construct_Ceiling,       !- Name
>     CP02CARPETPAD,           !- Outside Layer
>     MATCC058HWCONCRETE;      !- Layer 2
>
>Construction,
>     Construct_Roof,          !- Name
>     RoofMembrane,            !- Outside Layer
>     RoofInsulation,          !- Layer 2
>     MetalDecking;            !- Layer 3
>
>Construction,
>     Construct_InternalMass,  !- Name
>     StdWood6inch;            !- Outside Layer
>
>Construction,
>     Construct_WINDOW,        !- Name
>     TheoreticalGlass;        !- Outside Layer
>
>
>!-   ===========  ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========
>
>GlobalGeometryRules,
>     LowerLeftCorner,         !- Starting Vertex Position
>     Counterclockwise,        !- Vertex Entry Direction
>     Relative,                !- Coordinate System
>     Relative,                !- Daylighting Reference Point Coordinate System
>     Relative;                !- Rectangular Surface Coordinate System
>
>
>!-   ===========  ALL OBJECTS IN CLASS: ZONE ===========
>
>Zone,
>     Zone_1,                  !- Name
>     ,                        !- Direction of Relative North {deg}
>     0,                       !- X Origin {m}
>     0,                       !- Y Origin {m}
>     0;                       !- Z Origin {m}
>
>
>!-   ===========  ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========
>
>BuildingSurface:Detailed,
>     Zone_1Floor,             !- Name
>     Floor,                   !- Surface Type
>     Construct_Floor,         !- Construction Name
>     Zone_1,                  !- Zone Name
>     Ground,                  !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     ,                        !- View Factor to Ground
>     12,                      !- Number of Vertices
>     -37.4999282479636,       !- Vertex 1 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     -12.4998560302497,       !- Vertex 2 X-coordinate {m}
>     -37.4995517736283,       !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     -12.500247152548,        !- Vertex 3 X-coordinate {m}
>     -12.5002202030691,       !- Vertex 3 Y-coordinate {m}
>     0,                       !- Vertex 3 Z-coordinate {m}
>     12.500247156774,         !- Vertex 4 X-coordinate {m}
>     -12.500220198843,        !- Vertex 4 Y-coordinate {m}
>     0,                       !- Vertex 4 Z-coordinate {m}
>     12.4998560378564,        !- Vertex 5 X-coordinate {m}
>     -37.4995517710927,       !- Vertex 5 Y-coordinate {m}
>     0,                       !- Vertex 5 Z-coordinate {m}
>     37.4999282479636,        !- Vertex 6 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 6 Y-coordinate {m}
>     0,                       !- Vertex 6 Z-coordinate {m}
>     37.500062206978,         !- Vertex 7 X-coordinate {m}
>     37.4999256462301,        !- Vertex 7 Y-coordinate {m}
>     0,                       !- Vertex 7 Z-coordinate {m}
>     12.4998366788769,        !- Vertex 8 X-coordinate {m}
>     37.4995582240832,        !- Vertex 8 Y-coordinate {m}
>     0,                       !- Vertex 8 Z-coordinate {m}
>     12.5002148910978,        !- Vertex 9 X-coordinate {m}
>     12.5002524645056,        !- Vertex 9 Y-coordinate {m}
>     0,                       !- Vertex 9 Z-coordinate {m}
>     -12.5002148868717,       !- Vertex 10 X-coordinate {m}
>     12.5002524687316,        !- Vertex 10 Y-coordinate {m}
>     0,                       !- Vertex 10 Z-coordinate {m}
>     -12.4998366712703,       !- Vertex 11 X-coordinate {m}
>     37.4995582266187,        !- Vertex 11 Y-coordinate {m}
>     0,                       !- Vertex 11 Z-coordinate {m}
>     -37.500062206978,        !- Vertex 12 X-coordinate {m}
>     37.4999256462301,        !- Vertex 12 Y-coordinate {m}
>     0;                       !- Vertex 12 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Roof,              !- Name
>     Roof,                    !- Surface Type
>     Construct_Roof,          !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     12,                      !- Number of Vertices
>     -37.4999282479636,       !- Vertex 1 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 1 Y-coordinate {m}
>     5,                       !- Vertex 1 Z-coordinate {m}
>     -12.4998560302497,       !- Vertex 2 X-coordinate {m}
>     -37.4995517736283,       !- Vertex 2 Y-coordinate {m}
>     5,                       !- Vertex 2 Z-coordinate {m}
>     -12.500247152548,        !- Vertex 3 X-coordinate {m}
>     -12.5002202030691,       !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     12.500247156774,         !- Vertex 4 X-coordinate {m}
>     -12.500220198843,        !- Vertex 4 Y-coordinate {m}
>     5,                       !- Vertex 4 Z-coordinate {m}
>     12.4998560378564,        !- Vertex 5 X-coordinate {m}
>     -37.4995517710927,       !- Vertex 5 Y-coordinate {m}
>     5,                       !- Vertex 5 Z-coordinate {m}
>     37.4999282479636,        !- Vertex 6 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 6 Y-coordinate {m}
>     5,                       !- Vertex 6 Z-coordinate {m}
>     37.500062206978,         !- Vertex 7 X-coordinate {m}
>     37.4999256462301,        !- Vertex 7 Y-coordinate {m}
>     5,                       !- Vertex 7 Z-coordinate {m}
>     12.4998366788769,        !- Vertex 8 X-coordinate {m}
>     37.4995582240832,        !- Vertex 8 Y-coordinate {m}
>     5,                       !- Vertex 8 Z-coordinate {m}
>     12.5002148910978,        !- Vertex 9 X-coordinate {m}
>     12.5002524645056,        !- Vertex 9 Y-coordinate {m}
>     5,                       !- Vertex 9 Z-coordinate {m}
>     -12.5002148868717,       !- Vertex 10 X-coordinate {m}
>     12.5002524687316,        !- Vertex 10 Y-coordinate {m}
>     5,                       !- Vertex 10 Z-coordinate {m}
>     -12.4998366712703,       !- Vertex 11 X-coordinate {m}
>     37.4995582266187,        !- Vertex 11 Y-coordinate {m}
>     5,                       !- Vertex 11 Z-coordinate {m}
>     -37.500062206978,        !- Vertex 12 X-coordinate {m}
>     37.4999256462301,        !- Vertex 12 Y-coordinate {m}
>     5;                       !- Vertex 12 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_1,            !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -37.4999282479636,       !- Vertex 1 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     -12.4998560302497,       !- Vertex 2 X-coordinate {m}
>     -37.4995517736283,       !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     -12.4998560302497,       !- Vertex 3 X-coordinate {m}
>     -37.4995517736283,       !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     -37.4999282479636,       !- Vertex 4 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_2,            !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -12.4998560302497,       !- Vertex 1 X-coordinate {m}
>     -37.4995517736283,       !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     -12.500247152548,        !- Vertex 2 X-coordinate {m}
>     -12.5002202030691,       !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     -12.500247152548,        !- Vertex 3 X-coordinate {m}
>     -12.5002202030691,       !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     -12.4998560302497,       !- Vertex 4 X-coordinate {m}
>     -37.4995517736283,       !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_3,            !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -12.500247152548,        !- Vertex 1 X-coordinate {m}
>     -12.5002202030691,       !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     12.500247156774,         !- Vertex 2 X-coordinate {m}
>     -12.500220198843,        !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     12.500247156774,         !- Vertex 3 X-coordinate {m}
>     -12.500220198843,        !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     -12.500247152548,        !- Vertex 4 X-coordinate {m}
>     -12.5002202030691,       !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_4,            !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     12.500247156774,         !- Vertex 1 X-coordinate {m}
>     -12.500220198843,        !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     12.4998560378564,        !- Vertex 2 X-coordinate {m}
>     -37.4995517710927,       !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     12.4998560378564,        !- Vertex 3 X-coordinate {m}
>     -37.4995517710927,       !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     12.500247156774,         !- Vertex 4 X-coordinate {m}
>     -12.500220198843,        !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_5,            !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     12.4998560378564,        !- Vertex 1 X-coordinate {m}
>     -37.4995517710927,       !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     37.4999282479636,        !- Vertex 2 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     37.4999282479636,        !- Vertex 3 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     12.4998560378564,        !- Vertex 4 X-coordinate {m}
>     -37.4995517710927,       !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_6,            !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     37.4999282479636,        !- Vertex 1 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     37.500062206978,         !- Vertex 2 X-coordinate {m}
>     37.4999256462301,        !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     37.500062206978,         !- Vertex 3 X-coordinate {m}
>     37.4999256462301,        !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     37.4999282479636,        !- Vertex 4 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_7,            !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     37.500062206978,         !- Vertex 1 X-coordinate {m}
>     37.4999256462301,        !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     12.4998366788769,        !- Vertex 2 X-coordinate {m}
>     37.4995582240832,        !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     12.4998366788769,        !- Vertex 3 X-coordinate {m}
>     37.4995582240832,        !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     37.500062206978,         !- Vertex 4 X-coordinate {m}
>     37.4999256462301,        !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_8,            !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     12.4998366788769,        !- Vertex 1 X-coordinate {m}
>     37.4995582240832,        !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     12.5002148910978,        !- Vertex 2 X-coordinate {m}
>     12.5002524645056,        !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     12.5002148910978,        !- Vertex 3 X-coordinate {m}
>     12.5002524645056,        !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     12.4998366788769,        !- Vertex 4 X-coordinate {m}
>     37.4995582240832,        !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_9,            !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     12.5002148910978,        !- Vertex 1 X-coordinate {m}
>     12.5002524645056,        !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     -12.5002148868717,       !- Vertex 2 X-coordinate {m}
>     12.5002524687316,        !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     -12.5002148868717,       !- Vertex 3 X-coordinate {m}
>     12.5002524687316,        !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     12.5002148910978,        !- Vertex 4 X-coordinate {m}
>     12.5002524645056,        !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_10,           !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -12.5002148868717,       !- Vertex 1 X-coordinate {m}
>     12.5002524687316,        !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     -12.4998366712703,       !- Vertex 2 X-coordinate {m}
>     37.4995582266187,        !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     -12.4998366712703,       !- Vertex 3 X-coordinate {m}
>     37.4995582266187,        !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     -12.5002148868717,       !- Vertex 4 X-coordinate {m}
>     12.5002524687316,        !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_11,           !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -12.4998366712703,       !- Vertex 1 X-coordinate {m}
>     37.4995582266187,        !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     -37.500062206978,        !- Vertex 2 X-coordinate {m}
>     37.4999256462301,        !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     -37.500062206978,        !- Vertex 3 X-coordinate {m}
>     37.4999256462301,        !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     -12.4998366712703,       !- Vertex 4 X-coordinate {m}
>     37.4995582266187,        !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>BuildingSurface:Detailed,
>     Zone_1Wall_12,           !- Name
>     Wall,                    !- Surface Type
>     Construct_ExterierWall,  !- Construction Name
>     Zone_1,                  !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -37.500062206978,        !- Vertex 1 X-coordinate {m}
>     37.4999256462301,        !- Vertex 1 Y-coordinate {m}
>     0,                       !- Vertex 1 Z-coordinate {m}
>     -37.4999282479636,       !- Vertex 2 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 2 Y-coordinate {m}
>     0,                       !- Vertex 2 Z-coordinate {m}
>     -37.4999282479636,       !- Vertex 3 X-coordinate {m}
>     -37.5000596052537,       !- Vertex 3 Y-coordinate {m}
>     5,                       !- Vertex 3 Z-coordinate {m}
>     -37.500062206978,        !- Vertex 4 X-coordinate {m}
>     37.4999256462301,        !- Vertex 4 Y-coordinate {m}
>     5;                       !- Vertex 4 Z-coordinate {m}
>
>
>!-   ===========  ALL OBJECTS IN CLASS: PEOPLE ===========
>
>People,
>     Zone_1People,            !- Name
>     Zone_1,                  !- Zone or ZoneList Name
>     Occupancy week day schedule,  !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     370,                     !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.7,                     !- Fraction Radiant
>     ,                        !- Sensible Heat Fraction
>     PeopleOfficeActivity;    !- Activity Level Schedule Name
>
>
>!-   ===========  ALL OBJECTS IN CLASS: LIGHTS ===========
>
>Lights,
>     Zone_1Lights,            !- Name
>     Zone_1,                  !- Zone or ZoneList Name
>     Interior lighting weekday schedule,  !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     40012,                   !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0,                       !- Return Air Fraction
>     0.72,                    !- Fraction Radiant
>     0.18,                    !- Fraction Visible
>     0;                       !- Fraction Replaceable
>
>
>!-   ===========  ALL OBJECTS IN CLASS: ELECTRICEQUIPMENT ===========
>
>ElectricEquipment,
>     Zone_1Equip,             !- Name
>     Zone_1,                  !- Zone or ZoneList Name
>     Equipment schedule weekday,  !- Schedule Name
>     Watts/Area,              !- Design Level Calculation Method
>     ,                        !- Design Level {W}
>     8.07,                    !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0,                       !- Fraction Latent
>     0.3,                     !- Fraction Radiant
>     0;                       !- Fraction Lost
>
>
>!-   ===========  ALL OBJECTS IN CLASS: EXTERIOR:LIGHTS ===========
>
>Exterior:Lights,
>     Exterior lighting,       !- Name
>     Exterior lighting schedule weekday,  !- Schedule Name
>     5.4;                     !- Design Level {W}
>
>
>!-   ===========  ALL OBJECTS IN CLASS: HVACTEMPLATE:THERMOSTAT ===========
>
>HVACTemplate:Thermostat,
>     AllZoneThermostat,       !- Name
>     HeatingSchedule,         !- Heating Setpoint Schedule Name
>     ,                        !- Constant Heating Setpoint {C}
>     CoolingSchedule,         !- Cooling Setpoint Schedule Name
>     ;                        !- Constant Cooling Setpoint {C}
>
>
>!-   ===========  ALL OBJECTS IN CLASS: HVACTEMPLATE:ZONE:VAV ===========
>
>HVACTemplate:Zone:VAV,
>     Zone_1,                  !- Zone Name
>     AHU,                     !- Template VAV System Name
>     AllZoneThermostat,       !- Template Thermostat Name
>     ,                        !- Supply Air Maximum Flow Rate {m3/s}
>     ,                        !- Zone Heating Sizing Factor
>     ,                        !- Zone Cooling Sizing Factor
>     ,                        !- Zone Minimum Air Flow Input Method
>     ,                        !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Flow/Area,               !- Outdoor Air Method
>     ,                        !- Outdoor Air Flow Rate per Person {m3/s}
>     0.0025,                  !- Outdoor Air Flow Rate per Zone 
> Floor Area {m3/s-m2}
>     ,                        !- Outdoor Air Flow Rate per Zone {m3/s}
>     Electric,                !- Reheat Coil Type
>     ,                        !- Reheat Coil Availability Schedule Name
>     ,                        !- Damper Heating Action
>     ,                        !- Maximum Flow per Zone Floor Area 
> During Reheat {m3/s-m2}
>     ,                        !- Maximum Flow Fraction During Reheat
>     ,                        !- Maximum Reheat Air Temperature {C}
>     ,                        !- Design Specification Outdoor Air Object Name
>     ,                        !- Supply Plenum Name
>     ,                        !- Return Plenum Name
>     ,                        !- Baseboard Heating Type
>     ,                        !- Baseboard Heating Availability Schedule Name
>     ;                        !- Baseboard Heating Capacity {W}
>
>
>!-   ===========  ALL OBJECTS IN CLASS: 
>HVACTEMPLATE:SYSTEM:PACKAGEDVAV ===========
>
>HVACTemplate:System:PackagedVAV,
>     AHU,                     !- Name
>     AirSideSystemAvailability,  !- System Availability Schedule Name
>     ,                        !- Supply Fan Maximum Flow Rate {m3/s}
>     ,                        !- Supply Fan Minimum Flow Rate {m3/s}
>     ,                        !- Supply Fan Placement
>     ,                        !- Supply Fan Total Efficiency
>     ,                        !- Supply Fan Delta Pressure {Pa}
>     ,                        !- Supply Fan Motor Efficiency
>     ,                        !- Supply Fan Motor in Air Stream Fraction
>     TwoSpeedDX,              !- Cooling Coil Type
>     ,                        !- Cooling Coil Availability Schedule Name
>     ,                        !- Cooling Coil Setpoint Schedule Name
>     12.7777777777778,        !- Cooling Coil Design Setpoint {C}
>     ,                        !- Cooling Coil Capacity {W}
>     ,                        !- Cooling Coil Rated Sensible Heat Ratio
>     2.5,                     !- Cooling Coil Rated COP
>     ,                        !- Heating Coil Type
>     ,                        !- Heating Coil Availability Schedule Name
>     ,                        !- Heating Coil Setpoint Schedule Name
>     ,                        !- Heating Coil Design Setpoint {C}
>     ,                        !- Heating Coil Capacity {W}
>     ,                        !- Gas Heating Coil Efficiency
>     ,                        !- Gas Heating Coil Parasitic Electric Load {W}
>     ,                        !- Maximum Outdoor Air Flow Rate {m3/s}
>     ,                        !- Minimum Outdoor Air Flow Rate {m3/s}
>     ,                        !- Minimum Outdoor Air Control Type
>     ,                        !- Minimum Outdoor Air Schedule Name
>     FixedDryBulb,            !- Economizer Type
>     LockoutWithCompressor,   !- Economizer Lockout
>     12.7777777777778,        !- Economizer Maximum Limit Dry-Bulb 
> Temperature {C}
>     ,                        !- Economizer Maximum Limit Enthalpy {J/kg}
>     ,                        !- Economizer Maximum Limit Dewpoint 
> Temperature {C}
>     4,                       !- Economizer Minimum Limit Dry-Bulb 
> Temperature {C}
>     ,                        !- Supply Plenum Name
>     ,                        !- Return Plenum Name
>     ,                        !- Supply Fan Part-Load Power Coefficients
>     ,                        !- Night Cycle Control
>     ,                        !- Night Cycle Control Zone Name
>     ,                        !- Heat Recovery Type
>     ,                        !- Sensible Heat Recovery Effectiveness
>     ,                        !- Latent Heat Recovery Effectiveness
>     ,                        !- Cooling Coil Setpoint Reset Type
>     ,                        !- Heating Coil Setpoint Reset Type
>     ,                        !- Dehumidification Control Type
>     ,                        !- Dehumidification Control Zone Name
>     ,                        !- Dehumidification Setpoint {percent}
>     None,                    !- Humidifier Type
>     ,                        !- Humidifier Availability Schedule Name
>     ,                        !- Humidifier Rated Capacity {m3/s}
>     ,                        !- Humidifier Rated Electric Power {W}
>     ,                        !- Humidifier Control Zone Name
>     ;                        !- Humidifier Setpoint {percent}
>
>
>!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:SURFACES:DRAWING ===========
>
>Output:Surfaces:Drawing,
>     DXF;                     !- Report Type
>
>
>!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:METER ===========
>
>Output:Meter,
>     Electricity:Facility,    !- Name
>     Timestep;                !- Reporting Frequency
>
>Output:Meter,
>     Photovoltaic:ElectricityProduced,  !- Name
>     Timestep;                !- Reporting Frequency
>
>
>
>
>
>
>
>
>------------------------------------
>
>Primary EnergyPlus support is found at:
>http://energyplus.helpserve.com or send a message to 
>energyplus-support@xxxxxxxx
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are currently allowed but be mindful that not everyone 
>has a high speed connection.  Limit attachments to small files.
>
>EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
>under the Documentation link and press the "search" button.
>Yahoo! Groups Links
>
>
>



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/